Ground fault using generators

I have a digital circuit tester that I keep plugged into an ac receptacle in my trailer. When I use my Honda 2000 generators (either in both in tandem or a single solo) I get a ground fault alarm on the tester. I have tried connecting the ground terminals of each generator together and to the body of the trailer. The alarm sounds even when the trailer is insulated from earth - stabilizers raised, hitch jack raised, truck and trailer on rubber tires.
pjmoser is offline   Reply With Quote
Old 05-31-2013, 08:21 AM   #2
Rivet Master
 
AirsDream's Avatar
 
1999 23' Safari
Perrysburg , Ann Arbor
Join Date: Sep 2005
Posts: 916
Do you ground your generators, using their ground terminal (don't know about Hondas, but my Yamahas have a separate ground point on their frame) and a good, deeply planted ground rod?
AirsDream is offline   Reply With Quote
Old 05-31-2013, 09:55 AM   #3
Rivet Master
 
Buttercup's Avatar
 
1977 27' Overlander
1954 25' Cruiser
1990 34.5' Airstream 345
VC Highlands , Nevada
Join Date: Mar 2005
Posts: 2,151
Send a message via Skype™ to Buttercup
In most Honda portable gas generators the neutral circuit is not bonded to the frame of the generator or to the earth ground lead; and are commonly called Floating Neutral generators. The floating neutral configuration is common for applications such as connection to a recreational vehicle and connection to home power where the transfer switch does not switch out the neutral to ground connection.

Even if you bond the trailer to the ground connection on the generator, you still do not have a Neutral Bonded setup. So, the fault detector is likely seeing that.



In a Floating Neutral system, trailer occupants are not endangered by electrocution from current going to ground since the ground wire and the neutral wire are not bonded at the generator bus, the equipment grounding wire does not offer a path for the fault current to complete the circuit back to the generator windings. In effect an open circuit, current will not travel it and so the fault current does not even go to ground. The figure above, illustrates why that is the case.

At my house, I have a 240-120 volt, 7kva step down transformer powering the trailer when it is parked. I set this up so that I could run the AC at home when I need and doing that through an extension cord on 120 volt outlet causes too much voltage drop...blah, blah, blah. My point is that this transformer is an isolation transformer and as such I do not have a neutral bonded to earth ground even though the ground wire of the trailer is bonded to the ground of my electrical system of my house. The nature if the electrical isolation of my primary and secondary windings of my transformer prevent a path for current to flow through the ground of my trailer. It also is a floating neutral in this case.

__________________
Buttercup's Web Site. WBCCI #17330, 11281 & 7830. VAC Past President, TAC NV-2 & NV-3
Buttercup is offline   Reply With Quote
Old 05-31-2013, 10:25 AM   #4
"Cloudsplitter"

 
2003 25' Classic
Houstatlantavegas , Malebolgia
Join Date: Jun 2007
Posts: 20,000
Images: 1
Quote:
Originally Posted by pjmoser View Post
I have a digital circuit tester that I keep plugged into an ac receptacle in my trailer. When I use my Honda 2000 generators (either in both in tandem or a single solo) I get a ground fault alarm on the tester. I have tried connecting the ground terminals of each generator together and to the body of the trailer. The alarm sounds even when the trailer is insulated from earth - stabilizers raised, hitch jack raised, truck and trailer on rubber tires.
I use a "dog bone" adaptor when using our 2000i...


You need to put a short jumper wire between the ground and neutral in the end that plugs into the generator.

The fault your seeing isn't a safety concern, it's done just so the circuit won't show a fault when a tester is applied.

Bob
__________________
I’m done with ‘adulting’…Let’s go find Bigfoot.
ROBERT CROSS is offline   Reply With Quote
Old 05-31-2013, 10:34 AM   #5
3 Rivet Member
 
Currently Looking...
Austin , Texas
Join Date: Mar 2008
Posts: 213
Bob has it right. Built-in Surge Guard or Progressive EMS will also show an error code. The remote on the Progressive has a bypass switch but the better way is make up a plug with the jumper wire between ground and neutral. Plug into one of the two 20 amp receptacles on the Honda or Yamaha and the error goes away. You only need one plug even if you are using 2 generators in parallel.
pattonsr is offline   Reply With Quote
Old 05-31-2013, 03:31 PM   #6
Rivet Master
 
2005 19' Safari
GLENDALE , AZ
Join Date: Aug 2004
Posts: 2,453
Quote below is from Honda EU2000i Generator Owners Manual. There is no need to worry about a ground fault indication using regular AC circuit testers.

==========

Ground System

Honda portable generators have a system ground that connects generator frame components to the ground terminals in the AC output receptacles. The system ground is not connected to the AC neutral wire. If the generator is tested by a receptacle tester, it will not show the same ground circuit condition as for a home receptacle.
Phoenix is offline   Reply With Quote
Old 04-18-2014, 08:26 AM   #7
3 Rivet Member
 
2014 23' Flying Cloud
2015 28' Flying Cloud
Kalamazoo , Michigan
Join Date: Oct 2012
Posts: 102
I hope you guys understand all this???? My take away is... it's safe to use the generators despite the error indicator, right?
mwilliamsmd is offline   Reply With Quote
Old 04-18-2014, 08:44 AM   #8
Rivet Master
 
aftermath's Avatar
 
2006 25' Safari FB SE
Spokane , Washington
Join Date: Sep 2009
Posts: 1,858
Yes
aftermath is offline   Reply With Quote
Old 04-18-2014, 09:00 AM   #9
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,672
Another way of stating all this is in your home, neutral is bonded to safety ground and also connected to a ground rod at the meter. Thus the power system is referenced to earth ground and a shock hazard to earth ground exists. The generator system, as explained by buttercup, is a floating neutral, not referenced to ground either safety ground or earth ground and thus there is no shock hazard as long as the isolation is maintained. But also as pointed out by several, some analyzers will detect the lack of a bond between the neutral and ground.

Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 10-10-2015, 02:48 PM   #10
1 Rivet Member
 
chasgail's Avatar
 
2007 23' Safari SE
Sacramento , California
Join Date: Feb 2006
Posts: 12
Thanks for the info - great forum, bunch of brainiacs willing to share good data so we all sleep a little better. Much appreciated.
chasgail is offline   Reply With Quote
Old 10-10-2015, 05:30 PM   #11
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by pjmoser View Post
I have a digital circuit tester that I keep plugged into an ac receptacle in my trailer. When I use my Honda 2000 generators (either in both in tandem or a single solo) I get a ground fault alarm on the tester. I have tried connecting the ground terminals of each generator together and to the body of the trailer. The alarm sounds even when the trailer is insulated from earth - stabilizers raised, hitch jack raised, truck and trailer on rubber tires.
When the trailer electrical cord is plugged into the generator, the ground wire from the trailer is connected to the ground terminal on the generator through the receptacle and plug. Connecting the ground terminal to the trailer in another way does not ground anything. Possibly, contact to earth, otherwise known as ground, can be accomplished through the jack or stabilizers, but this is not reliable. Possibly, in an older trailer with a copper plumbing a ground could be accomplished through the water system, though it would not be reliable.

If you want the whole system to be grounded while the generator is connected to the trailer, you must connect the ground terminal of the generator to an earth ground. A wire connected from the generators ground terminal and mechanically fastened (clamped) either to a ground rod driven into the earth or to a metal water pipe partially buried in the earth will do this. I think (not sure) grounding using this method will correct the issue with your tester and also the ground fault breakers and GFCI receptacles will function properly.
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 10-10-2015, 05:35 PM   #12
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
Ground fault using generators

An earth ground will not correct the fault reading on the fault detector.

Only bonding the ground and neutral will do this, but this "fix" is neither desirable or necessary.

The best fix is to ignore the fault reading while on generator.


Brevi tempore!
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 10-10-2015, 05:47 PM   #13
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
Davidson County , NC Highlands County, FL
Join Date: Aug 2006
Posts: 4,493
Quote:
Originally Posted by J. Morgan View Post
An earth ground will not correct the fault reading on the fault detector.

Only bonding the ground and neutral will do this, but this "fix" is neither desirable or necessary.

The best fix is to ignore the fault reading while on generator.


Brevi tempore!
Will the ground fault breakers and GFCI receptacles function if your advice is taken?
__________________
Alan
2014 Silverado LTZ 1500 Crew Cab 5.3L maximum trailering package
A W Warn is offline   Reply With Quote
Old 10-10-2015, 06:40 PM   #14
"Cloudsplitter"

 
2003 25' Classic
Houstatlantavegas , Malebolgia
Join Date: Jun 2007
Posts: 20,000
Images: 1
Question

Quote:
Originally Posted by J. Morgan View Post
The best fix is to ignore the fault reading while on generator.
Brevi tempore!
Really....how would you know if you actually had a ground fault?....



I'll use my genetically modified doggie bone...TYVM.



Bob
__________________
I’m done with ‘adulting’…Let’s go find Bigfoot.
ROBERT CROSS is offline   Reply With Quote
Old 10-10-2015, 07:31 PM   #15
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
http://www.noshockzone.org/generator...utral-bonding/


Brevi tempore!
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 10-31-2015, 05:40 PM   #16
cmipilot
 
1975 27' Overlander
Flower Mound , Texas
Join Date: Jun 2008
Posts: 14
Am I missing something obvious here or isn't modifying the "dog bone" going to require cutting off the factory end and replacing it to provide access for the jumper wire you're proposing?
cmipilot is offline   Reply With Quote
Old 10-31-2015, 07:45 PM   #17
Rivet Master
 
J. Morgan's Avatar
 
1972 31' Sovereign
1975 31' Excella 500
Currently Looking...
Benton , Arkansas
Join Date: Mar 2013
Posts: 5,868
Images: 11
No, you plug it into the spare generator receptacle.

However, IMHO, it is a total waste of effort, but I reserve the right to be wrong.


Brevi tempore!
__________________
The fact that I am opinionated does not presuppose that I am wrong......

J. Morgan is offline   Reply With Quote
Old 10-31-2015, 08:14 PM   #18
Rivet Master
 
Msmoto's Avatar
 
2015 30' International
2009 27' FB International
2007 25' Safari
Currently Looking...
Greensboro , North Carolina
Join Date: Aug 2008
Posts: 1,564
Images: 135
Ground fault

Every time I fire up my Northern Tool 4000w electric start generator which is sitting on the ground, it triggers the ground fault breaker to trip on my Serenity.

My plan is to have the generator connected to a good ground, possibly a five foot heavy chain, or even a copper pole in the ground to see if this can be eliminated. It is frustrating to have to reset this each time I use the generator.
__________________
Happy trails and Good Luck
Ms Tommie Fantine Lauer, Greensboro, NC
AIR #31871 KQ3H

www.fantinesvoice.com
Msmoto is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 12:59 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.