Can I hook up to the home wiring?

Can I hook up my Sport 22 to my home wiring if I employ a 30 amp breaker on the wiring? I am asuming the wiring is the standard 20 amp wiring used for residential building. the house was built three years ago. I do have a generater but I am wanting t hook up to the house once in awhile. I do understand that I need to change out the connection box to mate with my RV extension chord.
Thanks,
Mike
TexasVine is offline   Reply With Quote
Old 10-26-2015, 06:16 AM   #2
Rivet Master
 
IanPoulin's Avatar
 
2021 25' International
Full timer , Virginia
Join Date: Oct 2012
Posts: 665
Images: 4
Yes; and if you don't plan on using any high amperage gear, such as the heat pump, you can get a 20A plug to 30A input converter and just run via weatherproof extension cord.

If you want to wire up a genuine 30A camper plug, make sure the electrician knows NOT to make it 220v as some may believe they need to do for that type of plug.
__________________
2024 Airstream Globetrotter 30RB
2022 Ford F350 Lariat Diesel
WBCCI 4CU 8118
IanPoulin is offline   Reply With Quote
Old 10-26-2015, 07:25 AM   #3
Rivet Master
 
1977 31' Sovereign
1963 26' Overlander
1989 34' Excella
Johnsburg , Illinois
Join Date: Jul 2005
Posts: 2,944
house wiring

The normal house wiring uses 14 gauge for 20 amp service. If you run a line and install a 30 amp breaker in the central box and an RV 110 volt box on the outside of the house, I would recommend you use 10 gauge wire. Then, you can use your air conditioner at home. If you are not going to use your air conditioner, I would suggest you simply by a 30 amp RV to 20 amp dogbone adapter and plug into the normal outlet on the house.
dwightdi is offline   Reply With Quote
Old 10-26-2015, 08:04 AM   #4
Rivet Master
 
TG Twinkie's Avatar
 
1974 Argosy 26
Morrill , Nebraska
Join Date: Nov 2009
Posts: 6,014
Images: 2
Blog Entries: 5
Can I hook up to the home wiring?

Dwightdi

Correction: #14 wire is rated at 15 amps. #12 wire is rated at 20 amps. #10 wire is rated at 30 amps.
Do not increase the circuit breaker size above the capacity of the wire or the receptacle. Most homes have 15amp receptacles. 20 amp receptacles have one slot that looks like a "T" lying sideways.


Sent from my iPod touch using Airstream Forums
TG Twinkie is offline   Reply With Quote
Old 10-26-2015, 08:14 AM   #5
Rivet Master
 
dznf0g's Avatar
 
2007 30' Classic
Oswego , Illinois
Join Date: Jul 2010
Posts: 13,669
Images: 5
Understand that the gauges listed above are dependent upon the length of the run as well. My 30A RV circuit was approx 45 feet from the box, which (IIRC) was right on the cusp of requiring 8ga wire. So I went that route. I actually went with 6ga....but that was only because the store was out of 8ga.

This was my second 30A RV circuit, as I poured a pad on the far end of the house. My first one was on the drive and a shorter run. That curcuit is only about 20 feet and 10ga was used.
__________________
-Rich-

"If the women don't find you handsome, they should at least find you handy." - Red Green
dznf0g is offline   Reply With Quote
Old 10-26-2015, 09:16 AM   #6
3 Rivet Member
 
TexasVine's Avatar
 
2021 27' International
Fredericksburg , Texas
Join Date: Oct 2015
Posts: 239
Blog Entries: 1
Thank you everyone for the responses. Not the answers I wanted to hear but the truth will keep me from making a mistake. I will now run the power off the barn instead where I have the correct wiring
TexasVine is offline   Reply With Quote
Old 10-26-2015, 09:25 AM   #7
Rivet Master
 
bwoodtx's Avatar
 
1997 30' Excella
1961 26' Overlander
1954 22' Flying Cloud
1981 28' Airstream 280
San Antonio , Texas
Join Date: Jul 2009
Posts: 1,436
As long as you do not run the A/C you can run off the house circuit. You can run the fridge,lights, tv and even a small fan. We do this when we are cooling down the fridge for a trip.
__________________
Bruce
WBCCI# 9259 AIR# 38927 TAC-TX 14
Stop Littering-Spay & Neuter-- Adopt From Rescue
No amount of time will erase the memory of a great dog.
bwoodtx is offline   Reply With Quote
Old 10-26-2015, 09:32 AM   #8
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
Our AC will run on the low setting but not high when plugged into a 15 amp 110 vac outlet.
nrgtrakr is offline   Reply With Quote
Old 10-26-2015, 09:55 AM   #9
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 6,408
Images: 2
Blog Entries: 2
If you ONLY want to run the cONVERTER, a 15 AMP circuit is sufficient.

If you want to use the AS as additional space, wire a 50 AMP circuit. That way you will be "prepared" for any "upgrades"...
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 10-26-2015, 10:39 AM   #10
Rivet Master
 
Larry C's Avatar
 
1996 34' Excella
Elberta , Alabama
Join Date: Oct 2006
Posts: 837
Blog Entries: 1
Quote:
Originally Posted by nrgtrakr View Post
Our AC will run on the low setting but not high when plugged into a 15 amp 110 vac outlet.

Just to be on the safe side, when you are running your a/c on the low setting, feel the wire, and the 30/15amp adaptor and make sure they aren't getting hot.

