20 Amp or 30 Amp, that's the question

Here's one for the experts to noodle out. The main circuit breaker coming into the 110v panel from the shore power is only a 20 amp breaker. Coming out of the panel there are two 20 amp breakers that feed the interior of the camper. One of these 20 amp branch circuits feeds the air conditioner. The other 20 amp branch circuit feeds all of the other 110v outlets.

So the question is, why only a 20 amp for the main, shouldn't it be a 30 amp? Is there any reason why I can't replace it with a 30 amp?

The shop manual isn't much help here. The wiring diagram in the manual shows the circuit layout to be exactly what I have (wiring only). The diagram of the breaker panel (panel only)shows only 2 20 amp breakers, one to the shore power and one to everything else inside the camper (obviously this isn't correct).

As always, thanks for the help!

Jim
__________________

__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 07:17 AM   #2
Well Preserved

 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 20,193
the reason for this is because the air conditioner is completely separate from the rest of the wires. The wiring in the trailer is only supposed to be able to handle 20 amps.
__________________

__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Old 01-21-2008, 07:23 AM   #3
Got gandkids?
 
Jim & Susan's Avatar

 
1973 27' Overlander
'Possum Holler , Georgia
Join Date: Oct 2004
Posts: 5,406
Images: 39
I understand that part of it; the air conditioner should have its own dedicated circuit from the panel. What I don't understand is why the shore power breaker is only 20 amp. If the camper is supposed to be 30 amp, why wouldn't the main breaker be a 30 amp? The mystery continues....
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 07:26 AM   #4
Rivet Master
 
juel's Avatar

 
1976 31' Sovereign
Currently Looking...
Chandler , Oklahoma
Join Date: Oct 2004
Posts: 1,770
Images: 24
My trailer is the same; however, we had an additional plug installed on the AC circuit for use in the winter. Since we have the elect/LP water heater on the other circuit, we were limited in our use of the 20amps. In the winter we use the AC circuit for an electric heater. We have not put in a new furnace and have been hesitant about using the original central heat in the Argosy. Actually we don't use the trailer much in the really cold part of our winters, so with the cat heater and the electric space heater this has worked out well.
__________________
juel is offline   Reply With Quote
Old 01-21-2008, 07:32 AM   #5
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,281
Jim,

Look at the guage of the wire that is feeding the breaker box from the street connection. The breaker on that lead should the wire guage.....20 amp for 12 guage and 30 amp for 10 guage.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 01-21-2008, 07:42 AM   #6
Got gandkids?
 
Jim & Susan's Avatar

 
1973 27' Overlander
'Possum Holler , Georgia
Join Date: Oct 2004
Posts: 5,406
Images: 39
I just went out and checked, the street connection is 10 guage and printed on the wire it reads "30 amp" service. SO that means that I can replace the 20 amp street side breaker with a 30 amp, right?
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 08:06 AM   #7
4 Rivet Member
 
empresley's Avatar
 
1984 34' International
1977 Argosy 24
Central , Georgia
Join Date: Jun 2006
Posts: 491
Images: 15
Our '77 has 10 ga. service wire & 30A main breaker.

The individual circuits are protected at 20A so I (not being an electrician) would feel comfortable changing the main to 30A.

Seems like you should be able to maximize the use of 30A service offered by campsites.
For example:
If you are using the AC (has it's own 20A circuit) and a microwave (let's say 800 watt size) on the receptacle circuit; the 30A main would allow this when the existing 20A may not. right?

Qualified advice is needed here. Amateur electricians can burn things up.

martin.
__________________
Travelers by aluminum roadships, loyalists to one species,
masters of convenience, herdsmen steeped in maintenance and restoration.


empresley is offline   Reply With Quote
Old 01-21-2008, 08:14 AM   #8
Got gandkids?
 
Jim & Susan's Avatar

 
1973 27' Overlander
'Possum Holler , Georgia
Join Date: Oct 2004
Posts: 5,406
Images: 39
Well, I just went back out and looked at things again. Then looked back at the shop manual. Seems things got a little confused here because of a PO's "creative wiring". Let me see if I can explain.

First, there is no "main" breaker facing streetside. The shop manual shows a direct feed from the street to the main buss without a circuit breaker. Then, there are 2 20 amp breakers that feed the two branch circuits described above (one for the air conditioner, one for everything else). This is actually how things are wired in the panel.

Seems a PO rewired things and left an extra 20 amp breaker in there that is not wired to anything.

So I suppose the real question now is, should I rewire the streetside connection so that it actually has a true "main" circuit breaker that can trun the power off coming from the street. Weird.

