Old 01-21-2016, 06:04 AM   #1
3 Rivet Member
 
2016 28' Flying Cloud
The Plains , Ohio
Join Date: Dec 2015
Posts: 159
30 amp service

I am visiting the Airstream park in Pensacola. It's very nice, and convenient to my visiting my son who lives in Gulf Shores Alabama.
The very nice camp hosts told us to park at any of the sites since most of them were empty. I found a nice pull through site, leveled, unhitched but when I went to connect to shore power, I found it was a 30 amp site. My FC28 is wired for 50 amps but AS provided a 50 to 30 amp adapter. I didn't want the hassle of hooking up and moving to another site and my understanding was that so long as I didn't run both ACs, 30 amp would work.
Well last night I turned on both heat pumps and I also had an electric heater running and lost power. The shore power was dead, and had no circuit breaker on it. Fortunately, my power cord was long enough to reach a shore power plug in the next empty site and using only one furnace, I was able to get through the night.
So was the problem running both heat pumps? Do both heat pumps also need 50 amps like trying to run both ACs? Or was it the additional load of the space heater?
I'm going to see the camp host this morning and see if they can't reset the breaker somewhere. it's ugly having my power cord snaking around the trailer. Or maybe I should bite the bullet and hook up and move to a 50 amp site.
Thoughts?

Richard
whitegs is offline   Reply With Quote
Old 01-21-2016, 06:18 AM   #2
Rivet Master
 
mimiandrews's Avatar
 
1966 22' Safari
Hilltop Lakes , Texas
Join Date: Jun 2008
Posts: 1,767
A heat pump is basically an air conditioner with the freon cycle running backwards. It has the same power requirements as it does when it's being a normal air conditioner. Sorry, you can't run them both on a 30 amp circuit.
mimiandrews is offline   Reply With Quote
Old 01-21-2016, 06:33 AM   #3
4 Rivet Member
 
TRIPPPIN's Avatar
 
2012 25' FB Eddie Bauer
Southwestern Ontario , Ontario Canada
Join Date: Mar 2007
Posts: 307
Images: 6
Send a message via MSN to TRIPPPIN Send a message via Yahoo to TRIPPPIN
You likely cannot run even one Heat pump with an electric space heater and other appliances on too with 30A.
TRIPPPIN is offline   Reply With Quote
Old 01-21-2016, 06:35 AM   #4
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
You are not going to be able to run an electric heater in addition to the heat pump on 30 amp service. In fact, you might be pushing it to even try the hot water heater on electric. That is why you have propane...run the furnace.

Larry
lsbrodsky is offline   Reply With Quote
Old 01-21-2016, 06:40 AM   #5
3 Rivet Member
 
2016 28' Flying Cloud
The Plains , Ohio
Join Date: Dec 2015
Posts: 159
Quote:
Originally Posted by lsbrodsky View Post
You are not going to be able to run an electric heater in addition to the heat pump on 30 amp service. In fact, you might be pushing it to even try the hot water heater on electric. That is why you have propane...run the furnace.

Larry
Live and learn. I just hope I didn't fry the camp's electric outlet.
whitegs is offline   Reply With Quote
Old 01-21-2016, 06:43 AM   #6
Rivet Master
 
mimiandrews's Avatar
 
1966 22' Safari
Hilltop Lakes , Texas
Join Date: Jun 2008
Posts: 1,767
All electrical appliances should have a nameplate on them somewhere that states how many watts are required to run that item. A watt is one volt times one amp. At 120 volts, 30 amps equals 3600 watts. Exceed that, and something's going to blow--hopefully it's the circuit breaker and nothing catches fire.

Suggest you read a few nameplates, especially the heavy stuff like air conditioners, electric heaters, microwaves, and hair dryers, then do the math. You have to budget electricity more so than you do money--there are no lenders available when you use too many watts.
mimiandrews is offline   Reply With Quote
Old 01-21-2016, 08:32 AM   #7
Rivet Master
 
kscherzi's Avatar
 
2013 27' FB International
El Dorado Hills , California
Join Date: Jan 2013
Posts: 2,023
Images: 24
One heat pump/AC eats about 18 to 20 amps of your 30 allowance. The space heater maybe 12 or. Add in lights, fridge, and water heater and the circuit is blown.
kscherzi is offline   Reply With Quote
Old 01-21-2016, 08:35 AM   #8
Rivet Master
 