Just sayin'

Larry
Larry C is offline   Reply With Quote
Old 10-26-2015, 11:54 AM   #11
New Member
 
2016 28' International
Englewood , New Jersey
Join Date: Oct 2015
Posts: 1
Be certain not to exceed the capacity of your main breaker box.

I recommend adding a subpanel adjacent to where you will be parking.

Also a good comment to follow above... Wire sub panel for 110 not 220.

If you are going to the trouble of adding a sub panel; go for 50 amps with two receptacles 30 and 50. You may wish to run two AC units if you get a larger rig - the additional cost is minimal.
Steventancer is offline   Reply With Quote
Old 10-26-2015, 01:08 PM   #12
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
Quote:
Originally Posted by Larry C View Post
Just to be on the safe side, when you are running your a/c on the low setting, feel the wire, and the 30/15amp adaptor and make sure they aren't getting hot.



Just sayin'



Larry

Yep ... and the extention cord if using one.
nrgtrakr is offline   Reply With Quote
Old 10-26-2015, 02:42 PM   #13
Rivet Master
Airstream Dealer
 
Inland RV Center, In's Avatar
 
Corona , California
Join Date: Feb 2002
Posts: 16,497
Images: 1
We have used a "pocket reference book" published by Sequoia Publishing, for many years.

The following is a small wire chart, 1 page out of 864 pages that lists all kinds of charts, scales and you name it.

These numbers are the maximum total length, including the present city power cable, subtracting the 25 foot USA cable. These numbers are for a 3 wire flexible cable.

The 36 foot coach cable length has been subtracted, therefore the following is the maximum length of an extension cord, that can be added, using a maximum of a 2 percent voltage drop.

If you want to be super safe with the current draw, the minimum wire size that should then be used, is a #8 3 conductor wire. If more current is used higher than the below numbers, then a voltage drop greater than 2 percent will occur. When that happens, running the AC, as an example, could cause the breaker to blow, because when the voltage goes down, the current increases, which could ruin the compressor. As the chart shows, using a extension cord of #8 wire, not more than 35 feet long, is the best overall. That size would allow a 30 amp draw for a distance of 60 feet, a 35 foot extension cord and the 25 foot cable from the coach. It's a MUST that you also add the current draw from the Univolt, and anything else that you may turn on, plus the current draw from the AC

For 20 amps, #12 wire no extension
#10 wire 21 feet
# 8 wire 54 feet
# 6 wire 104 feet

For 25 amps, #10 wire 9 feet
# 8 wire 36 feet
# 6 wire 79 feet

For 30 amps, #10 wire 2 feet
# 8 wire 24 feet
# 6 wire 59 feet

Andy

__________________
Andy Rogozinski
Inland RV Center
Corona, CA

Inland RV Center, In is online now Report Post
__________________
Andy Rogozinski
Inland RV Center
Corona, CA
Inland RV Center, In is offline   Reply With Quote
Old 10-26-2015, 02:49 PM   #14
Rivet Master
 
SuzyHomemakr's Avatar
 
1972 29' Ambassador
Boynton Beach , Florida
Join Date: Dec 2013
Posts: 568
We installed this spiffy Midwest box with a 30A breaker and plug. It's worked great. We kept on throwing the 20A breaker with the feeble extension cord.
Attached Thumbnails
Click image for larger version

Name:	2015-10-26 16.43.43.jpg
Views:	94
Size:	96.9 KB
ID:	251074  
SuzyHomemakr is offline   Reply With Quote
Old 10-26-2015, 04:07 PM   #15
Regular Guy
 
NavyCorpsman's Avatar
 
1978 31' Sovereign
Hot Springs , Arkansas
Join Date: Aug 2014
Posts: 603
Whatever the Amperage, AWG and length of the run, always check for voltage drop. NEVER let it go beyond 10%.
NavyCorpsman is offline   Reply With Quote
Old 10-26-2015, 05:14 PM   #16
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 6,408
Images: 2
Blog Entries: 2
Quote:
Originally Posted by NavyCorpsman View Post
Whatever the Amperage, AWG and length of the run, always check for voltage drop. NEVER let it go beyond 10%.

While under load.
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 10-26-2015, 05:24 PM   #17
Rivet Master
 
Wayne&Sam's Avatar
 
2014 25' Flying Cloud
Cuddebackville , New York
Join Date: May 2007
Posts: 4,346
Images: 21
Quote:
Originally Posted by Inland RV Center, In View Post
For 20 amps, #12 wire no extension
Well, I don't get that. It doesn't consider the length of the #12 in the house. If that is within limits, a #12 extension cord could certainly be used to the #12 limit.

In a house built in the past 30 years or so outlets are 20 amp with #12 wire.
__________________
2014 25' Flying Cloud Rear Twin
2019 Ford Expedition Platinum
Wayne&Sam is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
My Hook Things Won't Hook Sbb Rock Guards, Segment & Window Protectors 2 04-12-2015 06:16 PM
Wiring Tradewind power hook-up smith135 Electrical - Systems, Generators, Batteries & Solar 14 11-04-2009 08:38 AM
Hook up OR Not Hook up while camping purman Boondocking 29 08-18-2009 06:42 PM
How to hook up 30 amp to my home mtccollins Electrical - Systems, Generators, Batteries & Solar 9 11-23-2006 09:01 AM
Wiring Sequence to hook up 2 x 6 volt battery pack to your 12 volt trailer battery TobyJH Batteries, Univolts, Converters & Inverters 0 05-21-2004 12:04 AM