Old 04-16-2016, 07:28 AM   #1
Peapod
 
KenSanLan's Avatar
 
1985 31' Excella
Dade City , Florida
Join Date: Jun 2010
Posts: 126
Blog Entries: 1
Help please! Melted prong on 30 amp plug

This morning when preparing to move after a one night stay hubs discovered that one prong on our 30 amp plug had melted to the surge protector. Surge protector did not indicate a problem, no breakers blew. Was this likely a bad plug and we just need to replace it - and the surge protector - or should we be looking for another cause?
KenSanLan is offline   Reply With Quote
Old 04-16-2016, 07:40 AM   #2
Peapod
 
KenSanLan's Avatar
 
1985 31' Excella
Dade City , Florida
Join Date: Jun 2010
Posts: 126
Blog Entries: 1
1985 Excella 31'.
KenSanLan is offline   Reply With Quote
Old 04-16-2016, 07:49 AM   #3
Rivet Master
 
Minno's Avatar

 
1972 31' Sovereign
Lexington , Minnesota
Join Date: Feb 2009
Posts: 3,985
Typically, that's an indication of a loose plug to socket fitting, so current arcs from the socket to the plug blade, creating heat, and causing it to melt. I would replace both the plug and the surge protector, or maybe just the outlet on the surge protector if that can be replaced. The metal from the damaged plug blade is probably fused to the inside of the outlet socket, and it will never make good contact again.

Chris
Minno is offline   Reply With Quote
Old 04-16-2016, 07:52 AM   #4
Rivet Master
 
mimiandrews's Avatar
 
1966 22' Safari
Hilltop Lakes , Texas
Join Date: Jun 2008
Posts: 1,764
Could be a loose connector in the campground's side of the plug. Loose plug equals more resistance equals heat.

A simple surge protector probably would not see that. If you have a more sophisticated power monitor, it might.

My guess would be to replace the plug and try it out at the next stop.
mimiandrews is offline   Reply With Quote
Old 04-16-2016, 08:05 AM   #5
4 Rivet Member
 
Tn Traveler's Avatar
 
2006 25' Safari
Signal Mountain , Tennessee
Join Date: Jan 2016
Posts: 450
Images: 5
I concur with the loose connection probably causing arcing and heat. The problem could be in the chord plug or the receptacle on the surge protector. When you do install a new plug on the chord monitor the connection for heat. It could very well be a loose connection in the surge protector.
__________________
Don
'06 Safari 25 LS
'18 GMC 2500HD Duramax/Allison
TN,”Greenest State in the Land of the Free”.Davy Crocket
" America is not a place;it's a road." Mark Twain
Tn Traveler is offline   Reply With Quote
Old 04-16-2016, 08:09 AM   #6
Peapod
 
KenSanLan's Avatar
 
1985 31' Excella
Dade City , Florida
Join Date: Jun 2010
Posts: 126
Blog Entries: 1
Thank you so much! We are at Camping World right now buying new parts. Very glad we bought the extra warranty on the surge protector, and glad to hear it isn't a much bigger problem. We appreciate the replies.
KenSanLan is offline   Reply With Quote
Old 04-16-2016, 08:34 AM   #7
4 Rivet Member
 
Tn Traveler's Avatar
 
2006 25' Safari
Signal Mountain , Tennessee
Join Date: Jan 2016
Posts: 450
Images: 5
Quote:
Originally Posted by KenSanLan View Post
Thank you so much! We are at Camping World right now buying new parts. Very glad we bought the extra warranty on the surge protector, and glad to hear it isn't a much bigger problem. We appreciate the replies.
Thank you, for posting about your problem. I also picked up a new 30 amp surge protector at Camping World on their special deal last month. It makes me aware to check it closely for awhile.
__________________
Don
'06 Safari 25 LS
'18 GMC 2500HD Duramax/Allison
TN,”Greenest State in the Land of the Free”.Davy Crocket
" America is not a place;it's a road." Mark Twain
Tn Traveler is offline   Reply With Quote
Old 04-16-2016, 10:13 AM   #8
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
This problem is often a result of not turning off the source power before plugging into it. Failure to turn off the source power causes an arc at the plug/receptacle connection and over time destroys them. But you are only interested in your plug not the campgrounds receptacle.

Even if you do turn off the source power before plugging in you can get an indication of the status of the campground receptacle as you plug into it. The connection should be snug. A loose connection is an indication the the receptacle is on it's way out and often, if the AC is on, will result in a hot connection and reduced voltage during your stay. The older trailers had an indicator of low voltage. If you have a volt meter on your system any voltage below 105 you run the risk of damaging the AC.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 04-16-2016, 10:26 AM   #9
2 Rivet Member
 
1985 25' Sovereign
Olympia , Washington
Join Date: Dec 2005
Posts: 52
Thank you for sharing the problem and all thoughts about resolving. Makes me recall the start of a house fire at an outlet with a loosely fitted reading lamp.
Sovereign85 is offline   Reply With Quote
Old 04-16-2016, 12:05 PM   #10
Cajun Traveler
 
2014 27' FB International
Slaughter , Louisiana
Join Date: Nov 2014
Posts: 20
That happened to me. I had a terrible time removing our power cord from our camper because it was so much melting going on there. I brought it back to the airstream dealer and they found out that this was caused by a loose wire just inside the camper wall from the plug in. My cord was not damage. Thank goodness.

