Old 11-13-2011, 09:32 AM   #1
Air Mobile
 
2005 25' International CCD
Newport News , Virginia
Join Date: Apr 2010
Posts: 40
LPG Leak Detector Troubles/False Alarm beeps

My 2005 Intl 25' CCD came with a stock "Protechtor LP Gas Detector Series 2001", which I believe is made by a company called Atwood; though it says it was manufactured in China. It's giving me troubles, we just got back from a fall Rally and the darn thing started beeping every 30 secs in the middle of the night. There are three possible light colors flashing on led: Green - Power; Yellow - Fault; and Red - Alarm. The unit was solid yellow and beeped (very loud) every 30 secs. There was no gas leak, no problem, except with the unit. I could find no way to turn it off, and it caused my wife to have go outside with the dog into the cold weather for almost 90 mins as I tried to trouble shot everything. I, unfortunetely, couldn't find the owners manual on unit; did find a reference to it in the Airstream Owners manual, which said consult the manufactures guide. I discovered enough to know this wasn't an indication of a gas leak but that the unit was malfunctioning, why I don't know. I Unscrewed the thing, it's mounted 6 inches off the floor right near the furnace and discovered there is nothing to unplug and no way to turn the darn thing off. I was getting ready to just cut the wires and get my wife and dog in from outside when I noticed a black button which I pushed and it went back to green-power mode (no test tone sounded). This was all occuring from 3am to 4am so I wasn't thinking the clearest. As I checked the next morning I noticed that the button I pushed would have been the test button. Has anyone had a similar problem and know a solution. I am happy to replace the unit with a new one, but don't want to waste the money if all that was needed was an occasional test. Not sure where I read this, but somewhere I recall seeing something to the effect that the unit should be tested weekly or it can malfunction from something crudding up the sensor and it will go off to burn the crud away. I was actually at a weekend Airstream Rally and the folks I asked about this were long-time Airstreamers, but all had older units that came with no LPG detector so had no real insights. I am at loss and am going away for our last camping of the year over Thanksgiving and would be most grateful for anyones insight, so as to avoid a repeated sleepless night. I was told that LP gas has a scent added to it so if there is a leak it smells like rotten eggs (just like my homes natural gas) so with that informatiion I atleast know I'll smell a gas leak so am wondering what's the point of the detector; is this just something the lawyers thought up to avoid potential liability (I'm a lawyer so not being derogatory, I know what a litigous society in which we reside).

Thanks in advance,
Tim
Tim_S is offline   Reply With Quote
Old 11-13-2011, 09:47 AM   #2
3 Rivet Member
 
jkcru's Avatar
 
2010 28' Flying Cloud
Escondido , California
Join Date: Feb 2007
Posts: 196
It will also go off because of low batt voltage
jkcru is offline   Reply With Quote
Old 11-13-2011, 10:07 AM   #3
Air Mobile
 
2005 25' International CCD
Newport News , Virginia
Join Date: Apr 2010
Posts: 40
Thanks, I don't think that was the case for us this time since we were plugged into AC. But who knows maybe I am missing something
Tim_S is offline   Reply With Quote
Old 11-13-2011, 10:24 AM   #4
Rivet Master
 
Silver Goose's Avatar
 
2008 27' Classic FB
Burkburnett , Texas
Join Date: Jul 2010
Posts: 985
Here's a link to the manual for your detector:

http://www.atwoodmobile.com/manuals/...%20LP%20RV.pdf

The chart says for a solid amber light and repeating chirps to press test button to reset the device, if problem persists to contact manufacturer. Sounds like they anticipate that can happen! Too bad this is not included in all the warnings printed on the front that are so useless when you're standing on your head at 2AM trying to read them.

LPG being heavier than air will collect near the floor. It could possibly go unnoticed until the oven pilot for example set it off and that would be too late for everyone. The detector is hardwired to the battery so even putting the battery in store mode or pulling the shore power doesn't kill the power to it.

