extension cord rated for 20 amps?

My 69 Overlander is 200 ft from my house.
I'm trying to decide whether to hardwire an outlet from house or try and find an extension cord rated for 20 amps and 200 feet.
The question is-will the cost of 200 ft of 12 gauge wire be more than an extension cord?
And - is a rating for 20 amps sufficient (I will not run AC with extension cord-just lights and recharge 12 V battery)-
if I have to get over 10 gauge, then coiling a cord gets a little difficult.


hmmmm.
Any suggestions? (I know solar is an option...)
I'd like to explore the extension cord route.
Martha is offline   Reply With Quote
Old 02-24-2003, 01:10 PM   #2
Still Working
 
smily's Avatar
 
1994 36' Classic 36
North Charleston , South Carolina
Join Date: Jul 2002
Posts: 1,686
Images: 19
yes

either way is suitable for lights only and maybe some low receptacle use.

Definitely do not attempt to run Air Con from this distance without the 10 guage wire.

Sounds like you may be leaving this connection in place for a while so I would probably use some 10 AWG romex cable, (house cable).

If you dont mind the extra expense, some UV rated cable might be in order.

I use a 100 foot extension cord all of the time. 12 AWG

smily
smily is offline   Reply With Quote
Old 02-24-2003, 02:24 PM   #3
Rivet Master
 
Chas's Avatar
 
Austin , Texas
Join Date: Oct 2002
Posts: 949
Images: 22
Probably the easiest way to do it is get some db cable (direct burial) which is basically the grey UV rated stuff that smily is talking about. You would be better off burying it but you could get by leaving it on top of the ground until lawnmowing season starts again, which was last week until this arctic blast hit us last nite, thanks a bunch you Canadians!! Personally if I was going thru the trouble I would run some grey PVC conduit and pull in the #10 (or even #8 conductors) and do a proper 30 amp weathertite campground style box. Summer will be here soon enough and you know how miserable it can be without a/c which will be nice while you are fixing up your Overlander. If you need any more hints you can pm me, I was a commercial electrician for a number of years.

Chas
Chas is offline   Reply With Quote
Old 02-24-2003, 04:57 PM   #4
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
wire size

based on a 3% voltage drop, 30 amps at 120 v. aluminum conductor would require #1 awg for direct burial.

i used this

seems a bit conservitive to me, what do you think chas?

our house services at that length are usually 1/0 aluminum.

john
john hd is offline   Reply With Quote
Old 02-24-2003, 05:07 PM   #5
Rivet Master
 
Chas's Avatar
 
Austin , Texas
Join Date: Oct 2002
Posts: 949
Images: 22
#1??

Major overkill!!

I will find my Ugly book and see what it has to say. I have been wanting to put an outlet out by my storage slab anyways, the #10 SO cord is getting a bit old.

Chas
Chas is offline   Reply With Quote
Old 02-24-2003, 05:11 PM   #6
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
i thought so!

chas

all my books are in the job shack (wells cargo) for the apprentices.

that site was the best i could do for now...

i think 5% voltage drop would be more realistic!

john
john hd is offline   Reply With Quote
Old 02-24-2003, 06:48 PM   #7
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
overhead!

chas,

i think the solution would be a couple of 40' poles and a span of #2 triplex with a #4 neutral!

waddya think?

john
Attached Thumbnails
Click image for larger version

Name:	light_11.jpg
Views:	275
Size:	62.8 KB
ID:	1602  
john hd is offline   Reply With Quote
Old 02-24-2003, 07:52 PM   #8
Rivet Master
 
Chas's Avatar
 
Austin , Texas
Join Date: Oct 2002
Posts: 949
Images: 22
That's the way my old man would have done it!!

Actually not a bad idea, that triplex can carry a lot of load. I lean towards the more unobtrusive approach.

What ya doin' up that pole? Gettin' free cable?

Chas
Chas is offline   Reply With Quote
Old 02-24-2003, 07:59 PM   #9
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
free cable? i wish!

chas,

doing a government job for a buddy, new yard light fer the farm!

john

P.S. underground is great until you have to find it or fix it!
john hd is offline   Reply With Quote
Old 02-24-2003, 08:27 PM   #10
Rivet Master
 
RoadKingMoe's Avatar
 
2001 34' Limited
The State of , Ohio
Join Date: Sep 2002
Posts: 1,605
Images: 23
Don't you have to put buried down 3'? And can't you put sat/cable TV and/or telephone 2' above it? That would make it easier to find with a metal detector.
__________________
Maurice
RoadKingMoe is offline   Reply With Quote
Old 02-24-2003, 08:58 PM   #11
4 Rivet Member
 
