Furnace blows hot, then cold. What gives?

Anyone had this happen before? We have a Suburban Furnace and it will blow hot air for a while (maybe 5 minutes) to heat the cabin, then a few minutes later the air is blowing but no longer warm/hot. Thermostat is on the whole time (it's not the one turning off the warm air). I can turn the thermostat off, wait a minute, then back on, then the furnace will again blow warm/hot air for a while then go to cold.

Any clues? Do I need a new furnace?
__________________

__________________
trekerboy is offline   Reply With Quote
Old 10-03-2015, 11:29 AM   #2
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 5,936
Images: 2
Perhaps There is a "cool down cycle"? Our 1999 will run a bit after "heat" cycle.
__________________

__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 10-03-2015, 11:35 AM   #3
Rivet Master
 
Lumatic's Avatar

 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 6,642
Images: 16
Blog Entries: 1
Your furnace is pretty old. I would consider replacing it with a new furnace if you need to drop a bunch of money into it for repair . It is hard to find anyone willing to work on old furnace for liability reasons. A new furnace would be so much easier to use and efficient.

The problem may not be the furnace at all. It could be the regulator on your tanks. If it also is original it is living on borrowed time. Same thing applies to your thermostat. You could rule this out by disconnecting the wire leads and crossing them. If the furnace now runs OK that is your problem.

Any cheap thermostat will work even it it says 24v. A new regulator will cost you about $50.
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 10-03-2015, 11:49 AM   #4
Rivet Master
 
1974 Argosy 20
2014 20' Flying Cloud
Kooskia , Idaho
Join Date: Jul 2009
Posts: 4,591
If it is an original pilot light furnace (not electronic ignition) it is time to replace it anyway. You can play whack a mole with them, fix one thing, another pops up. They rust out, become dangerous, and that era of Suburban furnaces had recall issues. No recall parts are available from Suburban any more.

Even if the furnace has already been replaced with a newer one, often finding the real issue, be it sail switch, temp limit switch, circuit board issues, gas valve issues etc can be a real PITA. Unless you are a dedicated and knowledgable tinkerer and just love to pull furnaces apart, you are often better off just replacing it.

I am such a tinkerer, but over the years and many rigs, have learned my lesson, and now just replace old furnaces with new ones and LIVE happily ever after. LIVE is the operative word here, there is danger lurking in old rusty furnaces.
__________________
idroba is offline   Reply With Quote
Old 10-03-2015, 12:02 PM   #5
3 Rivet Member
 
KAYAKAMPERS's Avatar
 
1966 26' Overlander
Stone Mountain , Georgia
Join Date: Jan 2009
Posts: 225
Yes, I agree with idroba, it may be time to replace if it is original. Our '66 Overlander has a furnace from the late 90's with electronic ignition and has a bad overheat sensor. The problem sounds the same. Comes on for a few minutes and the sensor cuts it off. I replaced that and works well now, but I was risking the ' whack a Mole' syndrome. If yours is original, then it is something else most likely.
__________________
_______________________________
Beth Wallace & Chris Sanor
1966 26' Overlander International
Towed by 2006 Dodge Dakota 8 cyl.
Tin Can Tourist
TAC #GA-27
AIR #34930
KAYAKAMPERS is offline   Reply With Quote
Old 10-03-2015, 02:55 PM   #6
Rivet Master
 
mimiandrews's Avatar

 
1966 22' Safari
Weatherford , Texas
Join Date: Jun 2008
Posts: 1,425
The older furnaces did have a cool-down period. It makes sure everything inside there is cool before the fan shuts down. Safety stuff, old style.
__________________
mimiandrews is offline   Reply With Quote
Old 10-03-2015, 03:05 PM   #7
Rivet Master
 
Alumaholic's Avatar

 
1966 24' Tradewind
Albuquerque , New Mexico
Join Date: Nov 2005
Posts: 1,751
Images: 33
Because That is What is Supposed to Do...

There is nothing wrong with your furnace.
At the end of a heating cycle, after the the thermostat signals that desired tenp as been reached, the gas valve closes, the flame goes out, and the blower fan runs until the burner is completely cool.
This does not indicate need for a new furnace.
__________________
Ken L
1966 Tradewind 24
2007Chevy Silverado 2500 HD Duramax/Allison
Four Corners Unit WBCCI #8654
Alumaholic is offline   Reply With Quote
Old 10-03-2015, 04:56 PM   #8
cwf
Rivet Master
 
cwf's Avatar
 
1999 34' Excella
Currently Looking...
Hillsboro , Texas
Join Date: Feb 2013
Posts: 5,936
Images: 2
As mentioned, the newer are safer than old. The older tend to develop holes that can allow combustion gasses into Your breathing air yielding a permanent nap. Please have it professionally evaluated or replace yourself if you have skillz..
__________________
Peace and Blessings..
Channing
WBCCI# 30676
cwf is offline   Reply With Quote
Old 10-03-2015, 05:07 PM   #9
Rivet Master
 
Currently Looking...
Mission , Texas
Join Date: Jun 2015
Posts: 836
Quote:
Originally Posted by trekerboy View Post
Anyone had this happen before? We have a Suburban Furnace and it will blow hot air for a while (maybe 5 minutes) to heat the cabin, then a few minutes later the air is blowing but no longer warm/hot. Thermostat is on the whole time (it's not the one turning off the warm air). I can turn the thermostat off, wait a minute, then back on, then the furnace will again blow warm/hot air for a while then go to cold.

