Old 05-29-2013, 08:31 AM   #15
4 Rivet Member
 
2008 16' Safari
Destrehan , Louisiana
Join Date: May 2009
Posts: 395
Great; you can run two SEPERATE 120 vac 30 amp curcuits.
You may not use two outlets to provide power to a single trailer.
L1 - Neutral = 120 vac
L2 - Neutral = 120 vac
Neutral to Ground = 0 vac
BUT :
L1 to L2 will always be 240 VAC
__________________

__________________
dlb435 is offline   Reply With Quote
Old 05-29-2013, 06:16 PM   #16
Rivet Master
 
VeggieBullet's Avatar
 
1973 31' Sovereign
2007 20' Safari SE
Vintage Kin Owner
Wesley Chapel , Florida
Join Date: Oct 2011
Posts: 879
Quote:
Originally Posted by dznf0g View Post
So, I have a 4 prong 240V outlet for an electric stove (unused, I have gas) right on the other side of the garage wall. What do I do to convert it to a 30 amp, 120V RV outlet if I moved it through the wall?
any pics of the outlet?
__________________

__________________
Still One Nation under GOD
2 chronicles 7:14
VeggieBullet is offline   Reply With Quote
Old 05-29-2013, 08:50 PM   #17
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
1999 34' Excella
Davidson County, NC , Highlands County, FL
Join Date: Aug 2006
Posts: 2,567
Quote:
Originally Posted by dznf0g View Post
So, I have a 4 prong 240V outlet for an electric stove (unused, I have gas) right on the other side of the garage wall. What do I do to convert it to a 30 amp, 120V RV outlet if I moved it through the wall?
Safety First! If you do not know how, you should get a qualified electrician to do this for you.

If I were in your situation, I would remove the 4 prong outlet (relocate wires as needed) and use the existing wire to feed a small 240v sub-panel. If the existing wire is to short you might add a junction box and extend this set of wires to where you would like the sub-panel to be. Add a 30 amp single pole GFCI breakers to the sub-panel to feed a 120v 30amp RV outlets. You could add additional 120v circuit breakers if you need more than one outlet. You can extend the wires from the sub-panel to where ever you want the outlets, if at a different location. #10-2 copper with ground will carry the load of 120v 30 amp, if you are not extending a long distance.

edit: to be legal the person doing the work must be licensed and a permit is required.
edit 2: I assumed the existing outlet for a stove is 30 amp 240v. If the breaker controlling this wire is less than 30 amp double pole it will not work.
__________________
Alan
2014 Silverado 1500 Crew Cab 5.3L maximum trailering package (yes, I'm towing the 34')
A W Warn is online now   Reply With Quote
Old 05-29-2013, 10:28 PM   #18
Rivet Master
 
A W Warn's Avatar
 
2000 25' Safari
1999 34' Excella
Davidson County, NC , Highlands County, FL
Join Date: Aug 2006
Posts: 2,567
Quote:
Originally Posted by VeggieBullet View Post
thanks for all the replies, as always Airforums is a great community!!
Well the whole issue here is that we have a generator cord rated 30AMP 240 (4prongs) and we were wondering if we can use that cable & install a 30Amp 240V Outlet to have 2 trailer plugged with full 30Amp.
I see that there is still a split decision whether "yes" and "no".
We are planning on installing a 50AMP 240 and have the "Y" adapter to 2 30Amps 120V but since we have the generator cord that could save us a ton of funds that can be very useful for some aluminum...
If you are installing a 50 amp circuit, you should add a sub-panel with breakers, not a 50 amp plug with a splitter adapter. You probably could rig something using that 30 amp cable that would work, but it might be dangerous.
1. You should get a qualified electrician to do the work if you are modifying any portion of the existing permanent electrical system you are connecting to. Or, if just plugging into an existing outlet, have someone look your work over before you power it up. You could damage your home and/or your trailer.
2. The chord you have for your generator should not be used as permanent fixed wiring inside your house or garage. It is meant to be a temporary drop chord.
3. If you spit the wires on a 240v 50 amp circuit without using breakers to protect any extensions from it, you will have 50 amps on the wires rated for 30 amps. The chord is probably has #10 wire rated for 30 amp.
4. The 240v circuit is protected by a double pole breaker. A 120v circuit extended from a 240v circuit should be protected by a single pole breaker with amp rating no larger than the amp rating the wire extending from it.

PM me if you have additional questions.
__________________

__________________
Alan
2014 Silverado 1500 Crew Cab 5.3L maximum trailering package (yes, I'm towing the 34')
A W Warn is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 07:35 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.