Heater stopped working

Hello,

Sorry if this has already been covered, but I wasn't able find troubleshooting information for the heater in the forums.

I have a 2013 interstate and the heater has stopped working. It doesn't attempt to start when turned on via the thermostat. (As apposition to the gas line being off and it trying to start, but not being able to)

I checked the circuit breakers and see nothing out of the ordinary.

Hoping someone might have a suggestion and its some small issue I've overlooked.


Thanks,

Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 12:36 PM   #2
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Are you out of propane?
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 12-20-2015, 12:45 PM   #3
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Nope. Full tank. Again, I've tried to start t in the past with the propane off and it will "click click click" as it tries to start. Currently it does nothing. No fan comes on, etc.


Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 12:53 PM   #4
Rivet Master
 
Lumatic's Avatar
 
1971 25' Tradewind
1993 34' Excella
Currently Looking...
Estancia , New Mexico
Join Date: Feb 2005
Posts: 7,743
Images: 16
Blog Entries: 1
Is the pilot light on? If not you may have a bad thermocouple or clogged orifice. You can check the thermostat by crossing the 2 wires that connect it to the furnace. If the furnace starts you have a bad thermostat. If that does not solve the problem I would suspect a bad circuit board.
__________________
Sail on silver girl. Sail on by. Your time has come to shine.
Lumatic is offline   Reply With Quote
Old 12-20-2015, 12:59 PM   #5
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Think I figured out the problem. I turned on the generator to see if that made a difference. (Shouldn't need the gen, but nothing else was working so I figured it couldn't hurt to try)

Anyway, once I turned k. The furnace, the domestic top unit turned on and started blowing air.

I had a valet brilliantly try to park the interstate in a cover garage and hit the top ax unit. The dealer replaced it over the summer but didn't set the dip switches correctly so furnace wasn't even an option showing up in the thermostat. They gave me the correct dip switch settings over the phone and I took of the cover front the top unit and set it correctly myself. The furnace setting showed up after changing the setting, but since it was the middle of summer I never actually tested to see if it worked.

Either the thermostat or top unit is probably confused and thinks it's should use the domestic for heat when it should be the furnace at door level.

Now that I think about it, it's probably the thermostat.

Wonder if I have programming instructions for the thermostat.

Hmm, I'll have to look and report back.

Anyone have experience with this that might be able to confirm if I'm looking on the right direction?


Thanks,

Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 01:00 PM   #6
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by jquayle View Post
I checked the circuit breakers and see nothing out of the ordinary.
The furnace will not attempt to start until the fan starts running. so if the fan doesn't start running, it's sensible to suspect an electrical problem. However, both the fan and the thermostat operate off 12vDC, not 120vAC. Checking circuit breakers doesn't help— you need to be checking fuses.

On Edit— the OP was posting at the same time I was, so my advice has already become a moot point. But instead of deleting this now-worthless post, I'll leave it up for the benefit of others who might be searching a solution to a similar problem later.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 12-20-2015, 01:10 PM   #7
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
No luck. Reset thermostat and no change.

Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 01:30 PM   #8
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Prot,

The fan for the floor furnace unit or from the top domestic unit?

I'll start checking fuses either way...


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 01:34 PM   #9
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by jquayle View Post
The fan for the floor furnace unit or from the top domestic unit?
Floor furnace fan is 12vDC. Rooftop A/C fan is 120vAC.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 12-20-2015, 01:37 PM   #10
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Heater stopped working

Fuses all look ok.

No fan comes on from floor furnace. I pulled the cover and there is a reset switch, but it was already on and resetting it made no difference.

Anything else I should check it is this looking like a dealer issue?

Thanks,


Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 01:42 PM   #11
Rivet Master
Commercial Member
 
Vintage Kin Owner
Naples , Florida
Join Date: Dec 2005
Posts: 7,508
If you have the ability, check to see that you have 12VDC at the furnace igniter board. If you do, you either have s problem with said igniter board or a communication problem between the CCC-II, the A/C's control board and the furnace igniter board.


