Old 01-07-2006, 01:13 PM   #1
1 Rivet Member
 
lbell's Avatar
 
1964 26' Overlander
Currently Looking...
Charing Cross , ON
Join Date: Sep 2002
Posts: 17
Images: 22
1963 Globe Trotter

Am refurbishing this unit. Not an electrician.

Noticed that the kitchen sink has a ground wire from a mouning screw to a screw on the interior shell.

All electrical outlets are 2 prong only. The box is a 15amp 110 service only.

Is this original? Where is the ground coming from? What are your recommendations?
lbell is offline   Reply With Quote
Old 01-07-2006, 01:35 PM   #2
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Quote:
Originally Posted by lbell
... Is this original? Where is the ground coming from? What are your recommendations?
I don't know if this is original, but I would leave it.

The interior shell is usually tied to the shore power ground. Grounding the sink in the way it is would help keep you from being electrocuted if you should accidentally bump the toaster, for example, into a sink full of water & reach in to get it.

If you are curious, you may want to get your ohmmeter out, and measure the resistance between your 15 amp service box shell, and your Airstream's skin. I will bet you will measure close to zero ohms resistance.

Tom
TomW is offline   Reply With Quote
Old 01-14-2006, 07:10 PM   #3
3 Rivet Member
Commercial Member
 
Jim Jarzabek's Avatar
 
1950 25' Cruiser
Currently Looking...
Currently Looking...
Lebanon , Ohio
Join Date: May 2004
Posts: 238
Images: 16
Ungrounded outlet o.k.

What you have are original ungrounded two prong outlets. Perfectly safe. New ones can be purchased to replace the old. Do not purchase or install grounding type with the third pin at the bottom. For extra safety, you could have the electrical panel changed and install g.f.c.i. (ground fault circuit interruptor) circuit breakers for extra safety. Only have this done by a qualified person.

Good luck!
Jim Jarzabek is offline   Reply With Quote
Old 01-14-2006, 07:33 PM   #4
3 Rivet Member
Commercial Member
 
Jim Jarzabek's Avatar
 
1950 25' Cruiser
Currently Looking...
Currently Looking...
Lebanon , Ohio
Join Date: May 2004
Posts: 238
Images: 16
For all practical purposes....

The original poster discovered a "bond" wire and not a "ground" wire. The two serve different purposes. Two prong outlets were used during this period and new replacement two prong outlets are available for replacement purposes. The original poster did not mention any problems with stray voltage when touching the sink. An ohm meter is only as useful as the person using the instrument. Readings can vary depending on atmospheric conditions and the reference point to "ground". A 43 year old travel trailer will have some type of corrosion. Without getting technical and without other concerns being presented by the original poster, replacing the two prong outlets would suffice. Adding g.f.c.i. protection to the wiring at the circuit breakers would add extra protection. The poster should already be plugging into a g.f.c.i. 120 volt 15 or 20 amp circuit already, so this may be redundant.
Jim Jarzabek is offline   Reply With Quote
Old 01-14-2006, 08:03 PM   #5
Rivet Master
 
65CV's Avatar
 
1959 26' Overlander
Western , Massachusetts
Join Date: Sep 2005
Posts: 1,468
Images: 6
Bond wires

I echo the GFCI recommendation -- it's cheap insurance, especially if you can't inspect all connections. The wiring in our '63 Globetrotter was updated, so I can't make a comparison. If you do have BX cable, you can consider the 3 prong replacement if the third leg is properly grounded through the shield on the BX.

On well-built boats, large metal objects are grounded for lightning protection. Is this what the original builders were up to?

63GT
65CV is offline   Reply With Quote
Old 01-14-2006, 08:32 PM   #6
3 Rivet Member
Commercial Member
 
Jim Jarzabek's Avatar
 
1950 25' Cruiser
Currently Looking...
Currently Looking...
Lebanon , Ohio
Join Date: May 2004
Posts: 238
Images: 16
Purpose of a bond...

Bond wires are used to maintain an equal potential return path in lieau of the normal return path; i.e. if the current returns on a path other than the intended neutral. This way, in theory, there is a balance and electrocution is minimized. Armored cable from this period was not intended to have the outer jacket utilized as a ground.
Jim Jarzabek is offline   Reply With Quote
Old 01-22-2006, 02:58 PM   #7
1 Rivet Member
 
lbell's Avatar
 
1964 26' Overlander
Currently Looking...
Charing Cross , ON
Join Date: Sep 2002
Posts: 17
Images: 22
Thank you for the help. Like the GFCI breaker idea for safety.
lbell is offline   Reply With Quote
Old 01-22-2006, 03:17 PM   #8
Rivet Master
 
C Johnson's Avatar
 
1965 17' Caravel
1968 28' Ambassador
Butte , Montana
Join Date: Feb 2005
Posts: 1,201
Images: 326
Send a message via MSN to C Johnson Send a message via Yahoo to C Johnson
On my install of the new electrical panel I put a central GFCI on the circuit that powers all of the outlets. It is mounted under the panel in its own electrical box. Here is a picture of what I did. I now have 4 separate circuits plus a separate main to shut everything down at once. I wired the ground exactly as it was in the old electrical box. Do not tie the white and bare ground wires together as you would in a house.

