Old 07-26-2019, 09:23 AM   #1
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
Roof AC Tripping Generator 30 AMP 20 AMP OK

2005 Land Yacht 30 ft 50 AMP service

30 amp trips after approx. 5 min of cooling 85 outside temp, will run longer in cooler temp - front ac unit

20 amp does not - rear ac keeps cooling

When on shore power AC runs no problem

Would replacing breaker on generator be the best place to start as to fixing problem
1956elli is offline   Reply With Quote
Old 07-26-2019, 09:30 AM   #2
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Hi

Best bet is the A/C unit is not in good shape.

Bob
uncle_bob is offline   Reply With Quote
Old 07-26-2019, 11:32 AM   #3
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
Thanks Bob

Having "limited" knowledge on electrical and how it works - I shall ask

If it does not trip the breaker on the inside panel when attacked to shore power why would it then trip the generator breaker when not using shore power - both 30 amp
1956elli is offline   Reply With Quote
Old 07-26-2019, 11:48 AM   #4
3 Rivet Member
 
1988 Argosy 32
Lomita , California
Join Date: Aug 2012
Posts: 181
a clamp on amp meter will tell the tail, or you can PPC it, (pro parts changer)
Wolfe is offline   Reply With Quote
Old 07-26-2019, 11:58 AM   #5
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,724
Make sure that the generator is putting out the correct voltage. Low voltage can cause the AC to run less efficiently and use more current. Many AC's have a low voltage alarm but not all.


When you say the 30 amp breaker blows but not the 20, than I'm assuming you're talking about the breakers directly on the generator. Is this correct?
92landyacht is offline   Reply With Quote
Old 07-26-2019, 12:45 PM   #6
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
Yes the 30 on the generator the 20 does not trip

It will run with both AC units cooling but the front AC which is on the 30 will trip after about 5 to 10 min
1956elli is offline   Reply With Quote
Old 07-26-2019, 12:50 PM   #7
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
More info - I turn the 20 off at the generator and the 30 will still trip after the same time period

No appliances on in the coach, no lights
1956elli is offline   Reply With Quote
Old 07-26-2019, 12:59 PM   #8
Rivet Master
 
bibbs's Avatar
 
1977 Argosy Minuet 6.0 Metre
1973 21' Globetrotter
1975 26' Argosy 26
Vista , California
Join Date: Sep 2006
Posts: 589
Is the fridge set to gas? Also try unplugging the charger/converter. Does the water heater also use 120v?
bibbs is offline   Reply With Quote
Old 07-26-2019, 02:36 PM   #9
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,724
Turning that on or off will have no effect. You need to still verify voltage and current on that line. You'll need a digital multi-meter that has a current sensing clamp. You can pick them up pretty inexpensively now. Even Home Depot has them for around $59.00:


https://www.homedepot.com/p/Klein-To...L210/207144572

All you have to do to make a current reading is to put the clamp around the hot wire (black) and set the scale to read AC Amps. No need to probe anything. Voltage reading is easy as well. Set the meter to read AC volts ~ and then probe a socket that's on that breaker. The meter will auto range and give you an accurate reading.



I personally wouldn't travel without one.
92landyacht is offline   Reply With Quote
Old 07-26-2019, 03:42 PM   #10
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
Thanks for all the info - something to do tomorrow and somethings else to buy
Yall have a good weekend
1956elli is offline   Reply With Quote
Old 07-26-2019, 03:47 PM   #11
Rivet Master
 
92landyacht's Avatar
 
1992 36' Land Yacht
Grayson , Georgia
Join Date: Nov 2011
Posts: 1,724
Quote:
Originally Posted by 1956elli View Post
Thanks for all the info - something to do tomorrow and somethings else to buy
Yall have a good weekend

Welcome to the world of owning an RV. Seems like there's always something to do or buy.
92landyacht is offline   Reply With Quote
Old 07-26-2019, 03:56 PM   #12
Rivet Master

 
2007 22' International CCD
Corona , California
Join Date: Jul 2013
Posts: 9,180
Yeah, stay away from the “What did you get for your Airstream today” thread. Gets me in trouble every time.
__________________
Rich, KE4GNK/AE, Overkill Engineering Dept.
'The Silver HamShack' ('07 International 22FB CCD 75th Anniversary)
Multiple Yaesu Ham Radios inside and many antennae sprouting from roof, ProPride hitch, Prodigy P2 controller.
2012 shortbed CrewMax 4x4 Toyota Tacoma TV with more antennae on it.
rmkrum is offline   Reply With Quote
Old 07-26-2019, 05:53 PM   #13
Rivet Master
 
batman's Avatar
 
1964 22' Safari
modesto , California
Join Date: Jul 2010
Posts: 1,097
Just a quick couple questions.
What make and model of generator are you using?
Have you used this generator before with this trailer and both AC's running?


-Dennis
batman is offline   Reply With Quote
Old 07-26-2019, 07:34 PM   #14
2 Rivet Member
 
2006 30' Land Yacht 30 SL
Kendalia , Texas
Join Date: Mar 2019
Posts: 35
Images: 1
Purchased this past February and yes we ran the generator and both AC units for about 20 min. but it was a lot cooler then and no problems

Other trips I have only used shore power because it was cool enough while driving with dash AC

ONAN 5.5HGJAB-901C Per "sticker" 45.8 Amps 5.5 KW

Hay - I have plenty of experience buying STUFF - also got boat & WIFE
1956elli is offline   Reply With Quote
Old 07-26-2019, 08:00 PM   #15
Rivet Master
 
Al and Missy's Avatar
 
2002 30' Classic S/O
Fleming Island , Florida
Join Date: Nov 2013
Posts: 4,673
Is your generator gasoline or propane? The gasoline version has a mechanical governor that may need adjustment. Also the carburetor has an altitude adjustment.