Lew Farber
RVIA/RVDA Nationally Certified Master Tech
ABYC Certified Master Marine Electrician
Master Tech Energy Systems, Inc.
AM Solar Certified Installation Center*AMS Lithium Batteries
Lifeline AGM Batteries**Magnum Inverters
541-490-6357
__________________
lewster
Solar Tech Energy Systems, Inc.
Victron Solar Components and Inverters, Zamp Solar Panels, LiFeBlue and Battle Born Lithium Batteries, Lifeline AGM Batteries
lewster is offline   Reply With Quote
Old 12-20-2015, 01:53 PM   #12
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Thanks lew. Ill see if I can confirm power there.

Thank you everyone for all the quick responses!


Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-20-2015, 05:26 PM   #13
Rivet Master
 
Boxster1971's Avatar

 
2024 Interstate 19
Fulton , Maryland
Join Date: May 2010
Posts: 3,879
Quote:
Originally Posted by Lumatic View Post
Is the pilot light on? If not you may have a bad thermocouple or clogged orifice. You can check the thermostat by crossing the 2 wires that connect it to the furnace. If the furnace starts you have a bad thermostat. If that does not solve the problem I would suspect a bad circuit board.

No pilot light in the Interstate furnaces. It is electronic ignition.


- - Mike
2013 Lounge EXT on 2012 Sprinter
__________________
- - Mike
--------------------------
2024 Airstream Interstate 19e AWD
Previous: 2013 Airstream Interstate 3500 Ext Lounge
Boxster1971 is offline   Reply With Quote
Old 12-20-2015, 06:55 PM   #14
Rivet Master
 
Bambi_Bandit's Avatar
 
2008 27' International FB
1964 19' Globetrotter
1955 26' Cruiser Overlander
Austin , Texas
Join Date: Sep 2004
Posts: 608
Images: 12
Can you open the furnace access door from the outside, access the reset switch from "reset" to "off", check for loose wires/reset them and switch back to "reset"?

Is there any red blink light code from the circuit board?
__________________
Kevin & Prim Li
Bandit the Siberian Husky (RIP) & "G" the Min-Pin (RIP)
Cosmo the Custom 2008 27FB Intl CCD
Maxwell the 1964 Globe Trotter
Name TBD the 1955 Overlander
WBCCI # 6155
AIR # 6155

2nd love - 2006 28' Safari LS
1st love - 2004 19' CCD Bambi
Bambi_Bandit is offline   Reply With Quote
Old 12-20-2015, 07:16 PM   #15
Figment of My Imagination
 
Protagonist's Avatar
 
2012 Interstate Coach
From All Over , More Than Anywhere Else
Join Date: Dec 2011
Posts: 10,868
Quote:
Originally Posted by Bambi_Bandit View Post
Can you open the furnace access door from the outside
Airstream Interstates (except maybe older T1N models) don't have an outside access door for the furnace, only for the water heater.
__________________
I thought getting old would take longer!
Protagonist is offline   Reply With Quote
Old 12-21-2015, 06:40 AM   #16
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Bambi,

Access is on the inside as prot stated. I did pull the panel and tried the reset switch with no luck. Saw the chart of error codes in the manual, but i can't see any LEDs on. I may need to disassemble the unit in order to see the control board better. It faces inward and although it looks like nothing is on, I can't be 100%. (Although I would think I should be able to see something on or blinking without pulling it apart).

Doesn't seem to be easy to access anything by just removing the outer cover and I didn't have time to work on it yesterday beyond a quick look around.

It was recommended I short out the connection wires from the thermostat to see if it turns on. Anyone able to advise exactly where I should do that?

