Old 09-15-2017, 10:00 PM   #41
1 Rivet Member
 
1955 22' Flying Cloud
1962 26' Overlander
2011 30' Flying Cloud
East Jordan , Michigan
Join Date: Mar 2015
Posts: 13
Suggest use only 1 adapter - 50A to 20A
Klondike is offline   Reply With Quote
Old 09-15-2017, 10:35 PM   #42
4 Rivet Member
 
dasams's Avatar
 
Palm Desert , California
Join Date: Jul 2016
Posts: 301
Quote:
Originally Posted by mikeinca View Post
If I understood him correctly, his explanation was that power would be bridged on the other side of the converter, so it didn't matter if only one side of the 50amp circuit was hot.
As a new owner of a 50 amp AS, I've been trying to understand the wiring and my two AC's. I even started a thread about it. See http://www.airforums.com/forums/f37/...cs-172273.html

When I plugged into the 50 amp service where we are staying, I also attached my EMS-PT50X so that I could monitor the current. With the zone 1 AC running, there were ~20 amps on L-1 and ~3 amps on L-2. The second reading was interesting as I had read that the zone 2 AC was the only thing powered from L-2. Apparently not as the zone 2 AC was off but L-2 was pulling some amps. And I realize that AS has changed the wiring over the years.

I have the same Camco dogbone mentioned above and I'd like to do an experiment. If I have some downtime tomorrow, I'll switch to 30 amp service and put the EMS between the dogbone and the 50 amp cable to see which legs are hot. Any other ideas for a test run?

Thanks, Dave
__________________
2006 Cayenne S with V8, air suspension, factory tow
2018 FC 27 FB
2017 FC 25 RB Gone
dasams is offline   Reply With Quote
Old 09-16-2017, 06:46 AM   #43
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
The converter does not bridge the AC, and is powered from a single 20 amp breaker, 8 on mine , and does supply the entire DC distribution. That may be the L2 load.
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Old 09-16-2017, 09:50 AM   #44
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Quote:
Originally Posted by james.mileur View Post
The converter does not bridge the AC, and is powered from a single 20 amp breaker, 8 on mine , and does supply the entire DC distribution. That may be the L2 load.
Hi

.... so, if the Camco converter only powered up L1 and not L2, you would have no converter.....You also might not have the microwave if it also was on the other leg.

Bob
uncle_bob is online now   Reply With Quote
Old 09-16-2017, 11:11 AM   #45
4 Rivet Member
 
dasams's Avatar
 
Palm Desert , California
Join Date: Jul 2016
Posts: 301
30 Amp Test

Well I conducted my little test using the Camco 55185 dogbone referenced in post #32 above.

I plugged the dogbone into the 30 amp pedestal and then plugged in my EMS-PT50X and then the 50 amp cable. See the picture below.

Here are the test numbers and no I didn't try to run both AC's while on 30 amp service.

1. No AC: L1 = 12 amp, L2 = 5 amp
2. Zone 1 AC: L1 = 18 amp, L2 = 3 amp
3. Zone 2 AC: L1 = 15 amp, L2 = 15 amp.

I think this makes it pretty clear that the dogbone provides power to both legs of the 50 amp cable and that you can run either of the AC's.

If I had a do over, I would have turned off the elec water heater as I think it was pulling power through L-1 during the first and third tests. This is just a guess but I can't think of anything else to explain currents. Thoughts?
Attached Thumbnails
Click image for larger version

Name:	IMG_2835.jpg
Views:	75
Size:	274.9 KB
ID:	295012  
__________________
2006 Cayenne S with V8, air suspension, factory tow
2018 FC 27 FB
2017 FC 25 RB Gone
dasams is offline   Reply With Quote
Old 09-16-2017, 11:34 AM   #46
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,655
Blog Entries: 1
I see no problem with a 30 amp/50 amp adapter being wired so both legs of the 50 amp are connected. Because you never use 240v. there is no conflict with phase. As long as you remember that you still only have 30 amps available.
30 amp has a positive, neutral, and ground so the positive goes to BOTH + spades of the 50 amp, then the neutrals are connected and so are the grounds.
Attached Thumbnails
Click image for larger version

