Question Propane Tank Level Indicator Error?

After two separate fill ups, our tank consistently reads at 1/3 full. I suspect a level sensor, but don't know what or how the gauge is sensing propane (ok - C3H8) level. Can anyone enlighten me on what I should check or is it a trip to the dealer next spring?
__________________

__________________
All that is gold does not glitter,
Not all those who wander are lost
RC-AV8R is offline   Reply With Quote
Old 11-08-2018, 04:51 PM   #2
2 Rivet Member
 
Libertyville , Illinois
Join Date: Jun 2018
Posts: 26
Quote:
Originally Posted by RC-AV8R View Post
After two separate fill ups, our tank consistently reads at 1/3 full. I suspect a level sensor, but don't know what or how the gauge is sensing propane (ok - C3H8) level. Can anyone enlighten me on what I should check or is it a trip to the dealer next spring?


I canít answer your question but my sensor also seems off. It was reading 1/3 but only took 4 gallons of C3H8 so it must have been over 2/3ís full
__________________

Schmitte is offline   Reply With Quote
Old 11-08-2018, 04:54 PM   #3
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 5,646
The propane level sensor uses a variable resistor to sense level. One end of the resistor goes to your gauge panel. The other end connects to the tank body.

The problem is the body of the tank is not grounded solidly. Tighten the heck out of the tank hold-down and see if that helps any.

If you have a multimeter, check for voltage between the body of the tank and the metal of the A-frame. There should be as close to zero as the meter can read. If not, the tank is not well grounded...

In other threads, it was suggested adding a ground wire to the screw holding the sensor to the tank, and a two-prong connector to the tank so you get a solid ground for the gauge panel through one wire, and the other wire to the panel is well connected.

Another easy test: Pull the plug on your sensor and see if the gauge reads empty. Then ground that wire to the body or A-frame of the trailer. It probably will then read full. If it does, it's for sure a grounding problem.

Let us know what you find out...
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is online now   Reply With Quote
Old 11-08-2018, 05:42 PM   #4
Rivet Master
 
2013 Interstate Coach
Raymond , Iowa
Join Date: Jun 2014
Posts: 797
My propane tank has a gauge that use instead of the electronic gauge.
Titus is offline   Reply With Quote
Old 11-08-2018, 05:59 PM   #5
Wannabe RV'er in training
 
Alex AVI's Avatar

 
2018 Interstate Lounge Ext
High Desert , Las Vegas , Nevada
Join Date: Feb 2018
Posts: 1,357
Quote:
Originally Posted by rmkrum View Post
The propane level sensor uses a variable resistor to sense level. One end of the resistor goes to your gauge panel. The other end connects to the tank body.

The problem is the body of the tank is not grounded solidly. Tighten the heck out of the tank hold-down and see if that helps any.

If you have a multimeter, check for voltage between the body of the tank and the metal of the A-frame. There should be as close to zero as the meter can read. If not, the tank is not well grounded...

In other threads, it was suggested adding a ground wire to the screw holding the sensor to the tank, and a two-prong connector to the tank so you get a solid ground for the gauge panel through one wire, and the other wire to the panel is well connected.

Another easy test: Pull the plug on your sensor and see if the gauge reads empty. Then ground that wire to the body or A-frame of the trailer. It probably will then read full. If it does, it's for sure a grounding problem.

Let us know what you find out...
RMKRUM - is the grounding issue affecting the physical gauge on tank or the virtual gauges on Firefly or SeeLevel display? My physical seems spot on but the virtuals are off, like 1/8-1/4 (lesser than physical).
Alex AVI is offline   Reply With Quote
Old 11-08-2018, 06:01 PM   #6
Moderator
Commercial Member
 
eubank's Avatar
 
1967 30' Sovereign
1999 31' Land Yacht
Bosque Farms , New Mexico
Join Date: Jan 2004
Posts: 6,588
A nice, vivid example of why fillers are not permitted to fill cylinders based on what such gauges read.