I think I have a new task on my to-do list... Install a disconnect in the wire behind the detector so if it wakes us up at 2AM and won't reset I can pull the 4 screws and kill it.
Attached Thumbnails
Click image for larger version

Name:	image-3206999605.png
Views:	2247
Size:	1.09 MB
ID:	145090  
__________________
AIR 47751
Silver Goose is offline   Reply With Quote
Old 11-13-2011, 10:27 AM   #5
Rivet Master
 
Silver Goose's Avatar
 
2008 27' Classic FB
Burkburnett , Texas
Join Date: Jul 2010
Posts: 985
Quote:
Originally Posted by jkcru
It will also go off because of low batt voltage
Since it is hard wired to the battery, if the batteries were in store mode and got down to about 8-10 volts, the alarm would give a low battery alert even though the coach was fully powered by the converter.
__________________
AIR 47751
Silver Goose is offline   Reply With Quote
Old 11-13-2011, 01:08 PM   #6
Rivet Master
 
RamblinManGa's Avatar
 
2016 28' Pendleton
Currently Looking...
Scottsdale , Arizona
Join Date: Jul 2009
Posts: 840
Images: 2
Hi from GA. . .the same unit did the same thing a month ago in my 05 Safari 25, so I did the American thing and threw it away and bought a new one (from Dyers) regards, Craig
__________________
WBCCI 2851,4CU
RamblinManGa is offline   Reply With Quote
Old 11-13-2011, 02:57 PM   #7
Rivet Master
 
aftermath's Avatar
 
2006 25' Safari FB SE
Spokane , Washington
Join Date: Sep 2009
Posts: 1,858
Tim,

I have an '06 and experienced the same problem. There are two issues usually involved here. A low battery will cause this and just because you are hooked into AC it doesn't mean your battery will be up to snuff. You could be having some problem with your converter.

Mine "requires" a test on a regular basis. I remember reading something about how dust can settle on the important parts over time and the test procedure is supposed to help clean things. I reset mine just like you did, in the middle of the night, and it worked fine the rest of the season. I tested it before the next season and so far, so good. I would try these things before I went and replaced it.

Good luck.
aftermath is offline   Reply With Quote
Old 11-13-2011, 08:30 PM   #8
Rivet Master
 
Frank&Mike's Avatar
 
2016 27' Flying Cloud
Georgetown , Texas
Join Date: Oct 2008
Posts: 796
Images: 2
Supposed To Replace Approx. Every 4 Years

We had the same problem. There is a thread somewhere on the forums discussing this. Regardless, we found out these devices are intended to be replaced on a regular bases like smoke detectors are intended to be replaced on a regular basis.
Frank&Mike is offline   Reply With Quote
Old 10-07-2012, 06:09 AM   #9
Rivet Master
 
Fly at Night's Avatar
 
2010 27' FB Flying Cloud
Fraser Valley , British Columbia
Join Date: Jan 2011
Posts: 2,966
Images: 10
LOL!

I have discovered the "Protechtor" is very apt when it comes to protecting one against a good night's sleep. Note the time - 5 a.m. PST - and I have been up for two hours since my rude awakening in the wilderness. I came here for the peace and quiet - ha!

First order of business when I get home: disconnect the &^%^ thing and replace with another model - something that is portable that I can place on the floor.
__________________
easily distracted by shiny objects
Fly at Night is offline   Reply With Quote
Old 10-07-2012, 07:58 AM   #10
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by Tim_S View Post
My 2005 Intl 25' CCD came with a stock "Protechtor LP Gas Detector Series 2001", which I believe is made by a company called Atwood; though it says it was manufactured in China. It's giving me troubles, we just got back from a fall Rally and the darn thing started beeping every 30 secs in the middle of the night.
EXACTLY the same thing happened to mine, on my first outing. I must have accidentally kicked it or something. Careful perusal of the owner's manual (which I had to download, I didn't get one with my Interstate) shows that the fix is easy. Shut off the 12v power for about a minute to let it reset, then turn the power back on.