Name:	30-50ampDogbone.jpg
Views:	69
Size:	26.3 KB
ID:	295021  
Mollysdad is offline   Reply With Quote
Old 09-16-2017, 11:37 AM   #47
3 Rivet Member
 
Currently Looking...
belen , New Mexico
Join Date: Jan 2012
Posts: 191
I plug my 41 foot diesel pusher into a 110 outlet at two of our homes and can run one a/c plus the charger inverter. its all trial and error and common sense. In AZ I installed the 50 amp plug since we use it as a guest cottage and need to run both a/c in the summer.
alantbird is offline   Reply With Quote
Old 09-16-2017, 11:42 AM   #48
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,655
Blog Entries: 1
Quote:
Originally Posted by dasams View Post
I plugged the dogbone into the 30 amp pedestal and then plugged in my EMS-PT50X and then the 50 amp cable. See the picture below.

Thoughts?
I'm curious, did the EMS-50 show any odd readings? Since both legs were the same phase?

Your EMS 50 is chained to your ladder? But not the pedestal?
Mollysdad is offline   Reply With Quote
Old 09-16-2017, 12:09 PM   #49
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
I used the same 30 - 50 dog bone and EMS 50 for a couple months with no issues.

from my antique Note3 - James
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Old 09-16-2017, 12:55 PM   #50
Rivet Master
 
mikeinca's Avatar

 
2020 25' Globetrotter
Santa Rosa , California
Join Date: Feb 2017
Posts: 1,846
Images: 2
Quote:
Originally Posted by dasams View Post
Well I conducted my little test using the Camco 55185 dogbone referenced in post #32 above.

I plugged the dogbone into the 30 amp pedestal and then plugged in my EMS-PT50X and then the 50 amp cable. See the picture below.

Here are the test numbers and no I didn't try to run both AC's while on 30 amp service.

1. No AC: L1 = 12 amp, L2 = 5 amp
2. Zone 1 AC: L1 = 18 amp, L2 = 3 amp
3. Zone 2 AC: L1 = 15 amp, L2 = 15 amp.

I think this makes it pretty clear that the dogbone provides power to both legs of the 50 amp cable and that you can run either of the AC's.

If I had a do over, I would have turned off the elec water heater as I think it was pulling power through L-1 during the first and third tests. This is just a guess but I can't think of anything else to explain currents. Thoughts?
Dave, my only thought is that perhaps you could send your results to Rich at Camco and get him squared away on this!

Seriously, thanks for resolving my questions about the adaptor.
__________________
Mike

2020 25' Globetrotter Twin | 2024 GMC Sierra 2500HD Denali Ult. 4x4 Duramax
400Ah Battle Born lithium battery string | 580W solar (400W roof 180W portable)
mikeinca is offline   Reply With Quote
Old 09-16-2017, 01:01 PM   #51
4 Rivet Member
 
dasams's Avatar
 
Palm Desert , California
Join Date: Jul 2016
Posts: 301
Quote:
Originally Posted by Mollysdad View Post
I'm curious, did the EMS-50 show any odd readings? Since both legs were the same phase?
No odd readings or any other issues.

Quote:
Originally Posted by Mollysdad View Post
Your EMS 50 is chained to your ladder? But not the pedestal?
Ha Ha! Good one! It's now wrapped around the pedestal but the smallest of bolt cutters will be able to liberate it. More importantly for security, I've covered the readout with blue tape so that it's a bit more stealthy at night. Those red LED's shout "here I am, take me away".
__________________
2006 Cayenne S with V8, air suspension, factory tow
2018 FC 27 FB
2017 FC 25 RB Gone
dasams is offline   Reply With Quote
Old 09-17-2017, 06:56 AM   #52
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Hi

For what ever reason, the EMS boxes do not look at the L1 / L2 for the presence of 240V. I'm not wild about that since on a 50A circuit it can be a problem. I understand the issue of it tripping out on a 30A adapter and why they did it that way.