Lynn
__________________
WBCCI 21043
eubank is offline   Reply With Quote
Old 11-08-2018, 06:17 PM   #7
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 5,646
Quote:
Originally Posted by Alex AVI View Post
RMKRUM - is the grounding issue affecting the physical gauge on tank or the virtual gauges on Firefly or SeeLevel display? My physical seems spot on but the virtuals are off, like 1/8-1/4 (lesser than physical).
The remote displays will be messed up from the grounding issue. The physical gauge is totally mechanical. There is a float in the tank and a linkage with a magnet on it sealed inside the tank. The physical gauge needle picks up the magnet position with it's own magnet. The variable resistance thing is attached to the physical gauge needle inside the tank gauge assembly. There are usually two wires coming out of the gauge assembly. One is grounded only to the tank body with a screw, the other connects to a wire coming from the virtual gauge electronics.

The problem is that the ground connection is trying to work thorough all the paint, rust and dirt on the tank and the tank holder, so the electronics sees an increased resistance, and reads incorrectly. Typically a better ground connection will fix this.

Another, less likely possibility is that the electronics are not calibrated to the gauge. Firefly or SeeLevel is not as subject to that issue as the old MicroPulse system. Might be worth doing a calibration check on your system, but I'd make sure the ground connection is solid first.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is online now   Reply With Quote
Old 11-08-2018, 06:24 PM   #8
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 5,646
Quote:
Originally Posted by eubank View Post
A nice, vivid example of why fillers are not permitted to fill cylinders based on what such gauges read.

Lynn
Oh, absolute AMEN to that. That's why tanks are ALWAYS filled using weight, or the bleed screw spitting liquid to be sure. The new OPD valves made tank filling a bit safer, but I trust the bleed screw more...an overfilled tank in the desert heat around here is a largish bomb waiting to go off, IMHO. Being a front seat spectator in the middle of a potential fireball, plus flying steel shrapnel thrown in as an extra attraction is NO fun. Hopefully the pressure relief pops before the tank does...
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is online now   Reply With Quote
Old 11-08-2018, 07:34 PM   #9
Moderator
Commercial Member
 
eubank's Avatar
 
1967 30' Sovereign
1999 31' Land Yacht
Bosque Farms , New Mexico
Join Date: Jan 2004
Posts: 6,588
NFPA 59 (the "bible" of propane) requires the OPD, but does not include it as a safe way to fill cylinders. And there's a reason for that.

Prior to OPDs, home fillers would often overfill their cylinders and wind up with dangerous conditions (and all too often enough resulting in tragic accident). The introduction of OPDs was/is the attempt to stop or at least to slow this overfilling activity.

But there's a problem. OPDs are safety devices that work when installed, but they are never again inspected for function. By contrast, using the bleed valve (if legal in that state) relies only on gravity; and using weight relies on a scale whose accuracy is checked independently by the state. In other words, there is no point in the process that relies on "equipment" that is sold initially, but never checked again.

(Of course, there's a great deal of variation in how inspections, licensing and related matters are carried out from state to state; that's because regulations governing propane handling are state based, not federal.)


Lynn

Quote:
Originally Posted by rmkrum View Post
Oh, absolute AMEN to that. That's why tanks are ALWAYS filled using weight, or the bleed screw spitting liquid to be sure. The new OPD valves made tank filling a bit safer, but I trust the bleed screw more...an overfilled tank in the desert heat around here is a largish bomb waiting to go off, IMHO. Being a front seat spectator in the middle of a potential fireball, plus flying steel shrapnel thrown in as an extra attraction is NO fun. Hopefully the pressure relief pops before the tank does...
__________________
WBCCI 21043
eubank is offline   Reply With Quote
Old 11-08-2018, 08:52 PM   #10
2 Rivet Member
 
Libertyville , Illinois
Join Date: Jun 2018
Posts: 26
Quote:
Originally Posted by rmkrum View Post
The propane level sensor uses a variable resistor to sense level. One end of the resistor goes to your gauge panel. The other end connects to the tank body.

The problem is the body of the tank is not grounded solidly. Tighten the heck out of the tank hold-down and see if that helps any.

If you have a multimeter, check for voltage between the body of the tank and the metal of the A-frame. There should be as close to zero as the meter can read. If not, the tank is not well grounded...

In other threads, it was suggested adding a ground wire to the screw holding the sensor to the tank, and a two-prong connector to the tank so you get a solid ground for the gauge panel through one wire, and the other wire to the panel is well connected.

