Old 06-15-2006, 06:09 AM   #29
Images: 59
I believe jcanavera (post #15) and FrenchBern (post #22) have identified the problem. You have some kind of neutral to ground leakage. Turning off the circuit breakers doesn't prove anything; all that does is disconnect the hot legs.
My opinion: whoever told you to clip the ground connection is an ***ot that is trying to kill you.
Old 06-15-2006, 09:51 PM   #30
Retired Moderator
john hd's Avatar
1992 29' Excella
madison , Wisconsin
Images: 40
ditto that!
take that jackson center dog bone and throw it away! then hope your dog does not retrieve it!
i cannot believe some one at the factory would even suggest such a silly idea as a connector without a ground!
the person who reccomended that should be fired!
the problem is in your cord or your breaker box. take it to some one or hire someone that is qualified to repair your trailer properly before someone gets hurt!
most likely the paper insulation strip that prevents neutral wires from touching the case of your breaker box has been punctured. or some dummy grounded the neutral buss bar with too long of a screw!
john
you call them ferrets, i call them weasels.
Old 06-15-2006, 10:11 PM   #31
_
hi john, mark, garry and others....
i really value your guidance on this issue.....
to be clear the factory didn't suggest the groundless adapter....
a licensed electrican did....
i'm sure the liability control meeting in jc regularly remind the tech support folks NOT to suggest any gimmicks....
but what the factory DID suggest is just as silly......
"go to rv parks that don't have gfci outlets"
is pretty close to the exact words they offered.....
"a gfci cannot be plugged into a gfci....it will trip"
was the jc technical jargon.....honest.
never mind that others in the same park with the same setup had no issues..
i considered the cord, so i purchased 2 new ones......without help....
well they are new and look nice, but still the gfci trips...
my thoughts were a long screw, worn insulation, a loose wire and so on...
or a bad breaker....
the factory would not confirm any of these possibilites.....
and did not support the dealer service department chasing these issues...
in other words i don't think they authorized the service time?
they (factory folks)just repeated 'no gfci plugged into a gfci'.....
or the park box must be bad....
i'd be useless pulling breakers myself or messing with the wiring.... i am still within warranty and plan to go back to jc and have them trace and find the faulty connection.....but not for 3-4 months.....
and i will post whatever is found.....
when its found.
with pictures.
thanks again....
2air'
Old 06-16-2006, 09:24 AM   #32
crowbar68's Avatar
1975 27' Overlander
fort wayne , Indiana
gnd neutral leakage
reading some of these other posts. you may still have a ground loop. like someone suggested that your neutral bar and ground bar may be bonded at your camper panel. this should not be. you can ring it out w/ a ohm meter. you should get a open reading (high resistance) if you get a low resistance (0) that would be your problem.meter is between gnd and neutral. when doing this have camper disconnected from land pwr.
crowbar68 is offline   Reply With Quote
Old 06-16-2006, 03:30 PM   #33
2005 30' Classic
Images: 12
2Air,
I couldn't resist getting in on the electrical puzzle in an effort to bring this down a few notches on the technical scale.
A few months ago I was installing new wiring for shore power in my í66 Safari. I bought a new and larger panel box to accommodate the newly added circuits, and discovered that it did not have a separate ground bus. I asked a licensed electrician how to deal with this issue, and he told me to put both the ground and neutral on the same bus (i.e. metal connection).
When I connected to shore power, the Ground Fault Interrupt (GFI) breaker in my house, tripped.
I created my own ground bus and separated the neutrals from the ground, reconnected to power, and everything worked.
Needless to say, I lost confidence in the electrician and consulted my hunting buddy, who has worked 10-15 years as an Onan technician. When I told him the advice I had received, and that it had tripped a breaker, he immediately told me that I had a GFI somewhere in the shore power. I didnít ask further, as the problem was solved, but he seemed to imply (i.e. donít take this one to Vegas and bet on it) that the electricians advise would have worked if a GFI was not involved??!
What I hear others saying is that your neutral (normally white wires) and ground (normally green wires) are not completely separate.
For example, if your panel box is grounded (and it should be), and a neutral touches the panel - then the breaker on the shore line will trip. Realize if this is the case, that the breaker tripping could be intermittent, depending on the sureness of the connection/contact. This could be the case if the proper hardware was not used/installed to keep the wiring from rubbing against the panel box where the wire enters the box.
Calvin
GetOutDoors is offline   Reply With Quote
Old 06-16-2006, 05:13 PM   #34
ga501's Avatar
1956 26' Crusier Overlander
douglasville , Georgia
Hi SPiffy,
The electrician you talked to is apparently used to wiring HOUSES
the 'old' fashion way. Until the code changed a while back, that's how
in was done....all grounding conductors and neutrals terminate on the same
buss. When the code changed, these conductors are required to be separate, on differant ' buss ' bars, with the supplied bonding screw
discarded. The additional 'grounding bar' has to be purchased
separately. They can be bought in any Home Depot or Lowes.
Also, when these wires were tied to the same 'bar' a breaker or gfci
would trip if another gfci was plugged into the protected circuit.
I agree there has to be a 'bonding' issue some where in the trailer and it
was a good idea to separate the wires in your panel...make sure the bonding screw is removed (should be a green screw on the neutral bar).
