No shore power in Argosy, HELP!

Ok heres my dilemma. Have an 1975 Argosy 26ft that we just bought. Im the one who bought the MH for $120. I am having some bizzare electrical issues. I have a 5k portable generator that I am trying to use for temporary shore power while we work on the MH in our lot. The Generac Generator wont start so were trying to use the portable unit. I plug in the shore power cord into the generator and I get no power in the MH, only battery power. The generator has a 110v and 120v setting and I have tried both with no luck. FYI I have 2 new batteries installed, one to start the engine and the other for deep cycle for the MH.

Then I went in and checked voltage in the main breaker box. Only 30amp breaker checked out ok providing 120v AC. The other 3 breakers in the box seem not to work. None of the other 3 checked out for polarity! A quick stop to home depot for a 4 new breakers was in order. Replaced all 4 and still nothing for shore power. Onto the univolt and fuses.

Checked all fuses including the one in the front engine area. none were blown and polarity was checked on each removed fuse. Fuse connectors were a bit corroded but just rotating and moving the fuse about made a better connection. After all these checks on the fuses and univolt still nothing! No hum from univolt and when peering inside the univolt the epoxy coated circuit board has a ton of cracks in it.

Today went out and replaced Univolt with intellapower 45 unit and new fuse panel from best converter. Hooked up the same way as previous setup and still nothing.

Really at a standstill here, any help would be greatly appreciated.
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 01-30-2010, 09:48 PM   #2
2 Rivet Member
 
Olielulu's Avatar
 
1972 25' Tradewind
Webb Lake , Wisconsin
Join Date: Aug 2007
Posts: 46
Images: 29
I'm going to make a guess that the 30 amp breaker is the main power breaker. if it has power in and out, but none of the other breakers have power coming out, than it may be a bad or non-existant connection to the bus-tie. this is the main point that the other 3 breakers clip onto. Check that all the connections are tight and not corroded. if they are corroded, disconnect them, clean them to shiny metal and re-connect.

without seeing it, this is just a guess, but there shouldn't be too many options there.

Mike
Olielulu is offline   Reply With Quote
Old 01-30-2010, 09:52 PM   #3
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Checked the breaker box throughly and like I said even installed all new breakers. Zero corrosion visible. I will double check them tomorrow. Thanks for the ideas, keep em comin
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 01-30-2010, 11:08 PM   #4
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Just disassembled the original Univolt. Looks dead to me, I did not test this on its own but when I saw this cracking through the vent holes I decided to replace it. Any thoughts on the white wires in left photo's use? It was connected to the "power on" circuit with the 4amp fuse
Attached Thumbnails
Click image for larger version

Name:	IMG_0883.jpg
Views:	149
Size:	311.7 KB
ID:	95114   Click image for larger version

Name:	IMG_0884.jpg
Views:	139
Size:	354.6 KB
ID:	95115  

__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 01-31-2010, 03:28 PM   #5
Rivet Master
 
guy99's Avatar
 
1984 31' Airstream310
Dunsmuir , California
Join Date: May 2004
Posts: 1,336
Images: 16
Could your transfer switch be the culprit?
__________________
If you want others to be happy, practice compassion.
If you want to be happy, practice compassion - The Dalai Lama

1984 310 Limited Motorhome
Courtesy Parking (W/S/E/Wi-Fi) on I-5 in Northern California, 70 miles from Oregon border
guy99 is offline   Reply With Quote
Old 01-31-2010, 09:43 PM   #6
2 Rivet Member
 
Olielulu's Avatar
 
1972 25' Tradewind
Webb Lake , Wisconsin
Join Date: Aug 2007
Posts: 46
Images: 29
the power on circuit was just that. it just sent power to a light to the control panel to let you know the univolt was energized.

Any luck with the power today?

do you have a volt/ohm meter? pictures of the power panel with cover removed.

