Quote:
Originally Posted by malconium
or.
Relative to tank type water heaters it was my thought that typical RV units simply do not have enough BTU capacity to heat water enough. Perhaps I am wrong about that. If I recall most of the units that I looked at were rated somewhere in the range of 30k BTU's which did not seem like enough.
Malcolm
|
Hydronic system design is all about balance.
Malcolm's system, based on radiant surface area, can't dissipate more than around 8,000 BTU/h. The fan coil should have its own BTU rating though these are usually based on 180 degree water and would have to be derated for the water temperature actually in use. I have a table somewhere but for 130 degrees it's roughly half.
Any of the standard tank-type RV water heaters could deliver 8,000 BTU per hour.