Good luck!Steve
ga501 is offline   Reply With Quote
Old 06-18-2006, 10:05 AM   #35
crowbar68's Avatar
1975 27' Overlander
ground loop
the only place your ground and neutral are bonded is at the service panel (were power comes in off the street) and that is it. by code. even w/ gfi's. any were else and the neutral needs to be isolated.
lol
crowbar
Old 07-22-2006, 12:50 PM   #36
davidz71's Avatar
1986 25' Sovereign
Southern Middle , Tennessee
2air,
I was tripping the GFIC at a local campground and found it was due to a bad 30 amp plug. There was some sort of short inside. A maintenance man who worked in a factory was on the site next to me. Little did I know, while he was looking at it he hooked up a jumper wire from neutral to ground. While this may work in a house, it does not work with GFIC circuits. I replaced the plug head and it still tripped the campground breaker. I even bought romex wire, bypassed my electrical hose reel and wired straight into the fuse box. Still no go. I came back home and connected into the garage GFIC with a 15 amp dogbone and it still tripped. I looked at my wiring diagram and found an extra wire, the jumper he had wired in. I disconnected from shorepower, pulled out the jumper wire and everything started working fine. It was in the 30 amp plug all along and replacing it fixed my problem.
Craig
AIR #0078
3.73 rear end
Mag-Hytec rear diff cover
Amsoil synthetics all around
Old 07-22-2006, 01:38 PM   #37
_
Originally Posted by crowbar68
hey 2air! was wondering if your problem was fixed? were you able to get rid of your dog bones?
hi crowbar68 and craig....
lots of good advice given here and i appreciate it. also i saw your posts in the other thread but moved my reply over here...where most of the info resides...
i do suspect that a ground2neutral short is somewhere in the breaker box or 30amp connector....or in any of the many wiring connections....
in salem at the international rally, a/s had factory techs....doing repairs and service. they installed new tank sensors on my trailer and committed to inspecting my wiring for this issue....
they never got to it...to much other work to do....also i suspect they knew this might take several hours of testing and investigating....
so i plan to swing by the factory in the fall
and stay there until this issue is resolved
i'm not electrically skilled, don't want to hire a non a/s tech for this issue...
it's still under warranty, so i'm gonna ask them to solve the issue.
perhaps the new a/c that was installed twice last summer, has a screw into something it shouldn't, or perhaps the breaker box has a loose wire or the 30 amp connector has worn a short into the wiring....
hope to report back positively and definitively in the fall.., until then i carry the bone!
thanks for asking guys..
2air'
Old 07-23-2006, 10:36 AM   #38
crowbar68's Avatar
1975 27' Overlander
warranty
it definetly sounds like your on the right track. if it's under warranty i would let them handle as well. i had a buddy who did a small electrical side job w/ a gfci involved. it was basic few plugs. he did the job and the gfci would not hold at all. i went out to help trouble shoot. long story short ( 3 1/2 hrs) we found he tightened a connector to hold the romex in the box so much it bit into the neutral and essentially grounded it! sound familiar. we ripped his whole little side job apart to find this. and i got a fat steak dinner out of it. simple but hard to find.
when are you going to the factory? i don't live to far from their and thought about doing the tour and some repairs but i need to get more info. on repairs and such. keep me posted. i'm sure they will be able to repair.
crowbar
Old 07-23-2006, 10:41 AM   #39
crowbar68's Avatar
1975 27' Overlander
lol laughing now
lol
crowbar
i just realized lol means Laughing Out Loud! i thought it was Lots Of Luck! to many abbreviations. i hope i didn't offend. i'm laughing now!
crowbar
Old 10-04-2006, 08:36 PM   #40
_
hello all u electrically minded readers...
time to update this thread
and the news is good!
to recap, since august 05 i've not been able to properly plug in
at any campground with a gfci on the shore pole.
the nanosecond the 3 prongs touched connnections,
the gfci would trip...click...no juice.
initally my a/s service dept was told by the factory folks that
a 'gfci could not be plugged into a gfci' ------- so find other parks for camping...
PLEASE! how many ways is THAT advice nonsense?
while in salem the a/s factory guys told me the same thing....yep to my face.
anyway several here suggested a neutral2ground short somewhere in the trailer...
ah but where? and why? and how to find it?
eventually i learned the proper way to isolate the fault was pull each breaker,
then using a voltmeter touch each ground and neutral,
eventually finding the 'open circuit' with the fault.
then each outlet/connection on that circuit would need evaluation.
not only could this take hours, my only experience with electricity is using it!
so while in j/c last week the factory guys finally agreed to bird dog this issue...basically as described above. potentially an all day event.
what did they find?
open circuit was on the a/c breaker...
basically there is a junction box inside the air conditioner housing where the unit wiring is joined to the trailer wiring....
and the cover plate on this junction box had been overtightened in such a way as to pinch/short the neutral wire insulation...
viola! the short was found! recall this started in august 05?
that was when the same factory service department,
installed a new (the 3rd ) air conditioning on my trailer...
seems the short they found was a short they caused!
oh well, these things happen, and i'm just glad they found the problem! i was not imagining this problem! i am properly grounded again!
i can now retire the j/c dogbone (c post #27) since the n/g short cause by j/c in the a/c was found at j/c!
so even the factory finest can short circuit occasionally....
cheers and thanks for reading!
2air'
Old 10-04-2006, 08:42 PM   #41
Images: 59
So, alls well that ends well, thanks for your patience, sorry about the inconvenience; be sure to come back when you're looking for another travel trailer.
Old 01-22-2008, 04:41 PM   #42
crowbar68's Avatar
1975 27' Overlander
wahoo
thanks for the update. an easy problem not easily found! the gfi was working properly.
" If everything is working, something is wrong ! "
Black water problems Rob Waste Systems, Tanks & Totes 3 08-31-2002 08:34 PM
Shower head problems Pahaska Our Community 25 08-26-2002 11:43 AM
Fridge Cooling Problems 68International Refrigerators 6 07-10-2002 04:53 PM
Lighting problems ramoore53 Electrical - Systems, Generators, Batteries & Solar 1 05-08-2002 11:02 AM