Never had a problem with it since then.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 04-23-2014, 07:13 PM   #11
Rivet Master
 
DreamStreamr's Avatar
 
2005 25' International CCD
Fleetwood , North Carolina
Join Date: Aug 2005
Posts: 687
Images: 38
Send a message via Skype™ to DreamStreamr
Test button works to reset detector

Ours went on yellow alert this evening when I walked closely by it -- chirped, turned yellow, and chirped @ 30 seconds or so. Had the wire cutters ready to kill the power to it, because it is (1) hard wired directly to the battery, and (2) no plugs or switches to d/c the power to it otherwise.

Then did a browser search for "fault Atwood Protector" and before I finished typing it in, this thread popped up. The "push the test button" worked when I held it in for 10 seconds. Went to green.

Replaced the Atwood Protector 2001 two or three years ago, per mfr recommendation. Still totally within its life cycle.

Our voltage is steady at 13+ vdc, we didn't use the range or oven tonight. But gas water heater had been running and tripped -- maybe, maybe not the cause.

Nonetheless, push and hold the test button for 10 seconds, it may switch to green. Ours did.
__________________
Chasing 75 Degrees,

Jim N5RTG
dreamstreamr.com
DreamStreamr is offline   Reply With Quote
Old 05-24-2014, 10:44 AM   #12
Rivet Master
 
1999 28' Excella
New Orleans , Louisiana
Join Date: Aug 2012
Posts: 883
Images: 2
Our LP Gas Protector went off yesterday for the first time. We have now figured out after a few minutes of the generator running it goes off. I push the test button and it stops beeping.

If there is a problem that is setting it off that would be good to know..otherwise I guess we are up for replacement also.
badkat is offline   Reply With Quote
Old 05-24-2014, 11:06 AM   #13
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
Some of the devices (smoke detectors, LP gas alarms, CO detectors) have a limited sensor life, so they are now programed to go into a beep mode when they have reached the end of their design life. Four to seven years are the numbers I have seen. In essence they have a long term timer built into the electronics and after a certain number of hours they go off and cannot be reset.

Not every device has this feature, but when it does, and the life is reached, there is no solution but to replace it. The problem is was it just a false alarm which can be reset, or is it at the end of life? They need an indicator which clearly shows "end of life... replace me".
idroba is offline   Reply With Quote
Old 05-24-2014, 02:59 PM   #14
4 Rivet Member
 
2004 16' International CCD
Chicagoland , Illinois
Join Date: Apr 2014
Posts: 265
Images: 2
Better minds than mine will chime in shortly, but some additional information might help resolve the issue more quickly.

If you can consistently set off the alarm when you first start running the generator I wonder if problem is with the generator and not the alarm. Can you duplicate this behavior when you are on shore power or does it only happen when you are running your generator? Does your generator run on propane or gasoline? How far away from your trailer is the generator when it is running?

It might even be possible that the converter is causing an intermittent voltage drop to the detecotor when it is powered by your generator? Do you see any of your lights dim or experience any other electrical gremlins when the detector goes off?

Until you determine what the root cause of the alarms really is you should try to be very careful not to ignore the beeping when it sounds. You should also try to resist the urge to disconnect it. Fortunately LP gas has a distinctive odor, so as long as you're not sleeping you'll probably know it if you have a real leak.

If your unit is older, I would buy a new detector - hopefully a replacement sensor will resolve your problem. Here is one version that you might consider that you could get quickly:

Atwood 36720 Hydro LPG Leak Detector - Household Alarms And Detectors - Amazon.com
Airrogant is offline   Reply With Quote
Old 05-24-2014, 04:10 PM   #15
Rivet Master
 
1999 28' Excella
New Orleans , Louisiana
Join Date: Aug 2012
Posts: 883
Images: 2
The generator is by the back bumper of our 28' and runs on gasoline. The detector is OLD..needs replacing. Going to turn the gennie on again this afternoon and look at light strength. When reset with test button it shuts up..we will see what happens. Thanks for the tips.
badkat is offline   Reply With Quote
Old 05-24-2014, 09:29 PM   #16
Rivet Master
 