Here's the diagram from the manual

Click image for larger version

Name:	ImageUploadedByAirstream Forums1450705130.990791.jpg
Views:	178
Size:	104.6 KB
ID:	254239

Thank you,


Jeff


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Old 12-21-2015, 07:14 AM   #17
Rivet Master
 
InterBlog's Avatar
 
2007 Interstate
League City , Texas
Join Date: Oct 2014
Posts: 6,139
Quote:
Originally Posted by Protagonist View Post
Airstream Interstates (except maybe older T1N models) don't have an outside access door for the furnace, only for the water heater.
I have yet to see any lay-out or model year of T1N that has exterior furnace access. Everything I have seen in person and in the sales market has interior access only.
InterBlog is offline   Reply With Quote
Old 12-21-2015, 07:40 AM   #18
Rivet Master
 
Wingeezer's Avatar
 
2005 30' Classic
Burlington , Ontario
Join Date: Sep 2008
Posts: 2,743
From the wiring schematic that you posted, can you disconnect the +12v wire from the control board and pput 12vdc directly onto the motor to see if it starts up?

If not, that would seem to indicate that the motor is the problem, if not, then quite possibly the control board.

One thing I always do early in any attempt to diagnose problems with any appliance on the trailer is to unplug and re-plug all wiring connectors, cleaning them as well if there is any indication that it is needed. Also cleaned any ground connectors in the circuit to ensure good contact

Many times I have found such a simple thing gets everything working again. Probably you have already tried that though!

My trailers have always been bought a few years old, and as trailers age, bad electrical connections seem to be problematic.


Brian.
__________________
Brian & Connie Mitchell

2005 Classic 30'
Hensley Arrow / Centramatics
2008 GMC Sierra SLT 2500HD,4x4,Crew Cab, Diesel, Leer cap.
Wingeezer is offline   Reply With Quote
Old 12-21-2015, 08:03 AM   #19
Rivet Master
 
HowieE's Avatar
 
1991 34' Excella
Princeton , New Jersey
Join Date: Aug 2003
Posts: 7,070
Images: 12
On the right side of the diagram there is a Red and a Black wire. They have some form of connection to the heater, most likely a wire nut. Find that connection, disconnect it and test for 12 volts across the red and black wires. If you have 12 volts across them, reconnect the connections to the heater, then look for the on/off/circuit breaker switch in the heater. It will have 2 red wires on it. If the switch/breaker is on you will have 12 volts from each red wire to the black wire at the connection you just attached. If not the switch/breaker is open.

You have an electrical problem and you have to find out where that problem is. If you have 12 volts to the heater then the problem in in the heater. A fuse on the control board or the board itself. If you do not have 12 volts across the red and black wire you have a blown fuse in the 12 volt panel, a dead battery, or open wire suppling the heater.
__________________
WBCCI 12156 AIR 3144 WACHUNG TAC NJ6
2004 Excursion 4x4
1991 34 ft. Excella +220,000 miles, new laminated flooring, new upholstery, new 3200 lbs axles

HowieE is offline   Reply With Quote
Old 12-21-2015, 09:44 AM   #20
3 Rivet Member
 
jquayle's Avatar
 
2013 Interstate Coach
Napa , California
Join Date: Mar 2013
Posts: 122
Thanks all for bearing with me.

Confirmed power at the switch.

Not sure where to jump to bypass the control board.

Here's a picture. Don't want to jump in the wrong place and fry something

Click image for larger version

Name:	ImageUploadedByAirstream Forums1450716241.504042.jpg
Views:	134
Size:	96.2 KB
ID:	254250


Sent from my iPhone using Airstream Forums
jquayle is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Newbies: our instant hot water heater just stopped working! sampson Plumbing - Systems & Fixtures 6 05-18-2015 07:28 PM
Hood/hood lights and water heater stopped working!!! Thomas_G Electrical - Systems, Generators, Batteries & Solar 1 06-17-2013 12:49 PM
Forced air heater stopped working Dennis E Furnaces, Heaters, Fireplaces & Air Conditioning 0 03-18-2012 03:47 PM
The furnace stopped working ipso_facto Furnaces, Heaters, Fireplaces & Air Conditioning 13 02-24-2006 02:04 PM
Tail Lights Stopped Working dpope 2000 - 2004 Safari 8 04-05-2003 12:22 PM