Chris

PS - Since I had the inner skins off I put all new grounded outlets in the trailer and replaced wiring as needed.
__________________
AIR # 7276, WBCCI # 7276
Project 2k5
Life is a journey, not a destination
C Johnson is offline   Reply With Quote
Old 01-22-2006, 03:29 PM   #9
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
I missed this thread after making my last post to it. The traffic it has received warrants clarifying a few issues.

Quote:
zero ohms between you and ground is extremely dangerous.
Yes it is. My original post suggested checking the resistance between the skin & the breaker box - Not between the user & anything else.

Quote:
Originally Posted by 65GT
...In ESD safe environments there is always a 10K ohm resistor between whatever it is you are working on, your ground mat and true ground for your protection...
That resistor is, by design, fusible. It will blow to keep the person attached to the ground strap from being electrocuted. Most companies require wrist straps be verified on a separate device on a routine basis because the resistor gives up easily.

Quote:
The original poster discovered a "bond" wire and not a "ground" wire.
Jim, you lost me somewhere. My take is that both bond & ground wires, in this application, would serve to protect the end user. Did I miss your point?

Quote:
The poster should already be plugging into a g.f.c.i. 120 volt 15 or 20 amp circuit already, so this may be redundant.
Wishful thinking around here - Nothing like that in the bulk of campgrounds I have visited.

Ibell - Your safest course of action is to install GFCI breakers in your Airstream after ensuring that your shore power is properly wired for ground (three pins on your shore power plug).

Tom
TomW is offline   Reply With Quote
Old 01-22-2006, 03:31 PM   #10
Rivet Master
 
DavidsonOverlander's Avatar
 
1964 26' Overlander
1974 31' Sovereign
Milton , ON
Join Date: Oct 2002
Posts: 1,225
Images: 4
Quote:
Originally Posted by Jim Jarzabek
What you have are original ungrounded two prong outlets. Perfectly safe. New ones can be purchased to replace the old. Do not purchase or install grounding type with the third pin at the bottom.
Can you explain this, please? If I want to run something that has a 3 prong plug (like a microwave) should I cut off the third prong so it will fit? That doesn't seem like a good idea.

Couldn't new 3-prong outlets be installed and grounded to the trailer since the trailer is grounded through the 30 amp cord when you plug it in? I suspect from your post you're going to say no, but I'm not sure why.

Thanks,
__________________
1974 Sovereign
2005 F-350 SRW 4x4 crew cab long box
TAC ON-5

1965 Avion C-10 Truck Camper (65avion.home.blog)
DavidsonOverlander is offline   Reply With Quote
Old 01-22-2006, 03:47 PM   #11
Rivet Master
 
TomW's Avatar
 
1967 26' Overlander
Huntsville , Alabama
Join Date: Dec 2003
Posts: 3,018
Images: 4
Quote:
Originally Posted by DavidsonOverlander
...Couldn't new 3-prong outlets be installed and grounded to the trailer since the trailer is grounded through the 30 amp cord when you plug it in? ...
Yes; while this implementation would not fit current code, it would serve to protect the user. It certainly meets the intent of the code.

I think I know what Jim is getting at, but it is not coming out clearly. Hopefully he will catch this thread & end the confusion.

Tom
TomW is offline   Reply With Quote
Reply

Tags
1963


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
1961 - 1963 Bambi Serial Number Guide Andy R 1961 - 1963 Bambi 61 07-26-2022 07:20 PM
1963 Airstream Globe Trotter - Where Can I find these Parts Uncle_Phil 1960 - 1964 Globetrotter 12 03-27-2014 04:39 PM
Serial number of 1960s Globe Trotter ? What year is it ? oldvws Our Community 1 12-12-2002 08:25 PM
Globetrotter 1963 - Kitchen Sink Drain Leak Under the Floor Uncle_Phil Plumbing - Systems & Fixtures 3 08-09-2002 06:59 PM


Featured Campgrounds

Reviews provided by

Disclaimer:

This website is not affiliated with or endorsed by the Airstream, Inc. or any of its affiliates. Airstream is a registered trademark of Airstream Inc. All rights reserved. Airstream trademark used under license to Social Knowledge LLC.



All times are GMT -6. The time now is 07:57 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.