Journey with Confidence RV GPS App RV Trip Planner RV LIFE Campground Reviews RV Maintenance Take a Speed Test Free 7 Day Trial ×
 

Go Back   Airstream Forums > Airstream Restoration, Repair & Parts Forums > Electrical - Systems, Generators, Batteries & Solar
Click Here to Login
Register Vendors FAQ Community Calendar Today's Posts Search Log in

Reply
 
Thread Tools Search this Thread Display Modes
 
Old 07-04-2006, 11:24 AM   #1
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
ELECTRICIANS (or others knowledgeable) please help.

These are photos of the MARINCO Easy Lock power INLET used on current AIRSTREAMS.

We will install the same device on my 1976 Argosy.

The Marinco cordset , which you run from here to city or park power, is rated 30A 125v 2 pole, 3 wire.

My question is this:

What type wire should I run from the back of the device, thought the trailer, and up to the Main Breaker?

(The wiring will run through the belly pan and up through a closet to the Main.)

Same wire as the cordset? What gauge?

Somebody suggested #8 Cab Tire, 4 wire. Too much or correct?

Thanks for helping.

Sergei
Attached Images
  
SmokelessJoe is offline   Reply With Quote
Old 07-04-2006, 11:40 AM   #2
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
three conductor 10 gauge type SO or equivilent would work well. very similar to the cord set.

don't forget a strain relief clamp where it enters the breaker box.

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 07-04-2006, 02:53 PM   #3
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
Thanks John.

The suggestion for #8 cab tire, 4 wire came from an electrician friend who hasn’t seen the trailer.

I’m guessing that is overkill. Am I right?

Could there be any advantage to it?

Sergei
SmokelessJoe is offline   Reply With Quote
Old 07-04-2006, 03:01 PM   #4
2 Rivet Member
 
Join Date: May 2005
Posts: 64
Images: 3
Quote:
Originally Posted by SmokelessJoe
... from an electrician friend who hasn’t seen the trailer?

Could there be any advantage to it?
You consulted a good electrician. He did not see how far your extenstion cord would need to be, and recommended the safest thing for your Airstream. He might go with John if he/she thinks the distance is not too far.

BTW, my extension cord is 8 gauge.
joatmon is offline   Reply With Quote
Old 07-04-2006, 03:03 PM   #5
2 Rivet Member
 
Join Date: May 2005
Posts: 64
Images: 3
Quote:
Originally Posted by john hd
three conductor 10 gauge ...
Home improvement stores sell it as "two conductor with ground"
joatmon is offline   Reply With Quote
Old 07-04-2006, 03:06 PM   #6
2 Rivet Member
 
Join Date: May 2005
Posts: 64
Images: 3
Quote:
Originally Posted by SmokelessJoe
.. 4 wire came from an electrician friend who hasn’t seen the trailer.

I’m guessing that is overkill. Am I right?...
4 wire is a good idea for future expansion, but only two conductors plus ground will be used for your current Airstream.
joatmon is offline   Reply With Quote
Old 07-04-2006, 03:22 PM   #7
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
Joatmon:

Thanks for all the information.

Things electrical baffle me and I’m getting confused again.

From the layman’s perspective, if the 30A cords MARINCO sells to fit their 30A inlets are 10 gauge (they are, apparently) what then would be the advantage of going #8 from the inlet box to the Main Breaker?

You are suggesting that John meant to write 2 CONDUCTOR, 3 wire, #10; not 3 CONDUCTOR, right?

Thanks again for the help.

Sergei
SmokelessJoe is offline   Reply With Quote
Old 07-04-2006, 03:37 PM   #8
2 Rivet Member
 
Join Date: May 2005
Posts: 64
Images: 3
Voltage drop

Quote:
Originally Posted by SmokelessJoe
... what then would be the advantage of going #8 from the inlet box to the Main Breaker?

You are suggesting that John meant to write 2 CONDUCTOR, 3 wire, #10; not 3 CONDUCTOR, right?
If an extension cord is too long, the electricity will suffer a voltage drop. This voltage drop could hurt your air conditioner if not accounted for. You have not posted the distance your Airstream is from shore power, so I can not comment on the right wire gauge. Your electrician friend probably has a similar sentiment. Post distances, and you may get better answers.

