30 amp service

I am visiting the Airstream park in Pensacola. It's very nice, and convenient to my visiting my son who lives in Gulf Shores Alabama.
The very nice camp hosts told us to park at any of the sites since most of them were empty. I found a nice pull through site, leveled, unhitched but when I went to connect to shore power, I found it was a 30 amp site. My FC28 is wired for 50 amps but AS provided a 50 to 30 amp adapter. I didn't want the hassle of hooking up and moving to another site and my understanding was that so long as I didn't run both ACs, 30 amp would work.
Well last night I turned on both heat pumps and I also had an electric heater running and lost power. The shore power was dead, and had no circuit breaker on it. Fortunately, my power cord was long enough to reach a shore power plug in the next empty site and using only one furnace, I was able to get through the night.
So was the problem running both heat pumps? Do both heat pumps also need 50 amps like trying to run both ACs? Or was it the additional load of the space heater?
I'm going to see the camp host this morning and see if they can't reset the breaker somewhere. it's ugly having my power cord snaking around the trailer. Or maybe I should bite the bullet and hook up and move to a 50 amp site.
Thoughts?

Richard
__________________

__________________
whitegs is offline   Reply With Quote
Old 01-21-2016, 07:18 AM   #2
Rivet Master
 
mimiandrews's Avatar

 
1966 22' Safari
Weatherford , Texas
Join Date: Jun 2008
Posts: 1,425
A heat pump is basically an air conditioner with the freon cycle running backwards. It has the same power requirements as it does when it's being a normal air conditioner. Sorry, you can't run them both on a 30 amp circuit.
__________________

__________________
mimiandrews is offline   Reply With Quote
Old 01-21-2016, 07:33 AM   #3
3 Rivet Member
 
TRIPPPIN's Avatar
 
2012 25' FB Eddie Bauer
South Western Ontario , Ontario
Join Date: Mar 2007
Posts: 170
Images: 5
You likely cannot run even one Heat pump with an electric space heater and other appliances on too with 30A.
__________________
TRIPPPIN is online now   Reply With Quote
Old 01-21-2016, 07:35 AM   #4
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 1,687
You are not going to be able to run an electric heater in addition to the heat pump on 30 amp service. In fact, you might be pushing it to even try the hot water heater on electric. That is why you have propane...run the furnace.

Larry
__________________
lsbrodsky is offline   Reply With Quote
Old 01-21-2016, 07:40 AM   #5
3 Rivet Member
 
2016 28' Flying Cloud
The Plains , Ohio
Join Date: Dec 2015
Posts: 155
Quote:
Originally Posted by lsbrodsky View Post
You are not going to be able to run an electric heater in addition to the heat pump on 30 amp service. In fact, you might be pushing it to even try the hot water heater on electric. That is why you have propane...run the furnace.

Larry
Live and learn. I just hope I didn't fry the camp's electric outlet.
__________________
whitegs is offline   Reply With Quote
Old 01-21-2016, 07:43 AM   #6
Rivet Master
 
mimiandrews's Avatar

 
1966 22' Safari
Weatherford , Texas
Join Date: Jun 2008
Posts: 1,425
All electrical appliances should have a nameplate on them somewhere that states how many watts are required to run that item. A watt is one volt times one amp. At 120 volts, 30 amps equals 3600 watts. Exceed that, and something's going to blow--hopefully it's the circuit breaker and nothing catches fire.

Suggest you read a few nameplates, especially the heavy stuff like air conditioners, electric heaters, microwaves, and hair dryers, then do the math. You have to budget electricity more so than you do money--there are no lenders available when you use too many watts.
__________________
mimiandrews is offline   Reply With Quote
Old 01-21-2016, 09:32 AM   #7
Rivet Master
 
kscherzi's Avatar
 
2013 27' FB International
El Dorado Hills , California
Join Date: Jan 2013
Posts: 1,136
Images: 24
One heat pump/AC eats about 18 to 20 amps of your 30 allowance. The space heater maybe 12 or. Add in lights, fridge, and water heater and the circuit is blown.
__________________
kscherzi is offline   Reply With Quote
Old 01-21-2016, 09:35 AM   #8
Rivet Master
 
AnnArborBob's Avatar
 
2014 27' FB Eddie Bauer
Chelsea , Michigan
Join Date: May 2010
Posts: 1,764
Images: 12
Wow! How cold was it in Pensacola that you needed both heat pumps AND the space heater! Did you remember to close the windows???
__________________
Bob Martel
WBCCI# 5766
AnnArborBob is offline   Reply With Quote
Old 01-21-2016, 10:14 AM   #9
Rivet Master
 
dkottum's Avatar
 
2012 25' Flying Cloud
Battle Lake , Minnesota
Join Date: Jun 2009
Posts: 7,716
We have 30 amp service in our Airstream (and one Air conditioner) and it is plenty, when you learn how to manage it.