The current meter functions on an EMS are fairly simple in terms of accuracy. Is it 15A or 16A? is not the sort of question they are designed to answer. If you start to work out what's what by turning things on and off, this may fake you out a bit. You will turn on a minor load and it will not report with enough accuracy for you to see what happened. A proper current meter is a much better way to get into minor details. They are fine for looking at big loads and spotting open wires.

Bob
uncle_bob is online now   Reply With Quote
Old 09-17-2017, 07:41 AM   #53
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
Uncle bob, I called my EMS company to verify what they advertised as "accidental 240v". They verified it senses if the ground is missing and/or if the outlet is wired as 240 vice 2 single 120v legs.

Found this great summary for everyone that is still unclear.

http://www.rv-dreams.com/rv-electrical.html
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Old 09-17-2017, 07:47 AM   #54
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
What I use.
EMSPT50C Surge Protector https://www.amazon.com/dp/B004AQR53K..._GYNVzb6RMR24J
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Old 09-17-2017, 09:00 AM   #55
Rivet Master
 
Mollysdad's Avatar

 
2017 26' Flying Cloud
Tampa , Florida
Join Date: Feb 2017
Posts: 7,655
Blog Entries: 1
Quote:
Originally Posted by james.mileur View Post
I called my EMS company to verify what they advertised as "accidental 240v". They verified it senses .. if the outlet is wired as 240 vice 2 single 120v legs.
Sorry for beating a dead horse, but there is no difference in wiring an OUTLET in 240 or 2(120). The trailer's wiring determines the 2 (120).
Mollysdad is offline   Reply With Quote
Old 09-17-2017, 09:13 AM   #56
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Hi

Ok, back to the basics of the 50A connector.

1) You have a ground lead that should have no current on it in normal circumstances.

2) You have a neutral wire that is rated for 50A. Both the wire and the connector have this rating.

3) You have two hot leads each rated at 50A. Again both wire and connector have this rating.

If you had a DC circuit and put 50A into each of the hot leads, it all goes back out the neutral. That gives you 100A on a 50A wire. There are never fuses or breakers in a neutral. The problem would go un-detected. The wire (or connector) heats up and insulation melts. Next comes sparks and flames.

If you set up the two hot leads in phase, the neutral works just like a DC circuit. You overload the thing and bad stuff happens.

Fortunately it's AC and you have another option. You can change the phase of one of the hot leads. If the two currents are 180 degrees out of phase they cancel out. You get zero current down the neutral. Full load on one side and zero load on the other gives 50A down the neutral. That's ok, it's rated for 50A. When the two hots are 180 degrees out of phase a voltmeter will read 240V between them.

The AS its self could care less about in phase or out of phase once you get to the breaker panel in the trailer. Up to the panel, (inside and outside) it cares very much about phase if you are running > 50A into the trailer.

At least on my EMSTP50C, it's quite happy plugged into a 30A circuit through a normal dog bone adapter. In that case everything is in phase. It's also well below 50A, so no problem. I'd love to see some sort of LED flashing if it's in phase. I don't need it to disconnect. Just give me a sign all is not right ....

Lots of fun !!

Bob
uncle_bob is online now   Reply With Quote
Old 09-17-2017, 09:57 AM   #57
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,223
Images: 9
Airstream was usually able to wire the two A/C units to have one on each hot leg. Not mentioned above is that the factory inverter will be drawing power most of the time to keep the battery bank charged and or run the 12Vdc lights, refrigerator logic board, furnace logic board and water heater logic board plus all the other passive parasite 12Vdc loads.