Al
__________________
“You cannot reason someone out of a position they have not been reasoned into"
Al, K5TAN and Missy, N4RGO WBCCI 1322
2002 Classic 30 Slideout -S/OS #004
2013 Dodge 2500 Laramie 4x4 Megacab Cummins
Al and Missy is offline   Reply With Quote
Old 07-26-2019, 08:02 PM   #16
Rivet Master
 
dadstoy's Avatar
 
Currently Looking...
_ , _
Join Date: Mar 2008
Posts: 2,385
If the A/C is working fine on shore power, then I'm going to also guess that the GenSet is not putting out the correct voltage. See the post I wrote below...



http://www.airforums.com/forums/f311...ml#post2263689
__________________
May a Firefly land upon your shoulder
and bring you good luck, good fortune, and abundance.
dadstoy is offline   Reply With Quote
Old 07-27-2019, 07:00 AM   #17
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Hi

Never rule out a defective breaker

The "measure it" advice is really the only way to go. Otherwise you just start randomly swapping parts out. That gets expensive if the A/C is the first thing you swap ....

One thing to watch for as you go shopping:

Clamp on amp meters come in various ranges and types.

Most are designed to look at a whole house at once. Some have a 400A range and that's it. You will *never* need to measure 400A of AC current in an RV. If the "bottom end" of that scale is 4A, that's not real good. Take a look at how it does on low currents.

You can get AC only gizmos and they have been around for a *long* time. I have a couple with ... errr ... analog needle displays .... yikes !!! These days you can also get ones that will do both AC *and* DC. For an RV, that is a very handy thing. You are just as likely to be playing with 12V DC as with 120V AC. The same "current range" thing applies here as well.

A handy accessory for the AC version is a little inline plugin device. It lets you put it inline with an appliance. You can then clamp on to the (now accessible) lines to the device. The really cool ones have a 10X side that helps with the range on the amp meter. Even the fancy ones are dirt cheap. Yes, you can also make one from scratch.

If you go crazy, you can indeed spend a lot of money on this stuff. One example:

https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

(Yes, there's one sitting in the drawer over under the fridge. There's also a digital oscilloscope and a 5 1/2 digit DVM in the wardrobe closet .... crazy indeed ....)

Bob
uncle_bob is offline   Reply With Quote
Old 07-27-2019, 08:11 AM   #18
Rivet Master
 
lsbrodsky's Avatar
 
2012 25' FB International
Trent Woods , North Carolina
Join Date: May 2013
Posts: 3,120
"A handy accessory for the AC version is a little inline plugin device. It lets you put it inline with an appliance. You can then clamp on to the (now accessible) lines to the device. The really cool ones have a 10X side that helps with the range on the amp meter. Even the fancy ones are dirt cheap. Yes, you can also make one from scratch."

Thanks, I never knew those things existed although the use seems limited, first to something in a normal AC circuit limited to 15 amps. Seems like I would use my clamp-on more for stuff that is not or does not plug in to a normal outlet.

Larry
lsbrodsky is offline   Reply With Quote
Old 07-27-2019, 08:16 AM   #19
Half a Rivet Short
 
2017 30' Classic
2022 Interstate 24X
Carlisle , Pennsylvania
Join Date: May 2017
Posts: 15,742
Quote:
Originally Posted by lsbrodsky View Post
"A handy accessory for the AC version is a little inline plugin device. It lets you put it inline with an appliance. You can then clamp on to the (now accessible) lines to the device. The really cool ones have a 10X side that helps with the range on the amp meter. Even the fancy ones are dirt cheap. Yes, you can also make one from scratch."

Thanks, I never knew those things existed although the use seems limited, first to something in a normal AC circuit limited to 15 amps. Seems like I would use my clamp-on more for stuff that is not or does not plug in to a normal outlet.

Larry
Hi

Indeed the standard cheap gizmo is a "plug into a 15A outlet" sort of thing. The main use is checking things like fans, coffee grinders, wall chargers, .... to see how much they pull. Comes in handy when you are trying to sort out what will and won't work (and in what combinations) with your inverter.

Since all you are doing is putting a few coils of wire "inside" the clamp, there is no reason you can't use the same trick in other settings. You *do* need to have enough wire to make the loops and it has to be flexible enough.

Bob
uncle_bob is offline   Reply With Quote
Old 07-27-2019, 09:05 AM   #20
kpm
3 Rivet Member
 
2018 25' International
Mound , Minnesota
Join Date: Oct 2018
Posts: 236
Quote:
Originally Posted by uncle_bob View Post
[...]
A handy accessory for the AC version is a little inline plugin device. It lets you put it inline with an appliance. You can then clamp on to the (now accessible) lines to the device. The really cool ones have a 10X side that helps with the range on the amp meter. Even the fancy ones are dirt cheap. Yes, you can also make one from scratch.
Bob
Could you give an link to a decent one online?
kpm is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
20 amp shore power GFI tripping Aaron-Laura Electrical - Systems, Generators, Batteries & Solar 34 06-06-2019 06:11 AM
30 amp breaker at hookup tripping with one ac unit Newbie2018 General Repair Forum 24 07-08-2018 10:36 AM
30 Amp breaker tripping Bryker Electrical - Systems, Generators, Batteries & Solar 26 10-29-2015 02:36 PM
Over heated 20 amp AC breaker tripping woppa 4 Furnaces, Heaters, Fireplaces & Air Conditioning 18 05-21-2009 08:05 AM