Happy Camping
Billyg is offline   Reply With Quote
Old 04-16-2016, 12:48 PM   #11
Rivet Master
 
greghoro's Avatar
 
2013 25' Flying Cloud
Wheaton , Illinois
Join Date: Aug 2014
Posts: 649
The male plug blades are usually not solid metal but a strip of metal folded over on itself. You can increase their snugness in the receptacle by inserting a knife blade between the two strips and carefully prying them apart slightly, bowing each strip outwards. Carefully and slightly are the key words here.

Also, its good to remove the oxidation from time to time with some steel wool or fine emery paper, wiping the filings off before using the plug. A light touch is best, you want to minimize the removal of metal.

I used to put a fine layer of dielectric grease on the blades but found that it tended to
collect dirt.


Greg
greghoro is online now   Reply With Quote
Old 04-16-2016, 01:50 PM   #12
3 Rivet Member
 
Caroyl's Avatar
 
1964 26' Overlander
Warner Robins , Georgia
Join Date: Oct 2015
Posts: 200
Good to know ����
__________________
Caroyl & Tim
1964 Overlander "Gracie"
WBCCI # 31088
2009 F-150 "Big Red"
Caroyl is offline   Reply With Quote
Old 04-16-2016, 02:03 PM   #13
1 Rivet Member
 
2004 30' Classic
Evans , Georgia
Join Date: Feb 2016
Posts: 11
Factory Defect

After several years our 2004 AS fried the 30 amp plug twice. When replacing didn't work called electrician. We discovered the black wire was missing a wire nut and all wires fused together inside the vehicle. The other end of the hook up cable is connected to a junction box located behind a panel in the "trunk". That is where the meltdown occurred.
jshotton is offline   Reply With Quote
Old 04-16-2016, 02:27 PM   #14
1 Rivet Member
 
madison , Wisconsin
Join Date: Jan 2014
Posts: 9
Plug overheating.

Campground outlets need to be scrutinized before using. Melted/distorted or discolored plastic means stay away. Overheating will oxidize your plugs. This can I suspect be passed like a virus. The 30 amp outlet is most used and most likely to have poor conductivity. I carry a 50 to 30 adapter for such outlets, assuming a 50 outlet is available. It was a long day, I noticed the discolored outlet but went ahead. Next morning I found my plug overheated. I'm now more careful.
garen-kary is offline   Reply With Quote
Old 04-17-2016, 07:11 PM   #15
Vintage Kin
 
Fort Worth , Texas
Join Date: Nov 2006
Posts: 8,014
Images: 1
Assume that campground electrical service is less than ideal.

And consider the male end to be a wearing part.

I use the adaptor to 50A as "usually" that outlet has seen less use.
slowmover is offline   Reply With Quote
Old 04-17-2016, 07:38 PM   #16
Rivet Master
 
dbj216's Avatar

 
1986 34' Limited
1975 27' Overlander
1969 21' Globetrotter
Conifer , Colorado
Join Date: Jun 2009
Posts: 8,289
Images: 1
We cooked our 30 amp plug also. It was just like Minno said in our case. The blade has a rivet connecting it to the wire end. The rivet worked loose with all the stresses of plugging in and out. I cut the rubber housing so I could see how it was made inside. I'm glad we noticed it in time. There has been more than one fire caused by loose connections. We used to scan the load centers in the factory I worked it with an infrared scanner to identify hot spots. It helps reduce the chance of fires. Loose connections build resistance and heat.

David
Attached Thumbnails
Click image for larger version

Name:	1512 Electrical Plug Bad.jpg
Views:	170
Size:	292.6 KB
ID:	260922  
dbj216 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
URGENT HELP NEEDED - Found Melted Wires This Afternoon BoldAdventure Refrigerators 24 05-04-2015 11:28 PM
Help, 12 Volt TV melted the plug-in at wall. RLS Audio, Video & TV 6 04-14-2013 10:23 PM
Bargman #99 Tailight refit 6-prong to 7-prong silverkeeper 1960 - 1965 Safari 6 03-05-2011 10:01 AM
shore power plug melted wheel interested Electrical - Systems, Generators, Batteries & Solar 61 03-22-2010 09:59 AM
3-prong plug converter to fit in regular outlet codybear Off Topic Forum 13 08-21-2006 09:00 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 04:22 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.