Old 03-14-2006, 08:28 PM   #1
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,288
Images: 21
OPD valve with Remote Read Gauge

I finally ran out of connections for companies willing to fill my 40 lb Worthingtons without the OPD. Oh well.
So I took them to my local guru to have the valves changed and asked for remote read gauges. He can't find them and neither can I. I know Steve over at VTS sells new tanks with gauges but where can I find just the valves. All that I can find have a separate bore for the Gauge but my tanks just have one bore for the whole system. Oasis says they are available for 30 pounders but not the big ones. Anybody know?
I did a quick search here on OPV but didn't find anything. Thanks guys.
__________________

__________________
Randy...Converters, Inverters, Trimetric, Surge Protectors, Zamp Solar, AGM Batteries
www.bestconverter.com
68 Overlander is offline   Reply With Quote
Old 03-14-2006, 08:44 PM   #2
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Randy,

The guages on the tanks are a very rough indicator as they work on tank pressure....but most of the propane in the tank is in liquid form and the pressure is not a true indicator of the amount of liquid propane remaining in the tank. Better off with 2 tanks and an auto change regulator.
__________________

__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 03-14-2006, 08:49 PM   #3
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,288
Images: 21
Thanks Lew. I have two tanks and the auto changer but the indicator in the control panel is what I want to work. Not that big a deal until I realized i might not be able to have it if I really wanted it! I know they are not that accurate but I like gauges. Gives me something to look at instead of American Idol.
__________________
Randy...Converters, Inverters, Trimetric, Surge Protectors, Zamp Solar, AGM Batteries
www.bestconverter.com
68 Overlander is offline   Reply With Quote
Old 03-18-2006, 05:11 PM   #4
2 Rivet Member
 
Join Date: Mar 2004
Posts: 24
Guages

Home depot has an external guage.
When you convert the valve you lose 20% capacity of your tank.
__________________
Stagehand is offline   Reply With Quote
Old 03-18-2006, 08:10 PM   #5
Rivet Master
Commercial Member
 
lewster's Avatar
 
Vintage Kin Owner
Naples, FL , Hood River, OR
Join Date: Dec 2005
Posts: 7,279
Quote:
Originally Posted by Stagehand
Home depot has an external guage.
When you convert the valve you lose 20% capacity of your tank.
RIGHT! But any LP tank (like the ones on all Airstreams) can only be filled to 80% capacity. There has to be that 20% left at the top to allow space for the liquid propane to boil and vaporize into a gasseous state so it can move thru the suppply lines at low pressure.
__________________
Lew Farber...ABYC Certified Master Marine Electrician...RVIA Certified Master Tech ...AM Solar Authorized Installation Center...AIRSTREAM Solar & Electrical Specialist...Micro Air 'Easy Start' Sales and Installations
lewster is offline   Reply With Quote
Old 03-18-2006, 09:31 PM   #6
Rivet Master
 
1975 29' Ambassador
Reno , Nevada
Join Date: May 2003
Posts: 1,351
The new OPD valves have a float that shuts them off when the liquid gets to 80% to help prevent accidental overfilling. This float is why you don't have any OPD valves with proper level indicators. You have to get a two port tank so you can use one for a fluid level float and the other for the OPD.

Tank fillers should still open the vent and shut off the fill when liquid starts spitting from it.
__________________
bryanl is offline   Reply With Quote
Old 03-20-2006, 07:11 AM   #7
3 Rivet Member
Commercial Member
 
Jim Jarzabek's Avatar
 
1950 25' Cruiser
Currently Looking...
Currently Looking...
Lebanon , Ohio
Join Date: May 2004
Posts: 238
Images: 16
The colder it gets....

Quote:
Originally Posted by 68 Overlander
Thanks Lew. I have two tanks and the auto changer but the indicator in the control panel is what I want to work. Not that big a deal until I realized i might not be able to have it if I really wanted it! I know they are not that accurate but I like gauges. Gives me something to look at instead of American Idol.
I don't know where you live; but the colder it gets, the less efficient propane becomes. The b.t.u. output dramatically decreases as the temperature drops...