AnnArborBob's Avatar
 
2014 27' FB Eddie Bauer
Chelsea , Michigan
Join Date: May 2010
Posts: 1,792
Images: 12
Wow! How cold was it in Pensacola that you needed both heat pumps AND the space heater! Did you remember to close the windows???
__________________
Bob Martel
WBCCI# 5766
AnnArborBob is offline   Reply With Quote
Old 01-21-2016, 09:14 AM   #9
Rivet Master
 
dkottum's Avatar
 
2012 25' Flying Cloud
Battle Lake , Minnesota
Join Date: Jun 2009
Posts: 7,714
We have 30 amp service in our Airstream (and one Air conditioner) and it is plenty, when you learn how to manage it.

For heat we bought a small Dyson Hot space heater because it regulates the heat so well, and use the propane furnace to supplement it if too cold. We never use the heat pump, to noisy, hogs too much of the power so few if any other appliances can be used with it, and can provide little heat below forty degrees.

It is also good to have a voltmeter plugged into a 120V electrical outlet. In campgrounds during cold (and hot) weather, other camping units can pull enough power to lower available power. When you hook up to the power you may see a significant voltage drop as you turn your appliances on. If it drops below 112 volts, we shut something off because you're getting near a tripped breaker from too much current draw.
__________________
Doug and Cheryl
2012 FC RB, Michelin 16, ProPride 1400
2016 Ram 1500 Laramie Crew Cab 4X4 Ecodiesel 3.92 axles

The Truth is More Important Than the Facts
dkottum is offline   Reply With Quote
Old 01-21-2016, 09:36 AM   #10
Rivet Master
 
mefly2's Avatar
 
2015 25' FB Eddie Bauer
2013 25' FB Eddie Bauer
2012 20' Flying Cloud
Small Town , *** Big Sky Country ***Western Montana
Join Date: Feb 2010
Posts: 2,860
Quote:
Originally Posted by AnnArborBob View Post
Wow! How cold was it in Pensacola that you needed both heat pumps AND the space heater! Did you remember to close the windows???
ROFL ...
__________________
2015 25' Eddie Bauer Int'l FBQ / 2023 Ford Lightning ER
2022 Ford F350 6.2 V-8; equalizer hitch + Shocker air hitch
Honda Eu3200; AIR# 44105; formerly WBCCI 2015.1
Terminal Aluminitis; 2-people w/ 3+ dogs
mefly2 is offline   Reply With Quote
Old 01-21-2016, 09:58 AM   #11
3 Rivet Member
 
2016 28' Flying Cloud
The Plains , Ohio
Join Date: Dec 2015
Posts: 159
It's been below freezing here the past few days and my lovely wife cannot tolerate the cold
We didn't really need both heaters
whitegs is offline   Reply With Quote
Old 01-21-2016, 01:55 PM   #12
Rivet Master
 
mayco's Avatar
 
1982 31' Airstream 310
champaign , Illinois
Join Date: Oct 2012
Posts: 4,072
A good formula to help calculate your amperage draw....watts devided by voltage = amps.
So a common space heater running at 1500w devided by 120v=12.5 amps draw. We will run two small ceramic heaters at their low setting (750w) without worrying about it.
mayco is offline   Reply With Quote
Old 01-21-2016, 02:10 PM   #13
Rivet Master
 
paiceman's Avatar
 
2020 28' Flying Cloud
Upper St Clair , Pennsylvania
Join Date: Aug 2011
Posts: 2,943
Images: 1
As stated 30 amp will run one heat pump. However, heat pumps are only good down to about 40 degrees F, and then they simply will not warm up to a temperature that you will be comfortable with. We also have 50 AMP and we ran both A/C units most of the summer and time this fall both HP when the temp was 45 degrees in the morning. When temp went below 45 I turned them both off and turned the furnace on. It is much more efficient and warms the trailer up quickly (if it works) our did not for a couple of months, hopefully now fixed under warranty.

Bud
__________________
2020 28' Twin Flying Cloud
2021 F350 6.7 King Ranch
USAF Master Training Instructor (TI) & (MTI)- 68-72
Volunteer K9 Rehabilitator & Trainer
paiceman is offline   Reply With Quote
Old 01-21-2016, 02:30 PM   #14
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,222
Images: 9
In a 2016 with the duct heat system, the heat pumps must first warm up the space between the two sheets of aluminum on the roof and continue to heat that space and metal while blowing some warm air into the trailer. Some folks have been disappointed with the heat pump performance. Below 40 outside, they are going to do much.