For heat we bought a small Dyson Hot space heater because it regulates the heat so well, and use the propane furnace to supplement it if too cold. We never use the heat pump, to noisy, hogs too much of the power so few if any other appliances can be used with it, and can provide little heat below forty degrees.

It is also good to have a voltmeter plugged into a 120V electrical outlet. In campgrounds during cold (and hot) weather, other camping units can pull enough power to lower available power. When you hook up to the power you may see a significant voltage drop as you turn your appliances on. If it drops below 112 volts, we shut something off because you're getting near a tripped breaker from too much current draw.
__________________
Doug and Cheryl
2012 FC RB, Michelin 16, ProPride 1400
2016 Ram 1500 Laramie Crew Cab 4X4 Ecodiesel 3.92 axles

The Truth is More Important Than the Facts
dkottum is offline   Reply With Quote
Old 01-21-2016, 10:36 AM   #10
Rivet Master
 
mefly2's Avatar
 
2015 25' FB Eddie Bauer
Western , ** Big Sky Country ** Montana
Join Date: Feb 2010
Posts: 2,283
Quote:
Originally Posted by AnnArborBob View Post
Wow! How cold was it in Pensacola that you needed both heat pumps AND the space heater! Did you remember to close the windows???
ROFL ...
__________________
mefly2 is offline   Reply With Quote
Old 01-21-2016, 10:58 AM   #11
3 Rivet Member
 
2016 28' Flying Cloud
The Plains , Ohio
Join Date: Dec 2015
Posts: 155
It's been below freezing here the past few days and my lovely wife cannot tolerate the cold
We didn't really need both heaters
__________________
whitegs is offline   Reply With Quote
Old 01-21-2016, 02:55 PM   #12
Rivet Master
 
mayco's Avatar

 
1982 31' Airstream 310
champaign , Illinois
Join Date: Jun 2013
Posts: 2,760
A good formula to help calculate your amperage draw....watts devided by voltage = amps.
So a common space heater running at 1500w devided by 120v=12.5 amps draw. We will run two small ceramic heaters at their low setting (750w) without worrying about it.
__________________
mayco is online now   Reply With Quote
Old 01-21-2016, 03:10 PM   #13
Rivet Master
 
paiceman's Avatar

 
2017 30' Classic
Upper St Clair , Pennsylvania
Join Date: Aug 2011
Posts: 2,433
Images: 1
As stated 30 amp will run one heat pump. However, heat pumps are only good down to about 40 degrees F, and then they simply will not warm up to a temperature that you will be comfortable with. We also have 50 AMP and we ran both A/C units most of the summer and time this fall both HP when the temp was 45 degrees in the morning. When temp went below 45 I turned them both off and turned the furnace on. It is much more efficient and warms the trailer up quickly (if it works) our did not for a couple of months, hopefully now fixed under warranty.

Bud
__________________
SAFE TRAVELS
2017 30' Classic - F350 6.7 Diesel Crew
USAF - Military Training Instructor (TI) - 68-72
paiceman is offline   Reply With Quote
Old 01-21-2016, 03:30 PM   #14
Rivet Master
 
switz's Avatar

 
2014 31' Classic
2015 23' International
2013 25' FB International
Apache Junction , Arizona
Join Date: Sep 2012
Posts: 4,799
Images: 8
In a 2016 with the duct heat system, the heat pumps must first warm up the space between the two sheets of aluminum on the roof and continue to heat that space and metal while blowing some warm air into the trailer. Some folks have been disappointed with the heat pump performance. Below 40 outside, they are going to do much.

The furnace is the best factory installed heating device, but if it runs a lot in a 24 hour period, you might have to refill a 30 pound propane tank every other day.
__________________

__________________
WBCCI Life Member 5123, AIR 70341, 4CU, WD9EMC

TV - 2012 Dodge 2500 4x4 Cummins HO, automatic, Centramatics, Kelderman level ride airbag suspension, bed shell

2014 31' Classic model 30 twin beds, 50 amp service, 900 watt solar system, Centramatics, Dill TPMS, disc brakes, 16" tires & wheels
switz is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Goucho couch,original am/fm 8 track & lots of wood & aluminum from interior remodel gquailhunter Airstream Classifieds 0 09-19-2015 05:25 PM
Thirty Amp cord for new Fifty Amp service Msmoto Electrical - Systems, Generators, Batteries & Solar 10 06-14-2015 05:58 PM
Airstream 1976 original Service Manual & Owner's Manual, good cond. leong1 Airstream Classifieds 0 11-12-2014 02:44 PM
50 amp to 30 amp only service Pearson422 Electrical - Systems, Generators, Batteries & Solar 13 10-08-2013 09:01 AM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:38 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.