20 amp Breaker Trips when HOT

Symptom: AC will start when 90-deg outside after all day pulling. Within 3-5 mins. the 20a breaker for the AC trips off.

Conundrum: Only happens when it's HOT inside, when you *really need* AC. Runs and runs when it's 70 deg. outside.

Attempted:
1 - Replaced dual 20a breaker with a new one - no joy.
2 - Sanded all connections brite and reconnected - no joy.
3 - Moved AC breaker from left position to right position, trying to keep it cooler - no joy.
4 - Removed, cleaned, replaced AC filter elements inside - no joy.
5 - Left AC filter elements off inside - no joy.

Question: Could a MOD point me to the thread in which someone has solved this problem in the past? And/Or any suggestions for anyone?

I could stop at Out Of Doors Mart Monday to get parts or have service done if all else fails. THANKS!
Attached Thumbnails
Click image for larger version

Name:	PowerBox.jpg
Views:	71
Size:	160.3 KB
ID:	157570  
__________________

__________________
Greg and Linda Heuer
2011 31' Classic Ltd. - The Silver Otter III
2013 GMC Denali 2500HD 6.6 DuraMax
TAC VA-18 | WBAC 1927 - Shen. Valley Unit 149 | AIR 53869
https://www.linkedin.com/in/gheuer
Silver Otter is offline   Reply With Quote
Old 05-06-2012, 06:35 AM   #2
3 Rivet Member
 
kokopat's Avatar
 
Currently Looking...
Hendersonville, NC , North Carolina
Join Date: Sep 2008
Posts: 113
Images: 1
If you had a clamp-on amp meter (not a common tool) you could see how many amps are being pulled by the circuit. If it is close to 20 then it is going to heat up and trip, which is overload condition vs. direct short with trips immediately. Freon issues would cause the internal overload to trip but not the breaker. The air conditioner should be the only thing on that circuit.
Good luck,
Pat
__________________

__________________
kokopat is offline   Reply With Quote
Old 05-06-2012, 07:26 AM   #3
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,306
One thing to consider, when it's only 70 degrees outside, the air conditioner compressor may not even be running; it may just be circulating ambient air. Assuming of course you've got it set so that the fan blows air all the time.

Try this… Crank the thermostat as high as it will go, so that you know that the AC is only blowing ambient air. Then lower the thermostat a couple of degrees at a time until the compressor kicks on to start cycling freon. If the breaker trips then, you've isolated the problem. And if that doesn't cause the breaker to trip, you've eliminated a possible cause.
__________________
WBCCI #1105
TAC LA-4

My Google-Fu is strong today.
Protagonist is offline   Reply With Quote
Old 05-06-2012, 07:56 AM   #4
Moderator
 
blmitch5's Avatar

 
2006 19' International CCD
Olathe , Kansas
Join Date: Oct 2009
Posts: 4,221
Images: 1
You might PM Lewster, he is very helpful and is a certified RV tech.
__________________
Get involved and sign up for a Rally!
http://www.airforums.com/forums/calendar.php
WBCCI 4973
blmitch5 is offline   Reply With Quote
Old 05-08-2012, 04:53 PM   #5
Rivet Master
 
Silver Otter's Avatar

 
2011 31' Classic
Nellysford , Virginia
Join Date: Mar 2011
Posts: 979
Images: 6
Blog Entries: 1
END OF STORY. kokopat mentions a clamp-on meter. That's what the tech used at Out Of Doors Mart to determine the compressor was drawing over 16 amps by itself. It was at the end of its useful life. They replaced the full AC unit. Now it runs much quieter and draws only about 7-8 amps under load. Nice solution. Nice and cool inside. AND, they did all this for me without an appointment, fitting me into their shop schedule because I was on the road home. Also Nice!
__________________
Greg and Linda Heuer
2011 31' Classic Ltd. - The Silver Otter III
2013 GMC Denali 2500HD 6.6 DuraMax
TAC VA-18 | WBAC 1927 - Shen. Valley Unit 149 | AIR 53869
https://www.linkedin.com/in/gheuer
Silver Otter is offline   Reply With Quote
Old 05-08-2012, 05:19 PM   #6
Rivet Master
Commercial Member
 
sandlapper's Avatar
 
1993 34' Excella
York , South Carolina
Join Date: Jan 2010
Posts: 2,430
Images: 7
Another HIGH 5 to Out of Doors Mart! Glad you are fixed up, and on the road, coolin' it.
__________________
John
WBCCI #3892
Region 3 , 1st VP

Go often to the house of a friend, for weeds choke the unused path........Emerson

Never pick a fight with an old man. If he is too old to fight he will just kill you........a wise old man.
sandlapper is offline   Reply With Quote
Old 07-05-2012, 01:07 PM   #7
Toomuchfun
 
kcrockett's Avatar
 
2005 19' Safari
2005 30' Classic
Cincinnati , Ohio
Join Date: Jan 2010
Posts: 11
This same problem is happening to me in the 90's but ran fine last night with temps in the 80's. Anyone know a mobile RV service in Cincinnati, Ohio?
__________________

__________________
kcrockett is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off



Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 08:54 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.