Any clues? Do I need a new furnace?

How old is your furnace?
__________________
nrgtrakr is offline   Reply With Quote
Old 10-03-2015, 06:08 PM   #10
Rivet Master
 
drboyd's Avatar

 
1978 25' Tradewind
Metro Phoenix , Arizona
Join Date: Jun 2003
Posts: 1,428
First: Install a working carbon monoxide detector in your coach.

Second: The thermostat actually starts the burner and fan simultaneously. The burner, in turn, heats up the heat exchanger. As long as the heat exchanger is hot, the fan will continue to run - until the heat exchanger has cooled off. What you're seeing there is IMNSHO perfectly normal.

Save yourself the trouble and expense of a new furnace. Believe me, I installed a new furnace in my 1978, and it was a Serious PITA.
__________________
"Between what matters and what seems to matter, how should the world we know judge wisely?" - E.C. Bentley, Trent's Last Case
drboyd is offline   Reply With Quote
Old 10-03-2015, 06:55 PM   #11
4 Rivet Member
 
trekerboy's Avatar
 
1979 31' Excella 500
Charlevoix , Michigan
Join Date: Aug 2014
Posts: 318
Quote:
Originally Posted by Alumaholic View Post
There is nothing wrong with your furnace.

At the end of a heating cycle, after the the thermostat signals that desired tenp as been reached, the gas valve closes, the flame goes out, and the blower fan runs until the burner is completely cool.

This does not indicate need for a new furnace.

That's what I thought, but the thing is that the desired temperature has NOT been reached... In my case, I set the temp at 70 but the temp never rose above 61.
__________________
trekerboy is offline   Reply With Quote
Old 10-03-2015, 06:58 PM   #12
4 Rivet Member
 
trekerboy's Avatar
 
1979 31' Excella 500
Charlevoix , Michigan
Join Date: Aug 2014
Posts: 318
Quote:
Originally Posted by nrgtrakr View Post
How old is your furnace?

I'm not sure. We are the 3rd owners, I'm guessing it's original to this 1979 Excella 500.
__________________
trekerboy is offline   Reply With Quote
Old 10-03-2015, 07:05 PM   #13
Rivet Master
 
drboyd's Avatar

 
1978 25' Tradewind
Metro Phoenix , Arizona
Join Date: Jun 2003
Posts: 1,428
Try setting the thermostat higher? The temperatures and setting on those old thermostats are pretty unreliable...

The other option is that you're low on airflow, which is allowing the heat exchanger to overheat. This could be due to blockage in ducts or at outlets, or it could be due to wear on the brushes in the furnace blower motor.

In the latter case, you might as well bite the bullet and buy the new furnace.
__________________
"Between what matters and what seems to matter, how should the world we know judge wisely?" - E.C. Bentley, Trent's Last Case
drboyd is offline   Reply With Quote
Old 10-03-2015, 10:32 PM   #14
Rivet Master
 
Alumaholic's Avatar

 
1966 24' Tradewind
Albuquerque , New Mexico
Join Date: Nov 2005
Posts: 1,751
Images: 33
As drboyd has diagnosed you may be low on airflow. There is a device called an air sail safety switch in the air intake of your furnace. If there is impeded air flow, the sail switch breaks the circuit and the gas valve closes.
I have seen several instances where the intake was closed, once by physical damage to the opening and once by mud dabbers. Another time the owner had leaned something against the side of his Airstream and blocked the flow of intake air.
Don't be too worried about the age of your furnace. If properly cared for they work for years and years. Few of us use them enough to burn out the heat exchangers and get leakage of combustion gases into the coach. But you must install a carbon monoxide detector as suggested.
__________________

__________________
Ken L
1966 Tradewind 24
2007Chevy Silverado 2500 HD Duramax/Allison
Four Corners Unit WBCCI #8654
Alumaholic is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Duotherm AC blows hot not cold RichHog Furnaces, Heaters, Fireplaces & Air Conditioning 49 06-28-2016 08:29 PM
Electric furnace burning wire. Blows cold. janix2010 Furnaces, Heaters, Fireplaces & Air Conditioning 5 11-03-2010 03:22 PM
furnace blows cold air only 99Limited34 Furnaces, Heaters, Fireplaces & Air Conditioning 11 05-08-2010 09:49 PM
Furnace blows cold air guy99 Furnaces, Heaters, Fireplaces & Air Conditioning 37 04-06-2007 11:26 PM


Virginia Campgrounds

Reviews provided by




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 02:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, Jelsoft Enterprises Ltd.

Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.