The furnace is the best factory installed heating device, but if it runs a lot in a 24 hour period, you might have to refill a 30 pound propane tank every other day.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 01-21-2016, 02:56 PM   #15
Rivet Master
 
dkottum's Avatar
 
2012 25' Flying Cloud
Battle Lake , Minnesota
Join Date: Jun 2009
Posts: 7,714
Two other things that really help on cold nights, sharing the same bed and/or an electric blanket and you will be warm all night long. Save the propane for morning.
__________________
Doug and Cheryl
2012 FC RB, Michelin 16, ProPride 1400
2016 Ram 1500 Laramie Crew Cab 4X4 Ecodiesel 3.92 axles

The Truth is More Important Than the Facts
dkottum is offline   Reply With Quote
Old 01-21-2016, 05:54 PM   #16
2 Rivet Member
 
2005 31' Classic
Pleasant Plains , Illinois
Join Date: Nov 2015
Posts: 55
I'm agreeing with all who said only one heat pump/air conditioner can be operated from a 30 amp service. I've heard that there are often a 13.5 kbtu and a 15 kbtu unit on the Airstreams with two units, but I'm not sure about that.
__________________
Greg & Mary
2005, 31 ft. Classic - 2008 Ford F250
WGreg is offline   Reply With Quote
Old 01-22-2016, 02:31 AM   #17
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,222
Images: 9
The front unit is usually 15K BTU and the (optional on some models) rear is usually 13.5K BTU. In our 23D, the only unit is 13.5K BTU.

Since the foot print and wiring is the same, some folks upgrade the smaller unit to 15K BTU.
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 01-22-2016, 06:35 AM   #18
"Cloudsplitter"

 
2003 25' Classic
Houstatlantavegas , Malebolgia
Join Date: Jun 2007
Posts: 20,000
Images: 1
Thumbs up

'Old School'......





Bob
__________________
I’m done with ‘adulting’…Let’s go find Bigfoot.
ROBERT CROSS is offline   Reply With Quote
Old 01-23-2016, 02:43 AM   #19
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 6,222
Images: 9
Hot and Cold running chambermaids.....
__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic w/ twin beds, 50 amp service, 1000 watt solar system, Centramatics, Tuson TPMS, 12" disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Old 01-23-2016, 08:23 AM   #20
4 Rivet Member
 
2016 30' Flying Cloud
Oviedo , Florida
Join Date: Jan 2005
Posts: 264
Images: 1
I'm rather amazed Mystic Springs has pedestals with no circuit breakers. Since the adjacent pedestal worked, that would either indicate that the pedestals were all home-runned back to a panel with individual breakers, something actually went open in the pedestal or multiple pedestals are wired to a single branch circuit in the panel (thus allowing over current situations on a single pedestal that might exceed the ampacity of the pedestal wiring). The last two possibilities represent safety issues that I'm surprised the county allows a commercial operation to operate with.

When using a 50-30 adapter, you are relying on the pedestal breaker since your trailer has a 50A main breaker that will not trip if you overload a 30A pedestal. There is a safety issue here, especially if you are not using a surge protector that has an under voltage shutoff feature. If the pedestal is not protected by a breaker, you could draw enough current to generate substantial voltage drop (if the CG wiring is marginal) that would damage your appliances.

Out of curiosity, I will look forward to what the CG person tells you.
__________________
Keith & Barb
2016 30' Flying Cloud
2016 Ram 2500 diesel
Southeastern Camping Unit, WBCCI #1675
khollister is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Goucho couch,original am/fm 8 track & lots of wood & aluminum from interior remodel gquailhunter Airstream Classifieds 0 09-19-2015 04:25 PM
Thirty Amp cord for new Fifty Amp service Msmoto Electrical - Systems, Generators, Batteries & Solar 10 06-14-2015 04:58 PM
Airstream 1976 original Service Manual & Owner's Manual, good cond. leong1 Airstream Classifieds 0 11-12-2014 01:44 PM
50 amp to 30 amp only service Pearson422 Electrical - Systems, Generators, Batteries & Solar 13 10-08-2013 08:01 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 09:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.