John is a Lineman, and knows what he talking about. Although he is a better reference than me (he does this stuff for a living), I stand behind my wording of "Two conductors plus ground".
joatmon is offline   Reply With Quote
Old 07-04-2006, 04:25 PM   #9
Rivet Master
 
bhayden's Avatar
 
1978 24' Argosy 24
Woodinville , Washington
Join Date: May 2006
Posts: 682
Images: 10
No disagreement on the wire. Never hurts to go heavier but I can't see that you need it. The big question is what sort of insulation. I assume you're going to run stranded wire and not solid? Extra insulation is I think a prudent measure in this application. I think your choices are going to be 300V and 600V and I'd go with the 600V. For extra protection and just to make life easier you might want to go with a "cord set" type wire where there's insulation and some additional mechanical strenght containing the wire bundle. The reason for the extra insulation is the movement it's going to see via flex and vibration. Chances are you'd be doing this more as a favor for the next owner but your piece of mind over the next few decades is worth something.
bhayden is offline   Reply With Quote
Old 07-04-2006, 04:50 PM   #10
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
Quote:
Originally Posted by joatmon
Home improvement stores sell it as "two conductor with ground"
that would be correct!

phase neutral ground... 3 wires 2 conductors and a ground.

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 07-04-2006, 06:19 PM   #11
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Quote:
Originally Posted by john hd
that would be correct!

phase neutral ground... 3 wires 2 conductors and a ground.

john
Sergei,

I would go with a marine grade cable. The stranding is finer, providing more surface area for the electrons to fow and it is softer and easier to work with than the standard household wire that you get at the big box stores. I agree that 8 guage is overkill and not necessary. If you plan to run an outdoor cord longer than 50', I would consider going to 8 guage for that cord to deal with the voltage drop. I have tables to calculate the drop for different wires and I can look it up if you like. Let me know.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 07-04-2006, 07:54 PM   #12
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
Mission accomplished

Thanks to everyone for your help with this. Combining your advice, I’ve been able to see what I should do.

Most of you understood that I was talking about REWIRING my trailer, not an extension cord. I plan to buy a MARINCO cordset to fit the new inlet.

Tomorrow I’m going to buy #10 Cab Tire, 3 wire. I’m wondering now whether “cab tire” might be Canadian usage for what you are calling 600V or SO.

It’s a heavy duty, flexible, rubber covered, indoor-outdoor, waterproof kind of wire, something like welder’s cable.

I should have you all know that I’m only running the wiring through out the trailer. I don’t want to waste an electrician’s time with that and I want poking through the aluminum shell done my way.

In the end, I will have a Master Electrician come by to connect the outlets and hook up the panel.

Many of the interior panels have been removed so he/she will be able to see the runs.

Thanks again to everyone. Mission accomplished in one day.

(I wish the wiring would go as fast).

Sergei
SmokelessJoe is offline   Reply With Quote
Old 07-04-2006, 10:09 PM   #13
Retired Moderator
 
john hd's Avatar
 
1992 29' Excella
madison , Wisconsin
Join Date: Aug 2002
Posts: 4,644
Images: 40
Quote:
It’s a heavy duty, flexible, rubber covered, indoor-outdoor, waterproof kind of wire, something like welder’s cable.
that is perfect!

john
__________________
you call them ferrets, i call them weasels.
john hd is offline   Reply With Quote
Old 07-04-2006, 11:23 PM   #14
Rivet Master
 
bhayden's Avatar
 
1978 24' Argosy 24
Woodinville , Washington
Join Date: May 2006
Posts: 682
Images: 10
Welding Cable

Quote:
Originally Posted by SmokelessJoe
It’s a heavy duty, flexible, rubber covered, indoor-outdoor, waterproof kind of wire, something like welder’s cable.
Welder's cable is very good stuff. You may want to check out a welding supply outfit. Likely as good or better price than a hardware store and you'll get top quality stuff like Carol/Belden/etc. Welding cable is fine stranded for extra flexibilty and the insulation is designed to be tough and impervious to all manner of solvents.
bhayden is offline   Reply With Quote
Old 07-05-2006, 08:29 AM   #15
Rivet Master
 
1975 29' Ambassador
Reno , Nevada
Join Date: May 2003
Posts: 1,351
Keep in mind that the fittings on most breaker boxes work best with solid wire, not stranded. Most internal RV wiring is 14/2 Romex solid stuff just like used in houses for the shorter runs.