Jim
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 08:29 AM   #9
4 Rivet Member
 
empresley's Avatar
 
1984 34' International
1977 Argosy 24
Central , Georgia
Join Date: Jun 2006
Posts: 491
Images: 15
Jim,
Considering the age, capacity & limited utilization, I would suggest replacing
with something you can have confidence in.
Try an elec. supply house for a better selection of panels and... I bet you can get a small panel and necessary breakers for under $100. If McDonough doesn't have a large commerical supplier we have several in Macon & I can pick one up for ya.
__________________
Travelers by aluminum roadships, loyalists to one species,
masters of convenience, herdsmen steeped in maintenance and restoration.


empresley is offline   Reply With Quote
Old 01-21-2008, 08:38 AM   #10
Got gandkids?
 
Jim & Susan's Avatar

 
1973 27' Overlander
'Possum Holler , Georgia
Join Date: Oct 2004
Posts: 5,406
Images: 39
I think you're probably right, Martin. The idea of not being able to cut main power at the box isn't very appealing. On the other hand, I could just unplug the dang thing!
__________________
www.nesa.org

Air No. 6427
Jim & Susan is offline   Reply With Quote
Old 01-21-2008, 09:20 AM   #11
Site Team
 
, Minnesota
Join Date: Aug 2003
Posts: 6,940
Images: 59
If the service cord is connected directly to the buss, and the two 20a circuits are connected to the buss, you should install a 30a main breaker.

If the box has room for another breaker, you would install the 30a breaker on the buss, adjacent to the branch service breakers. Then you connect the hot wire from the service cord to 30a breaker.

It may look unusual. It will look like you are running the power "backwards" through the main breaker. This is how it is done.

Be sure that you have the ground and neutral wires separated. Sometimes a PO, or even a residential electrician, will bond the ground and neutrals together.
__________________
markdoane is offline   Reply With Quote
Old 01-21-2008, 10:09 AM   #12
Rivet Master
 
davidz71's Avatar
 
1986 25' Sovereign
Southern Middle , Tennessee
Join Date: Mar 2002
Posts: 3,150
Images: 23
Quote:
Originally Posted by markdoane
...Sometimes a PO, or even a residential electrician, will bond the ground and neutrals together.
This is exactly what happened about 7 years ago when I developed a short in the 30 amp power cord plug. It kept tripping the campground circuit GFIC so a well meaning factory maintenance electrician ran a jumper wire from ground to neutral. It kept tripping the campground circuit even after I replaced the power cord plug. Once home, I compared the breaker box to the schematics in my manual. Funny thing, there was an extra wire in there that was not there before. I know it was not there prior to this incident because I had replaced a 30 amp main breaker and decided to draw a diagram of the wiring just for the heck of it. Fortunately I kept the drawing and it matched the factory diagram. I removed the jumper and everything worked fine.
__________________
Craig

AIR #0078
'01 2500hd ext. cab, 8.1 litre gas, 5 sp. Allison auto
3.73 rear end
Mag-Hytec rear diff cover
Amsoil Dual by-pass oil filtration system
Amsoil synthetics all around
265 watt AM Solar, Inc. system
davidz71 is offline   Reply With Quote
Old 01-21-2008, 10:09 AM   #13
Rivet Master
 
Aerowood's Avatar

 
1971 21' Globetrotter
Arvada , Colorado
Join Date: May 2006
Posts: 2,841
I agree with EMPRESLEY on replacing the whole box with a new box. I am goimg to go a step further on my GT resto, and go with a 50 amp box to add a dedicated circut to the electric portion of the new hot water heater, fridge, and the micro wave, along with the air conditioning circut, and then a GFI breaker for all the regular outlets. The hot water heater will also have a GFI breaker. I am a strong believer in the saying "better to have and not need then to need and not have"

Kip
__________________
Aerowood is offline   Reply With Quote
Old 01-21-2008, 10:57 AM   #14
Well Preserved

 
1993 21' Sovereign
Colfax , North Carolina
Join Date: Jun 2003
Posts: 20,193
The limiting factor in your wiring is the wiring. you can't have more than a 20 amp breaker if the wiring will only handle 20 amps. From the breaker out to the pole the wiring is rated at 30. If you put a 30 amp inside the triler, the 20 amp rated wires will melt before the breaker will trip. The 20 amp main interior breaker is only for the trailer wiring, not the air conditioner, that wiring is completely seperate.
__________________

__________________
Meddle not in the affairs of dragons, for you are crunchy, and taste good with ketchup.
Terry
overlander63 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30 / 50 AMP Question kleimanr Electrical - Systems, Generators, Batteries & Solar 7 11-03-2007 03:58 PM
Car & Driver Jan 07, Airstream & Benz Karyn Airstream "In the News" 14 12-04-2006 11:26 PM
Preztels & Beer or Biscotti & Cappuccino? GreggH Community Polls 26 02-20-2006 07:08 PM
Curb Side & Front Glass Window & Clips Oceancontainer 1965 Safari 2 07-28-2003 08:04 PM
Dumb Question regarding the bed & sheets kamadeca 2003 Safari 8 06-23-2003 03:24 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 04:09 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.