Another easy test: Pull the plug on your sensor and see if the gauge reads empty. Then ground that wire to the body or A-frame of the trailer. It probably will then read full. If it does, it's for sure a grounding problem.

Let us know what you find out...


Thanks! This group is so awesome. Iíll check the ground tomorrow.
Schmitte is offline   Reply With Quote
Old 11-09-2018, 12:57 AM   #11
Wannabe RV'er in training
 
Alex AVI's Avatar

 
2018 Interstate Lounge Ext
High Desert , Las Vegas , Nevada
Join Date: Feb 2018
Posts: 1,357
Quote:
Originally Posted by Schmitte View Post
Thanks! This group is so awesome. Iíll check the ground tomorrow.
+1 Thank you from me too.

EUBANK - Thanks for that info on home fillers

RMKRUM - Thanks for clarifyIng which gauge is mechanical/electrical and I do see those 2 wires coming out of physical gauge. Didn't even have to go out to garage to check, I saw them on old pics I took of undercarriage area by tank gauge.
Alex AVI is offline   Reply With Quote
Old 11-09-2018, 05:55 AM   #12
2 Rivet Member
 
RC-AV8R's Avatar
 
2016 Interstate Grand Tour Ext
Salem , New Hampshire
Join Date: Jul 2018
Posts: 25
Thumbs up

+2 from me . Ground check it is today...

Thanks!
__________________
All that is gold does not glitter,
Not all those who wander are lost
RC-AV8R is offline   Reply With Quote
Old 11-09-2018, 06:14 AM   #13
Rivet Master
 
2013 Interstate Coach
Raymond , Iowa
Join Date: Jun 2014
Posts: 797
rmkrum
Thanks for the explanation of the inside electric gauge.

One also has to keep in mind how to interpret the gauges. The 2/3 light means something less than completely full, the 1/3 light means something less than 2/3 full, and the empty light means something less than 1/3 full.

Every so often I poke my head underneath to read the tank gauge. From what I remember from a recent trip the correlation between tank gauge and electric gauge was:
full light on electric gauge = full tank gauge (where full = 80% of 18 gallons)
2/3 light on electric gauge = 3/4 on tank gauge
1/3 light on electric gauge = 1/2 on tank gauge

Fresh water tank works similarly to the above; since mentally you are counting down from full.

Black and Grey tanks are just the opposite; since mentally you are counting up from empty:
1/3 light means not completely empty
2/3 light means something more than 1/3 full
Full light means something more than 2/3 full.
Titus is offline   Reply With Quote
Old 11-09-2018, 10:27 AM   #14
2 Rivet Member
 
RC-AV8R's Avatar
 
2016 Interstate Grand Tour Ext
Salem , New Hampshire
Join Date: Jul 2018
Posts: 25
Back from checking the tank. I couldn't get access to tighten down the tank mounting bolts (RV in storage) to check for grounding but the measurement differential was 0.4V.

One problem appeared to be the mechanical gauge - it was just hanging by its wires so using dabs of 1-minute epoxy I remounted that. Pulling in & out the sensor wires also appeared to help as the internal meter now reads 2/3 and basically matches the mechanical gauge.

Thanks again for the pointers.
__________________

__________________
All that is gold does not glitter,
Not all those who wander are lost
RC-AV8R is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fresh Water tank level indicator 79 28F DOCBloom Fresh Water Systems 5 08-23-2016 07:09 PM
Tank Level indicator lights and BLACK water ?? SagaCapt Plumbing - Systems & Fixtures 13 07-29-2016 01:45 PM
Gray Tank Level Indicator oreillychris Waste Systems, Tanks & Totes 1 11-28-2015 08:09 AM
Electronic Propane Level Indicator Bigventure LP Gas, Piping, Tanks & Regulators 4 11-28-2009 08:09 PM
Tank level indicator panel mcostanzo 2003 Safari 7 11-07-2003 10:27 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.




Copyright 2002- Social Knowledge, LLC All Rights Reserved.

All times are GMT -6. The time now is 03:59 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2018, Jelsoft Enterprises Ltd.