Those control panel gauges for propane never worked....
I would get a large tank with an adaptor valve & have it refilled where you are if possible
__________________
Jim Jarzabek is offline   Reply With Quote
Old 03-21-2006, 09:47 AM   #8
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,288
Images: 21
The pressure Gauge with a single bore not being accurate makes perfect sense. A double bore tank with a separate float also makes sense, and I see them in many catalogs and stores.
I just had the valves changed without gauges. I guess I'll use the control panel indicators for something else like... oh I don't know, maybe a wind speed indicator or something!
Thanks guys.
__________________
Randy...Converters, Inverters, Trimetric, Surge Protectors, Zamp Solar, AGM Batteries
www.bestconverter.com
68 Overlander is offline   Reply With Quote
Old 03-21-2006, 10:13 AM   #9
Rivet Master
 
Zeppelinium's Avatar

 
1975 31' Sovereign
1973 27' Overlander
1977 23' Safari
Palmer Lake , Colorado
Join Date: Oct 2005
Posts: 3,908
Send a message via Skype™ to Zeppelinium
Quote:
Originally Posted by Jim Jarzabek
... The b.t.u. output dramatically decreases as the temperature drops...
No, what really happens is the vapor pressure inside the tank drops dramatically as the temperature drops, so the ability of the tank/valves (like an auto-switch valve, which relies on pressure to operate and therefore has some pressure drop) to deliver sufficient flow is impaired. The b.t.u.s per mole (yeah, good old Avagadro) of propane burned is constant.

And the 80% tank limit might have some impact on allowing more surface area for propane vaporization, but what it's really for it to ensure that as the temperature of the propane increases (sunny day, etc.), there is enough expansion room for the liquid so as to not explode the tank from overpressure. When propane is a liquid, it's incompressible (you can only change its volume with temperature, not pressure). It has a high thermal expansion coefficient, so you have to leave serious gas volume in a "full" tank to allow for this.

If you're having trouble getting enough propane for your heater, check to see if your auto-switch valve is OK. If it's still a problem, you'll have to put in a "T" connection and switch tanks manually.
Zeppelinium is offline   Reply With Quote
Old 03-21-2006, 10:49 AM   #10
Moderator
Commercial Member
 
eubank's Avatar
 
1967 30' Sovereign
Bosque Farms , New Mexico
Join Date: Jan 2004
Posts: 6,423
If you want somewhat more accuracy, try your bathroom scale. The collar of your bottle has a marking "TW" indicating the empty weight of the bottle. You're probably using a 30 pound bottle (7 gallons, more or less), so add the TW to the 30 to know the weight when it's full of propane. The closer your bottle's weight is to the TW, the closer you are to being empty.


Lynn
__________________
WBCCI 21043
eubank is offline   Reply With Quote
Old 03-21-2006, 10:55 AM   #11
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,288
Images: 21
I have two 40 lb bottles with the change over so it's really not a big deal. I just kinda wanted the control panel to work, that's all.
I don't see myself toting the bathroom scale to the tongue of the trailer each morning but I have done things that will rival that.
__________________
Randy...Converters, Inverters, Trimetric, Surge Protectors, Zamp Solar, AGM Batteries
www.bestconverter.com
68 Overlander is offline   Reply With Quote
Old 03-27-2006, 11:51 PM   #12
1 Rivet Member
 
75excella's Avatar
 
1975 31' Excella 500
los alamos , California
Join Date: Feb 2005
Posts: 5
Images: 1
Try this link not sure if it will work? I have a 75 with the same problem?
http://www.cramerdecker.com/catalog/38-39.pdf
__________________
75excella is offline   Reply With Quote
Old 04-02-2006, 11:51 AM   #13
Rivet Master
Commercial Member
 
New Borockton , Alabama
Join Date: Sep 2002
Posts: 1,288
Images: 21
I don't think that will work but thanks for the link. If it doesn't have the capability to send the info remotely to the control panel, it doesn't make sense. If I have to visually inspect the bottle, the auto change indicator is good enough and like mentioned, the pressure sensing types are probably not accurate enough. I'm convinced the tank needs a separate bore with a float like the new models have. Thanks.
__________________
Randy...Converters, Inverters, Trimetric, Surge Protectors, Zamp Solar, AGM Batteries
www.bestconverter.com
68 Overlander is offline   Reply With Quote
Old 04-07-2006, 11:08 PM   #14
1 Rivet Member
 
75excella's Avatar
 
1975 31' Excella 500
los alamos , California
Join Date: Feb 2005
Posts: 5
Images: 1
I believe you are right, I did some searching myself and was told that some of the manufactoers are working on making OPD valves with a gauge, but they are no on the market yet? I wont hold my breath.
__________________

__________________
75excella is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fixed that dump valve !!! 77caravaner Waste Systems, Tanks & Totes 1 05-21-2010 06:55 PM
Thetford valve rebuild mkeith54 Waste Systems, Tanks & Totes 17 10-15-2007 03:37 PM
Black & Grey valve trouble camphost Waste Systems, Tanks & Totes 51 08-18-2006 09:45 AM
city water inlet valve failure? JohnGalt48 Fresh Water Systems 2 08-01-2002 05:43 PM
OPD valve w/sight gauges 83Excella LP Gas, Piping, Tanks & Regulators 1 04-16-2002 08:21 AM