1999 28' Excella
New Orleans , Louisiana
Join Date: Aug 2012
Posts: 883
Images: 2
OK, never went on with generator running..turned it off and later with nothing on went off a couple of times...guess it is dying. Kinda scary to sleep but guess it is a malfunction.
badkat is offline   Reply With Quote
Old 05-25-2014, 08:23 AM   #17
Rivet Master
 
Denis4x4's Avatar
 
2006 25' Safari FB SE
Currently Looking...
Durango , Colorado
Join Date: Feb 2006
Posts: 1,112
I will buy into the need for smoke detectors along with carbon monoxide detectors in RV's. However, after dealing with an LPG detector that when off three times in the wee hours of the morning the first night out, I disabled the damn thing. Having survived 40 years of RVing without one, I decided to take my chances!

Question: are these things mandated by the government?
Denis4x4 is offline   Reply With Quote
Old 11-22-2014, 12:09 PM   #18
3 Rivet Member
 
StagrLee's Avatar
 
2012 25' FB Eddie Bauer
Austin , Texas
Join Date: Aug 2012
Posts: 120
This is what came with with the Atwood Assembly No. 36720 RV Propane Gas Detector I ordered (and the older Atwood ProTechTor that came with my 2012 25'FB EB).

The bracket that came with the one I recieved isn't a perfect fit in the Airstream cutout for the larger, older ProTechTor; but works. Its close to the floor so you can't really tell that the bracket isn't flush with the paneling at the bottom.

Atwood lists the bracket separately as part number 35181 but nobody carries it and Atwood documentation doesn't mention that it is included with part 36720. I'm wondering if it's inclusion is temporary because lots of listings (Amazon and others) don't show the bracket adapter which you will need to retrofit from the older generation to the newer generation sized detector.

My ProTechTor only made it 3 years before it failed.
Attached Thumbnails
Click image for larger version

Name:	LPGasDetector.jpg
Views:	384
Size:	354.9 KB
ID:	227153  
__________________
"Stagr" Lee
2012-1/2 25' Eddie Bauer
StagrLee is offline   Reply With Quote
Old 12-05-2014, 10:20 PM   #19
3 Rivet Member
 
StagrLee's Avatar
 
2012 25' FB Eddie Bauer
Austin , Texas
Join Date: Aug 2012
Posts: 120
I wrote a detailed blog of updating the Atwood LP Detector from the old style to the newer, smaller part. I also took the time to move the detector to cutoff when the storage switch is thrown. Not a difficult mod...

No Excuse For Thinking: Airstream LP Detector Overhaul

see the above link for details
Attached Thumbnails
Click image for larger version

Name:	lp-detector5.jpg
Views:	291
Size:	469.1 KB
ID:	228084  
__________________
"Stagr" Lee
2012-1/2 25' Eddie Bauer
StagrLee is offline   Reply With Quote
Old 11-22-2015, 01:53 PM   #20
3 Rivet Member
 
Durango , Colorado
Join Date: Jul 2014
Posts: 144
Does anyone know where the inline 1 amp fuse is for the LP detector that is hard wired to the batteries in a 2007 19ft. Bambi? I was replacing the old Atwood with a new Atwood LP detector and assume i blew the fuse because with just changing the units and not cross wiring I lost power to the new unit. Everything was working fine but wanted to replace due to safety recommendations. Old unit was 8 years old.
Thanks,
Ken
pkm123 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pex fitting leak - toilet supply line eberrobw Sinks, Showers & Toilets 9 04-13-2012 09:55 AM
Where Is My Leak? Chaplain Kent General Repair Forum 6 10-07-2011 11:55 AM
Frustration !!Water leak at front of trailer!! william Haym Leaks - Weatherstrips, Gaskets, Caulks & Sealants 0 10-06-2011 11:41 AM
Water Leak bumper Airstream danyfr67 Leaks - Weatherstrips, Gaskets, Caulks & Sealants 15 06-07-2011 07:43 PM
Rear window leak fixed! Really? I think so. 1964 GlobeTrottin 1960 - 1964 Globetrotter 0 04-30-2011 05:42 AM