Putting stranded wire in fittings not designed for it is not a good idea. They tend to loosen and that can cause poor connections and heat.

Wire sizing is a matter of length and maximum load. The typical 10g for 30A RV service is for 30'. You can find some charts somewhere I think. For the short run from plug to box inside the trailer, 12g would probably do but larger sizes provide a safety margin - as long as the fittings fit the wire type and size! Both the box and the plug are designed for a wire size range and type and best results are obtained if you make sure that your wire is within its spec.
bryanl is offline   Reply With Quote
Old 07-05-2006, 08:55 AM   #16
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
Bryan:

Thanks a lot.

We used 12 gauge BX armored cable thought-out.

Could I just use a 10-gauge run of that from the inlet box, through the belly pan area, up to the Main?

If we use stranded cable, which the consensus here supports, could we use a soldered or clamped on lug were the wire connects to the main panel?

Sergei
Attached Images
 
SmokelessJoe is offline   Reply With Quote
Old 07-05-2006, 09:05 AM   #17
Rivet Master
 
bhayden's Avatar
 
1978 24' Argosy 24
Woodinville , Washington
Join Date: May 2006
Posts: 682
Images: 10
Breakers for use in a house type box are made to snap onto a rail (bus) and for solid wire. There are panels, like for boats that don't do this and are designed to be more mechanically robust and provide a better contact in an environment like a boat. They have scew terminals and are designed for use with ring lugs. Crimp on lugs are good IF you buy quality crimps (I like nylon over PVC insul but both can be good) AND you use the right tool to crimp the lugs. The right tool is a ratcheting crimper, not the cheap "pliers" that you get at the auto parts store with an assortment of crimps.

PS Don't use stranded wire in a breaker designed for solid. Or vice a versa for that matter.
bhayden is offline   Reply With Quote
Old 07-05-2006, 10:22 AM   #18
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
Bryan and Bernie,

Good advise about keeping stranded wire in stranded design breakers. The problem with solid wire is that in an RV situation where it is getting bumped and vibrated constantly, it eventually work hardens and breaks. I have found numerous electrical problems on RV's that were caused by a solid copper run that had broken from flexing and vibration.
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 07-05-2006, 12:39 PM   #19
Rivet Master
 
1975 29' Ambassador
Reno , Nevada
Join Date: May 2003
Posts: 1,351
Lew, the problem also exists with people who solder to tin a wire to go under a lug or to solidify a crimp. Soldering is not usually a good idea for wire under a screw or anywhere near a flexing situation.

RV's are usually wired internally with household fixtures, sockets, boxes, wire, and circuit protection. These usually age fairly well. It is the interface from the internal in the wall stuff to the external world where there is more exposure to flexing and bumping and other abuse that causes problems.

Many Airstreams going back to the indedependent Airstream company era (60's) have original solid A/C house wiring in good condition.

One should also note that the 110 VAC wiring and the 12 VDC wiring have significant differences in rules, codes, practices, policies, equipment, colors, materials, insulation, and so on.
bryanl is offline   Reply With Quote
Old 07-05-2006, 12:44 PM   #20
Rivet Master
 
SmokelessJoe's Avatar
 
1976 Argosy 24
now being enjoyed by Heath and Mary in , Vermont
Join Date: Sep 2005
Posts: 1,432
Bryan:

Can I use a 10-gauge run of BX armored wire from the inlet box, through the belly pan area, up to the Main?
SmokelessJoe is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help! Resistor on fan switch Sav'h Steve Electrical - Systems, Generators, Batteries & Solar 22 12-20-2003 08:01 AM
Safe from Lightning in an Airstream? maggieairstream Our Community 21 07-22-2003 04:18 PM
New Argosy owner! barbwire All Argosy Trailers 33 04-15-2003 07:14 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 10:13 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.