So one needs to do a little testing to determine which leg has the water heater, the microwave and the power outlets. If both A/C units are running and the the wife wants to run a hair dryer (typically 1,800 watts or 15 amps), then knowing which additional appliance needs to be secured will prevent tripping the breakers.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 09-17-2017, 12:47 PM   #58
Rivet Master
 
2014 20' Flying Cloud
Sag Harbor , New York
Join Date: Jun 2015
Posts: 17,523
Quote:
Originally Posted by switz View Post
. . .
Not mentioned above is that the factory inverter will be drawing power most of the time . . .
. . .
Don't you mean converter?
OTRA15 is offline   Reply With Quote
Old 09-17-2017, 03:09 PM   #59
Rivet Master
 
mikeinca's Avatar

 
2020 25' Globetrotter
Santa Rosa , California
Join Date: Feb 2017
Posts: 1,846
Images: 2
Key learnings (for me at least) from this thread so far:

The Camco 55185 30A/M < 50A/F dogbone will work in combination with a 30A/F < 15A/M dogbone to get power from an AC outlet as well as allow access to 30A power at an RV park without 50A service. It also seems that I should acquire a surge protector for 50A service and the Progressive Industries units seem like a popular choice; the EMS-PT50X being the latest version from what I've read.

Also, there is a single 50A < 15A adaptor that plugs directly into the trailer which will allow a normal heavy duty extension cord to provide power without having to use the 50A monster supply cable. This seems like an attractive option.

So one more question. If I use the 50A < 15A adaptor/extension cord setup to plug in to the 20A duplex circuit at my house, is a surge protector still required/desirable? If so, given the lower current involved could a regular 15A strip type surge protector be used? That would seem to be preferable to using the EMS-PTX50, presumably with multiple adaptors again involved.
__________________
Mike

2020 25' Globetrotter Twin | 2024 GMC Sierra 2500HD Denali Ult. 4x4 Duramax
400Ah Battle Born lithium battery string | 580W solar (400W roof 180W portable)
mikeinca is offline   Reply With Quote
Old 09-18-2017, 05:13 AM   #60
ObviouslyKnot
 
james.mileur's Avatar
 
Currently Looking...
KAILUA , HI
Join Date: Nov 2016
Posts: 862
Quote:
Originally Posted by Mollysdad View Post
Sorry for beating a dead horse, but there is no difference in wiring an OUTLET in 240 or 2(120). The trailer's wiring determines the 2 (120).
Well, fwiw, the old 3 wire 240 outlets for dryers/ovens that didn't have a neutral and with some electricians (I'm sure not uncle bob) who used the white lead and a piece of black tape for the second (white) hot lead from the second 120v breaker, results in a situation that could give a diy rv'r 240 to his new 30 rv outlet if, black tape was gone, he didn't understand how 240 comes through two leads (white & black), and didn't voltage check his new outlet, hooked up white to white, black to black, ground to ground, and no EMS in line.

Ka-pow, fizzle, puff of smoke, stink, buy all new converter, appliances, etc.

Or the trailer burns up in the driveway.

So, no dead horse, just burnt trailer 120v system. [emoji6]
__________________
James Mileur, HY80-2-Al,
2017 Classic Twin, 2016 RAM 3500 Megacab, ProPride hitch
james.mileur is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 Amp to 15 Amp Adapter to House Power Question Steamboatbob Batteries, Univolts, Converters & Inverters 39 08-08-2018 10:58 AM
Connecting 30 amp cord to 15 amp circuit Matth57 Batteries, Univolts, Converters & Inverters 8 06-21-2017 09:25 AM
Connecting TV to House Sound in Interstate stast01 Audio, Video & TV 0 10-26-2016 12:07 PM
Service snafu $&!&& and which battery is which amirm Sprinter and B-van Forum 25 07-04-2016 09:19 PM
Connecting to a house jpsuttoniii Full-Timing 2 04-16-2013 02:44 PM