Join Date: Feb 2002
Posts: 334
Images: 3
wiring method

I've done this task a few times. Any wiring enclosed in the proper size and schedule may in fact lay on the earth surface. Some places require any conduit/raceway be burried at a minium of 24 inches over a roadway. Pcv conduit schedule 40 is very cheap and wiring can be upgraded and repair is not a usual problem. For a long 100 ft run with a load of 30 amps at 120vac, some number 8 conductors of mtw or thhn stranded in a 1 1/2 conduit will be great. Conduit is not to be filled more than 60%, but big is better. I'm not a fan of direct buriel except for lanscape liting. The recepticle pedistal should have a nice pole for mounting equiptment. The circuit powering this circuit needs to be on it's own circuit breakers. Some would demand a gfi breaker. While installing conduit into earth, some tv cable and phone can be dropped too. The ground fault may be installed at either end of wiring........
__________________
Visit Idaho The people are great
FrankR is offline   Reply With Quote
Old 02-26-2003, 11:43 AM   #12
2 Rivet Member
 
Martha's Avatar
 
Join Date: Jan 2003
Posts: 41
Images: 38
Talking uh.....thanks, you guys......

Well, I certainly got a chuckle out of the responses.....
glad to see there is as much debate here as there is in my household regarding what is overkill vs minimum requirements....
(me-overkill; he-minimum)
I was even considering a new pole/meterloop until I priced it here in one- of-the -fastest-growing areas in the US...

fortunately, I followed most of the conversation ....
will consider all of the advice...
and maybe do something if the ground ever thaws out.
See some of ya'll next weekend...
Martha
Martha is offline   Reply With Quote
Old 02-28-2003, 08:40 AM   #13
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,477
So John/Chas,

If I am planning on running wire from my panel in the house through the underground conduit to the garage and I want to pull for the 30a circuit (and be able to maintain voltages) for the Bambi (has A/C). What kind of wire should I insist on or consider if the distance is about 50 feet from the main panel to the outlet taking into consideration an additional 15ft for the connector cable that came with the Bambi to connect it to the outlet I am planning on installing?

Based on the site you posted John, it looks like #8 solid copper. Any comments?

Thanks

Eric
Silvertwinkie is offline   Reply With Quote
Old 02-28-2003, 09:28 AM   #14
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,497
Images: 1
Wire sizes

Consideration must be given to how long a wire is from the circuit breaker panel to the outlet box that will be used.

The maximum distance for a #8 wire, with not more than a 2 % voltage drop at 30 amps is 60 feet. if a #6 wire was used, then a distance of 95 feet is the maximum. A #4 wire can be 150 feet long, and will not have a voltage drop of more than 2 %, at 30 amps.

These are important considerations to keep in mind, when the Air Conditioner will be used.

To make sure that your absoluely safe, check to see how far the outlet is from the circuit breaker panel.

That doesn't cost anything. Replacing an Air Conditioner because the compressor went bad due to operating it at low voltage, is expensive.


Andy
inlandrv.com
airstreamparts.com
airstreamcandy.com
__________________
Andy Rogozinski
Inland RV Center
Corona, CA
Inland RV Center, In is offline   Reply With Quote
Old 02-28-2003, 11:56 AM   #15
Aluminut
 
Silvertwinkie's Avatar
 
2004 25' Safari
. , Illinois
Join Date: Feb 2003
Posts: 10,477
Thanks Andy. I am under 95 feet. Closer to 50 feet to the outlet from my main house panel, and an addtional 15 feet for my yellow factory "hookup" cable.

It looks to me like #6 wire will not only meet my need, but exceed it. I'd rather be safe than sorry.

Regards,

Eric
Silvertwinkie is offline   Reply With Quote
Old 02-28-2003, 03:00 PM   #16
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
sounds good

eric

# 6 sounds good, the site i posted assumes 3% voltage drop.

if you over size it a little, it won't hurt anything and not cost much more.

john
john hd is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Cord replacement, 1959 Tradewind plowboy Electrical - Systems, Generators, Batteries & Solar 16 12-31-2013 04:03 PM
Original 2 prong cord, how do I make it safe? Jabba Electrical - Systems, Generators, Batteries & Solar 21 07-12-2010 02:01 PM
Hot Power Cord GoldFever Electrical - Systems, Generators, Batteries & Solar 7 07-13-2003 05:49 PM
External Power Cord Replacement jstaad Electrical - Systems, Generators, Batteries & Solar 3 01-23-2003 06:16 AM
Phone cord Joan D'Andrea Cabinets, Counter Tops & Furnishings 0 11-02-2002 10:38 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:44 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.