Mike
Olielulu is offline   Reply With Quote
Old 02-01-2010, 10:06 AM   #7
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Quote:
Originally Posted by guy99 View Post
Could your transfer switch be the culprit?
Not sure, where is that part? Might it be that cylindrical part in the front engine bay wit 4 wires connected to it? Attached is a picture. It it located under the black box on the left? Also just fyi the battery in this picture are is not like this anymore. I have 2 seperate ons hooked up to their respective wires
Attached Thumbnails
Click image for larger version

Name:	IMG_0865.jpg
Views:	120
Size:	251.1 KB
ID:	95307  
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 02-01-2010, 10:18 AM   #8
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Quote:
Originally Posted by Olielulu View Post
the power on circuit was just that. it just sent power to a light to the control panel to let you know the univolt was energized.

Any luck with the power today?

do you have a volt/ohm meter? pictures of the power panel with cover removed.

Mike
Thanks for the power on tip, thought that was it. Attached are some rough iphone pics on the breaker box and fuse panel. The interior of the breaker box looks spotless. I did change out all breakers for new ones. Now they all have continuity. When I replaced them seemed like I had 120v at the 30amp main. Kept the volt meter on the 30amp and activate the other 3 breakers, breaker 1 and 3 go on and dont change voltage but when I activate 2 it sends the voltmeter crazy like drops to 3v. This seems strange but I am going to recheck this to be sure my statements are correct.

One thing I noticed is that the shore power cord is large. On my old airstream trailer this cord goes directly to the breaker box. On the Argosy MH thet same cord does not. It looks like a piece of larger gauge romex, slightly bigger than the general romex coming out of the box. Is there a junction somewhere that Im missing?
Attached Thumbnails
Click image for larger version

Name:	IMG_0881.jpg
Views:	147
Size:	312.6 KB
ID:	95308  
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 02-01-2010, 10:26 AM   #9
banjobill
 
wmarsha's Avatar
 
2000 30' Limited
battle ground, , Washington
Join Date: Jun 2009
Posts: 516
a little help

ok, the gen is putting out 120VAC correct? and I suppose it also has 240VAC? Your info on 110 vs 120 is confusing. Now, you measure 120VAC at the 30 amp brkr? BOTH sides of it? Cuz all the breakers get their juice from the same place. You purchased new brkrs-I assume single pole, 120VAC brkrs, right? If you have juice to one of the brkrs, but not the others, there is something wrong in the service panel. The service panel is just a common buss to which the breakers connect. Your source will connect to this buss via the main breaker-the other breakrs will be your loads. I cannot give any more info without more photos or words from you.
wmarsha is offline   Reply With Quote
Old 02-01-2010, 10:39 AM   #10
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Quote:
Originally Posted by wmarsha View Post
ok, the gen is putting out 120VAC correct? and I suppose it also has 240VAC? Your info on 110 vs 120 is confusing. Now, you measure 120VAC at the 30 amp brkr? BOTH sides of it? Cuz all the breakers get their juice from the same place. You purchased new brkrs-I assume single pole, 120VAC brkrs, right? If you have juice to one of the brkrs, but not the others, there is something wrong in the service panel. The service panel is just a common buss to which the breakers connect. Your source will connect to this buss via the main breaker-the other breakrs will be your loads. I cannot give any more info without more photos or words from you.
There is a switch on the gen for 110 and 120, the 240v uses the twist 4 prong twist that I do not have. I have set it to both settings with no luck. I have tested it with VM and 120 is definitely coming out. Breakers were purchased at home depot, they only had one type that fit so I assumed this was ok. Yes I measured 120 coming out of the 30amp breaker. look at previous post for more about those breakers.
Thanks
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 02-01-2010, 10:49 AM   #11
banjobill
 
wmarsha's Avatar
 
2000 30' Limited
battle ground, , Washington
Join Date: Jun 2009
Posts: 516
I will be over in your area this aftnoon-want me to come by and give your electrical a look-see?
ol' bill
wmarsha is offline   Reply With Quote
Old 02-01-2010, 12:04 PM   #12
Rivet Master
 
guy99's Avatar
 
1984 31' Airstream310
Dunsmuir , California
Join Date: May 2004
Posts: 1,336
Images: 16
Quote:
Originally Posted by gmehal View Post
Not sure, where is that part? Might it be that cylindrical part in the front engine bay wit 4 wires connected to it? Attached is a picture. It it located under the black box on the left? Also just fyi the battery in this picture are is not like this anymore. I have 2 seperate ons hooked up to their respective wires
I'm not sure where your transfer switch is but it should be near where shore power comes in to the rig and near the 120 V breaker box. The function of the transfer switch is to make sure that the 120 V get power from the generator or the Shore power connection but NOT both. Here are some links to the sort of switch I am speaking of:

Automatic Transfer Switch

Transfer Relays

Mine failed the first year we had our MH. This meant I couldn't get power from the generator. But if the output side failed (don't know if this can happen), you wouldn't get power from either source.
__________________
If you want others to be happy, practice compassion.
If you want to be happy, practice compassion - The Dalai Lama

1984 310 Limited Motorhome
Courtesy Parking (W/S/E/Wi-Fi) on I-5 in Northern California, 70 miles from Oregon border
guy99 is offline   Reply With Quote
Old 02-01-2010, 07:46 PM   #13
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Well Bill was kind enough to stop out today and we both spent a couple of hours troubleshooting the electrical gremlin. What we have been able to come up with after MUCH experimentation and testing is that the original shore power cord end might be bad as well as the adapter. Both are original and look really old. Were thinking that inside the plug end might be very corroded.

What happens is we get 120v to all outlets but as soon as we put any king of load on them voltage drops like a rock and fluctuates. Bill and I think that the next step will be to replace the 30amp plug end and adapter and see what happens.

Any other thoughts would be appreciated. I will report back this week after I change out the plug ends.
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 02-01-2010, 09:16 PM   #14
2 Rivet Member
 
Olielulu's Avatar
 
1972 25' Tradewind
Webb Lake , Wisconsin
Join Date: Aug 2007
Posts: 46
Images: 29
A quick test you can do is bypass all of the culprits by making a suicide cord. Remove the female end from an extension cord (while it is unplugged is preferable) and disconnect the main power in at the breaker box (again, best done while unplugged.) now connect the suicide cord directly to the breaker panel where you disconnected the power in previously, then plug in and check for better results.

from what it sounds, you most likely do have a bad/loose/corroded connection somewhere. having voltage until there is a load is a good indicator. you may also want to look for grounds or shorts using your Ohm meter if fixing the cord doesn't fix the problem.

Mike
Olielulu is offline   Reply With Quote
Old 02-01-2010, 11:00 PM   #15
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Good idea. We did run an extension cord directly to the new intella power unit i installed and sure enough it worked immediately along with my new fuse panel. I will try your idea this week.
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Old 02-02-2010, 04:00 PM   #16
3 Rivet Member
 
gmehal's Avatar
 
1965 30' Sovereign
1975 26' Argosy 26
beaverton , Oregon
Join Date: Feb 2008
Posts: 169
Problem SOLVED!!!!

Well it was the shore power cord end. I simply replaced this and everything worked!

Currently refreshing the outlets but the AC and all outlets work now. Thanks all for your help, and especially Bill for coming out Monday to help me sort through it all.
__________________
1965 31ft Airstream Sovereign
1975 26ft Argosy Motorhome

Imagine the sight of them linked together!

gmehal is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace without shore power flmgrip Full-Timing, Winter Living & Workamping 62 06-15-2010 06:35 PM
Power surging from shore power in my Excella 500? NVDeputy Lights - Interior & Exterior 4 10-09-2009 11:52 AM
Testing shore power nbka1bm General Repair Forum 15 01-13-2008 11:51 AM
Shore Power Again The Flintstones Batteries, Univolts, Converters & Inverters 13 10-09-2007 07:18 PM
Shore power and battery power problems jfremstad Electrical - Systems, Generators, Batteries & Solar 5 05-03-2007 08:23 AM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 08:26 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.